Westward your argument has as much logic as the neutrals in switches argument. Some people just seem to stick their head in the sand and ignore facts.
You seem to admit that it complies with 7671 and yet insist on coding it!
You need to remember that coding can cost the occupier money, a lot of money. Unless you can justify a safety issue or a departure you CANT code.
Coding because of your personal views is simply unacceptable.
Don't recall suggesting it complied with BS7671 nor is it a personal view. I read Reg 314.4 that each final circuit should be given individual circuit protection that is it which I C3.
 
I am of the same opinion as @davesparks on this. It is one circuit no matter where the circuit is supplied from. If you have 2 radials in one MCB it is still one circuit with the supply to that circuit in the middle rather than at the end. If you consider the practicality of it, it actually is also safer. Consider you loose earth continuity on on leg of the circuit for whatever reason, the other leg of the circuit maintains its earth continuity. Also reduced loading if having 2 radials to the circuit means the overall length is reduced.

My interpretation of 314 and specifically in this case 314.4 is that for example you had 2 circuits, say upstairs lighting and downstairs lighting, these should not be connected to one MCB.

I would say it is down to the design and interpretation as to whether they should be separate circuits. If in the OP's case both radials in the MCB served a defined area (lets say downstairs) and the breaker is labelled so then I would personally say that is the downstairs lighting circuit. If one radial served the downstairs and the other radial served a light in the loft I would perhaps code it as C3 as there is a risk here of indirectly energising a final circuit intended to be isolated.

On a tangent: Why does a BRITISH standard have an American spelling of energising?
 
images.jpg ...........
 
I note it on the certificate as for example in conductor sizes 3x1.5 3x1.0 and note that in some cases more than one conductor is terminated into one protective device and this is how it can be noticed.

I know a lot of people who C3 this
 
Don't recall suggesting it complied with BS7671 nor is it a personal view. I read Reg 314.4 that each final circuit should be given individual circuit protection that is it which I C3.

So 2 rooms with say 3 sockets in each room,

Each room fed from it's own mcb ok (1 conductor in mcb)
Both rooms wired on the same ring ok (2 conductors in mcb)
Room 1 wired as a radial with room 2 spurred from any socket in room 1 ok (1 conductor in mcb)
Both rooms on same circuit but wired independently back to the same mcb not ok (2 conductors in mcb)
 
Final circuit, and yes I will still C3 it lawyers or no lawyers.

You can't just state 'final circuit' without giving a definition for it.
How do you define what constitutes a final circuit and, crucially to this debate,what does not constitute a single final circuit.

At the moment it appears that your definition includes a requirement that a final circuit must only have one conductor at the ocpd.

If there is a 1' piece of cable connected from the ocpd to a JB and then two cables leave that JB to each serve two sockets, is that one circuit or two?
 
Don't recall suggesting it complied with BS7671 nor is it a personal view. I read Reg 314.4 that each final circuit should be given individual circuit protection that is it which I C3.

I read the reg exactly the same, it is not that reg which is at debate, it is the definition of a circuit.

If the two cables were not both serving sockets, lets say one feeds sockets and the other a pillar drill, then I would be inclined to agree with you. But when both cables are serving sockets, and if there is no overload as a result of the number of sockets, then I see nothing to comment on.
 
You can't just state 'final circuit' without giving a definition for it.
How do you define what constitutes a final circuit and, crucially to this debate,what does not constitute a single final circuit.

At the moment it appears that your definition includes a requirement that a final circuit must only have one conductor at the ocpd.

If there is a 1' piece of cable connected from the ocpd to a JB and then two cables leave that JB to each serve two sockets, is that one circuit or two?
See "definitions".
 
I read the reg exactly the same, it is not that reg which is at debate, it is the definition of a circuit.

If the two cables were not both serving sockets, lets say one feeds sockets and the other a pillar drill, then I would be inclined to agree with you. But when both cables are serving sockets, and if there is no overload as a result of the number of sockets, then I see nothing to comment on.
Your latter statement is somewhat contradictory and why you keep harping on about definition of circuit whilst it is the Reg to which I debate I have no idea.
 
As far as I'm concerned if you take two separate lighting circuits on two separate mcb's, and connect them together into one mcb then they become a single circuit. As long as the schedule and board are correctly labelled and identified there is no issue. It may be claimed that this could result in confusion, anyone confused by a correctly identified circuit consisting of two radials linked at the OCPD shouldn't be touching it in the first place.
 
The On Site Guide (page 71) says you can connect a non-fused spur from a ring final circuit "at the origin of the circuit in the distribution board", which I think would mean three conductors in the MCB and would look like a ring and a radial connected to the same protective device.

If spurring off a ring final inside a consumer unit is allowed then surely having a radial go off in two or more different directions from a consumer unit is ok as well.

What if you add a light or a socket in an under stairs cupboard near the consumer unit, surely you can connect that to an existing lighting or socket circuit in the consumer unit.
 
Your latter statement is somewhat contradictory and why you keep harping on about definition of circuit whilst it is the Reg to which I debate I have no idea.

What are you debating about the reg? The reg requires that each circuit be fed from a separate way. It does not make any mention of the number of cables which can be connected to an ocpd, merely the number of circuits.
In order to comply with this reg you must have a definition of what a circuit is, otherwise the reg is meaningless.

In definitions a circuit is defined as:
"An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s)"
A final circuit is defined as:
"A circuit connected directly to current-using equipment, or to a socket-outlet or socket-outlets or other outlet points for the connection of such equipment."

Neither of these makes any mention of the number of cables which make up a circuit.
 

Reply to Two cables connected to mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
625
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
343
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
715
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
240

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock