    Hi,

    Is it allowable to install an underfloor heating thermostat inside the bathroom but outside any of the listed zones? We are having a room converted into a bathroom and there is no suitable place directly outside the room to install it, however the new bathroom itself is about 3m x 3m and there is plenty of room inside. If this isn't possible the only other location would be in another bedroom adjacent which is a bit daft!

    Am I correct in thinking it could be placed at least 600mm from the sink, near the doorway and away from any other sources of water. The sink would be the closest source of potential splashing.

    Thanks
     
  2. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    You should also ask the manufacturer if it’s suitable for that sort environment.
     
    • Agree Agree x 1
  3. TJ Anderson
    Offline

    TJ Anderson Forum Mentor

    Location:
    Derby
    Yes. If it is outside of Zones and has 30ma RCD protection (Additional Protection) then it is fine with the regs.

    However, as Midwest says above, check with manufacturer if the the thermostat itself is suitable for environment first.
     
  4. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Any UFH in bathrooms I have come across have a probe in the floor to the stat outside.
     
    • Agree Agree x 1
  5. mattg4321
    Offline

    mattg4321 Electrician's Arms

    Location:
    South East
    Or airing cupboard maybe
     