I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.

Based on what evidence? Whilst this is possibly what has happened, there is nothing in the regulations to prevent a circuit being extended in this way.
If a radial socket circuit has the capacity for additional sockets, then why not extend it from the DB if that's the most logical place to connect it? Surely this is better than adding an additional joint into the circuit somewhere?
 
reg 314.4
when an installation comprise more then one final circuit .each final circuit shall be connected to a separate way in the distribution board .

Yes, now add the definition of a circuit.

There is nothing which prevents a circuit being formed of two branches from an ocpd. This could be a better design if it reduces th overall length of the circuit
 
Why aren't you soaking up the sun, and drinking those lite beers the Yanks favour, instead of wasting your time on here. Holiday of a life time you said!!

Yup... Very true, but there's good wifi in the parks and there's time in the queues....

It's 32 here now and we've just got back to the villa..... And I've just had a dip in the pool. It'll be beer o'clock very soon, not rubbish yank beer though....
 
Yes yes yes heard all this and 314-01-04 refers to final circuit, I will not be swayed by sideway interpretations.

I don't think my interpretation is sideways, the definition of a circuit is clear, as is the regulation I think you are referring to, For the sake of avoiding ambiguity lets just call it the whole of 314.

You still have not provided any clear definition of a circuit which you are referring to, nor any clear regulation which prohibits a circuit having two branches, or two legs, being fed from the middle of the circuit, etc.

As it stands, if you were carrying out an eicr on an installation I had designed with a circuit of this nature then I think my lawyers would be ripping you a new one by now.
 
Westward your argument has as much logic as the neutrals in switches argument. Some people just seem to stick their head in the sand and ignore facts.
You seem to admit that it complies with 7671 and yet insist on coding it!
You need to remember that coding can cost the occupier money, a lot of money. Unless you can justify a safety issue or a departure you CANT code.
Coding because of your personal views is simply unacceptable.
 

Reply to Two cables connected to mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
629
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
344
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
716
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
242

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock