T

TailSpin

Hi All

I have come across two 3 phase in line WOODS fans rated @ 0.22 kW / 0.6 amps connected together on one overload. This does not seem correct is there anyway this could be right ?

Regards

Tailspin :shocked::confused:
 
wrong to me, not dangerous just doesn't really protect as it should.
 
Woods dual impeller fans were often connected like that. It’s 20 odd years since I worked on them. If your worried about it change it for one contactor with two O/L units but if it’s a Woods own brand starter, best of luck! They were tight on space at the best of times.

It’s important that they start and stop together so one contactor with two O/L units is the best way.
 
Last edited by a moderator:
Hi All

I have come across two 3 phase in line WOODS fans rated @ 0.22 kW / 0.6 amps connected together on one overload. This does not seem correct is there anyway this could be right ?

Regards

Tailspin :shocked::confused:



I don't think motors < 0.37kw require overloads yet this setup offers phase loss/imbalance protection and overload indication.

What is the overload set to?
 
As memory serves, that’s the basis of the original Woods starters.
Basically keep it simple.

The ones I worked on dated from the early 50’s (just older than me before you lot start), the only time they failed was when a kiln backfired and the fan motors got fried.
 
As memory serves, that’s the basis of the original Woods starters.
Basically keep it simple.

The ones I worked on dated from the early 50’s (just older than me before you lot start), the only time they failed was when a kiln backfired and the fan motors got fried.

I would have said it was roasted more than fried:yes::teeth_smile:
 
Hi all
Thanks for your thoughts . Overloads are rated for both to run together I was wondering if any regulations are in place to avoid running more that one motor on one overload ?

Regards
John
 
If you are using the original Woods starters then you are going by the manufacturers recommendations.
 
All of the overloads are Alan West : controlled by
Enbray contactors .
This set up is used through out the site for AHU extract and supply fans.
Regards
Tailspin
 
Christ, are you working in a museum?

How long have these motors been like that? Are they working OK?

Unless you’re trying drum up business for unnecessary work, leave it alone.
 

Reply to Two Three Phase motors on one Overload in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock