Discuss Underfloor heating L-E problem in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
2
Hi, ok I half dont want to ask this question as it doesnt sit right but Id like your opinions.
Installed a heating matt and after the tiles went down I did my final IR tests and there is now a problem between L-E at a reading of ~22ohms. The reading between L-N is still normal at 43ohms, correct value from the manufacturer. Now then what is going to be the main problem with me disconnecting the mat Earth from the main earth and letting it run like this? Problems i see are possible arcing causing further damage to the matt thus totally ruining it, possible electric shock but not sure as porcelain tiles arent known for there conductivity values.
Ideal situation is to rip the floor up and replace the matt but the tiler is denying its his fault and not going to pay for this, neither is the customer and im not also, so who foots the cost for this.
Anyone had this before?
Thanks
 
Whatever you do don't connect it up and don't leave it in a way that it can be livened up...
did you carry out an IR test prior to tiling?
who installed the mat?
 
Did you forewarn the customer about what could happen , I would now tell them that you tested the mat as recommended by the manufacturer and noted the readings , and the reasons for it , You cannot disconnect the earth as you're suggesting , the earth is there as a return path for fault currents , and would be unsafe to do this , I assume it was a tiler who laid the floor tiles??
 
Ok cool, thanks. I installed the matt, did an IR test after taking it out of the box still rolled up, then one after I laid it before the tiler got it.
 
If you tested before and after i would say you were in the clear mate. Crap situation but not one that you have caused. Explain to the customer it was fine before tiling and now its not and you won't energise it until the reading is correct. Don't ever bodge a job ESPECIALLY not when it's not your fault!
 
Yeah agreed, I do have it all written down so will return it to the customer and will hopefully get this resolved! Bugger when these nice simple jobs turn into nightmares!
 
Something I have done in the past is to get the customer to witness the readings before and after the floor is tiled.

I always return with a bit of trepidation before I carry out the post tiling tests.

As others have said, don't connect it up.
 
second previous advice. tiler's buggered it. tiler pays. end of.
 
1. Estimate approximate position using a multi meter.
the value already given may indicate it is halfway.
2. The use of a TDR would determine location more accurately.
3. My favourite, would be to use a thermal imaging camera
Once the damaged section is found it may become obvious why it is damaged.
Special repair kits are available but all you need is good quality heat shrink..
 
If I was the tiler and being accused of damage to the matt, I would just say prove it ?

Lift the tiles and what ? you still couldn't prove the tiler done it. I've fitted a few and never once had a tiler damage one of them mats or single cables. Like I said in another post, takes some doing to damage it.

You have to prove when you laid it and it was not damaged then and you can't.
 
Hi all
you can get it repaired & also find the location of the fault, company comes out & they put a test unit on the Matt that they then trace out the floor showing fault location then up with that tile & fix the fault, not used this before but have had other sparks who have had the same problem think they went through Matt manufacturers. Also when install underfloor heating I test mat first then install a test unit I leave on until I come back just has open circuit on it & gives a tone if circuit is shorted.
Good luck ( cost they spoke about was £350) for fault finding
 
Resolution is the key word..
Do what you can whether its at your cost or theirs, a bad word travels faster than a good word..

Ive found a few damaged heat mats;
Screws from the toilet being screwed down.
Screws from the door threshold..
Staple gun damage from initial install..
Also found a couple that have had tiles dropped on them from tilers
 
Hi Anthony
as someone helped me a few years ago & it works go the extra mile for the client even if hurts your pocket you will get a better feed back & in most cases repeat business, bad news always travels further than good news. If it was me I would stump just to prove the point of the damage if you can see it. Also did they latex the floor after the laying of Matt?
 
Last edited:
Totall agree with Marc, good advice..
if you can't locate the fault yourself then get someone in who can..
Well worth the cost as this is a large bathroom and the heat mat alone would have cost about £300..
Speak to the customer and try and come to an agreement between all parties
 

Reply to Underfloor heating L-E problem in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Hi all, i'm a home owner just looking for some advice. Over Christmas the RCD on a split panel fuse box kept tripping. We narrowed this down to...
Replies
12
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock