The correct size of cable would depend on the arrangement of the circuit and the installation method of the cable along with other derating factors and considerations towards prospective earth fault loop impedance values and volt drop.
 
If the protective device is 32A, then the CCC (Current Carrying Capacity) of the cable has to be higher.
The CCC will depend on the installation method, but generally you would use 4mm2 or perhaps if the cable runs through a lot of insulation, 6mm2.
 
Not a college question.
Installation was done in 2.5. and passed as being safe.
Recent problem and Home Emergency electrician informed me that it should not have passed and should be in 4mm.

If it is wired in 2.5mm cable as a ring circuit then it is (most likely in a typical domestic installation) fine on a 32A mcb. As a radial then no.
 
Not a college question.
Installation was done in 2.5. and passed as being safe.
Recent problem and Home Emergency electrician informed me that it should not have passed and should be in 4mm.
Who 'passed' it?
The Home Emergency guy is right.
There are two solutions
1. Rip out the cable and replace it with 4mm
2. Change the MCB to 20amp, or a 25amp if you can find one for your make of consumer unit.


My above reply does depend on some basic inforomation as asked by Pete
How long is the circuit
Installation method
Appendix 15 BS 7671
 
The area the area of the kitchen is approx 30 metres.
The radial circuit was installed around the perimeter of the kitchen before the kitchen was fitted and appliances installed.
 
So you’ll have to limit the current to the current carrying capacity of the cable. And that is somewhat less than 32amps.
Replace 32A MCB with a 20 or 25A MCB.

The alternate is to find the socket at the end of the radial and run a length of 2.5mm from there to the consumer unit. Then the radial becomes a ring final and ok for the 32amp MCB (subject to testing).
 
my first action wouyld be to replace the MCB with a20A or 25Aas previously suggested. cheapest , easiest option. if it trips, then conversion to a 32A ring would be next step.
 
I may get shot down for this but seeing that its a kitchen feed I would feel it better to keep it at 32A and make it into a ring.
Any other room I'd say change the breaker to a 20A.
 
Not a college question.
Installation was done in 2.5. and passed as being safe.
Recent problem and Home Emergency electrician informed me that it should not have passed and should be in 4mm.

I'm hoping you have the certificate and the details of the installer - and if you do you need to address your concerns in writing.

As its a kitchen I'm guessing you have multiple appliances on said circuit and therefore you really do need to get this sorted out before something starts smelling of burning.
 

Reply to Uncertainty over cable size in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
641
Hi , I’m going install a commercial 450mm extractor fan , what size and type of cable should i use ?
Replies
7
Views
363
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
262
Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if...
Replies
1
Views
609

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock