O
Octopus
Most of have 10mm and 16 mm to hand .... 10 mm nearly every time for me
Discuss Understanding minimum CPC requirements? in the Electrical Forum area at ElectriciansForums.net
Yes that is correct.
The CSA of the earthing conductor with both TN-S and TT can be less than that of the bonding conductors.
There was one edition of the OSG which said the minimum CSA for the earth in TN-C-S was 6mm2.Yup - shame the muppets who are assessing people don't seem to understand this
I blame the pretty pictures in the front of the OSG
Reply to Understanding minimum CPC requirements? in the Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.