Can anyone help with the time current characteristics of which will operate first? Essentially a 40A type D crabtree pole star fed from a BS 88 g 63A fuse. Looking at the time current characteristics I reckon that the BS88 would operate at a fault current of 500A for a 0.4s disconnection whereas a Type D operates at 800A for 0.4. Am I right and if so how can you justify using one?!:dunce2:
 
dont have the time graphs to hand but i do know that any circuit with a type D mcb needs a super low Zs , so i'd be checking that as well.
 
Why is there a 40A type D downstream of a 63amp bs88 what is the set-up for needing a type D in series with a bs88 general use fuse
 
Is this the requested mcb as per manufacturers instructions for the PSU if this was the case i would also be weary that although the BS88 although higher in current rating may operate on inrush as from you OP you said BS88 'g'.... gg are for general use and gm are usually for motor rated or other circuit with inrush currents, but both knowledge of the inrush peak of the psu and the inrush tolerance of the bs88 are needed usually sorted from manufacturers tech' help.
At a glance though you have inverse partial discrimination in favour of the upstream device and due to the nature of it supplying a DB then it shouldn't be set up this way.
If a fault current of 2ka flows it will exceed tripping points of both devices by a good margin then the decider to which operates is down to many variables but favouring the bs88 to rupture first.
 
From the B7671:2008+A1:2011 protective device characteristics it would appear that discrimination is not assured, however, you will need to consult the manufacturers data for the specific devices to be certain.
 

Reply to Type D 40A MCB upstream of BS88 63A Fuse in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
T
Can someone please point me in the direction of a time/current characteristics of a D type 20A MCB and the chart has to be from a manufacturer...
Replies
3
Views
972
T
V
Hey guys, i have started to do some inspecting and testing, i am finding it very interesting although the certification part is a little confusing...
Replies
26
Views
4K
W
Hi guys, Just had a bit of a tidy up at work regarding the circuitry of a few bits and bobs. I have recently just put in a new TPN 6 way and...
Replies
19
Views
3K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock