Discuss Understanding cable zones..... in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,600
Cable zones are vertical or horizontal from an accessory.

I was wondering how this is affected by accessories that are not visible? In theory you could have a cable going horizontal from a socket above kitchen worktop and then down to a socket below worktop which is hidden behind the washing machine. Also the same could happen with a cable going from a cooker switch to cooker outlet plate. I realise we usually bring the cable down first from the socket/switch in the 2 above examples but occasionally this may not be possible.

Cheers.
 
If the accessories cannot be easily seen, then they would not be providing prescribed routes.
If as you mentioned, you are unable to run a cable either vertically or horizontally from a visible accessory, you would have to provide another method (not RCD) of additional protection.
Earthed metallic sheathing, conduit, etc.
 
If the accessories cannot be easily seen, then they would not be providing prescribed routes.
If as you mentioned, you are unable to run a cable either vertically or horizontally from a visible accessory, you would have to provide another method (not RCD) of additional protection.
Earthed metallic sheathing, conduit, etc.
This makes perfect sense, but the regs don't actually state 'visible' in relation to the accessory. 522.6.202
I realise this would defeat the object of the cable zones though, although in the 2 above examples it could be argued that the socket behind the WM and the cooker outlet plate behind the cooker are visible, you just have to move the item blocking them?
 
Routing of cables is very subjective

I have seen sparks go at all funny angles and outside zones as it’s ‘just quicker this way’

Hmmm
 
Always find this annoying when cabling to external lights.
Yes! It's going to be on an external wall so the wall will be >100mm so you cant use the other side as a zone. Usually best (if the light is fairly high on the wall) to take it from a first floor socket, FCU next to it and drill straight out. Doesn't always work out nice and neatly like that though!
 
Yes! It's going to be on an external wall so the wall will be >100mm so you cant use the other side as a zone. Usually best (if the light is fairly high on the wall) to take it from a first floor socket, FCU next to it and drill straight out. Doesn't always work out nice and neatly like that though!
that's what i usually do for security lights. FCU in bedroom, drill straight out , then black flex to light. on a couple of occasions, I've zigzagged a chase down the mortar and buried the cable ( within the zone/s created by the fitting) for finicky customers.
 
Yes! It's going to be on an external wall so the wall will be >100mm so you cant use the other side as a zone. Usually best (if the light is fairly high on the wall) to take it from a first floor socket, FCU next to it and drill straight out. Doesn't always work out nice and neatly like that though!
Yea..seems ridiculous,I want my light there,no you can’t...unless...
 

Reply to Understanding cable zones..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
786
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
15
Views
389
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
15
Views
534
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Rewiring an old farm cottage… every wall brick and previous wiring not done well at all. I can’t locate any of the prescribed zones diagrams on...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock