Undertaking an eicr on a small commercial unit, tpn 100a 1361 main fuses to tpn dist board, 16mm tails
i have only read the side of the fuse carriers not actually pulled the fuses to confirm

i have clamp metered the supply at a roughly peak time in the premises and had <30A across any one phase, and have inspected all supply terminations for the 16mm at all points after the meter and show no signs of heat or overload damage at all, and look in good condition, the install is around 20 years old

i have put a C3 for this

what would be your opinion?
 
seconded ^^^^.
 
Thirded ^^^^^^
 
Fourthed
 
I would give it a code 3 requires improvement with further investigations required and mark on you cert under limitations that the fuse size is as labeled
 
As above C3 with further investigation required. Either the tails are too small (which I doubt) or the fuse carrier is incorrectly labelled. You will probably find the supplier has fitted 80 amp fuses and not updated the label on the fuse carrier.
 
16mm is fine as long as the supply is not PME (TNCS) in which case 25mm is the minimum and would require a "requires attention", "does not comply with BS7671" code.
 
i'm not a number, i am a free man.........the prisoner.
 
Last edited:
i'd be more afraid of falling off this:

Undersized main tails eicr code 225px-Prisoner_sm - EletriciansForums.net
 

Reply to Undersized main tails eicr code in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock