Discuss unqualified council inspection! in the Canada area at ElectriciansForums.net

W

welshgit

Hi all,

I have just completed the 1st fix on a rewire and have invited the local council along to inspect (huge invitation fee!!!!!) in order to apply for part P registration.

I have installed everything to 17th as this is my qualification and to me makes it easier.

Council guy is 16th and wants me to alter everything so he can adequately assess it!!!

He wants me to swap a 30ma RCD for a 100ma time delay RCD as the supply is TT. This cost is huge for the customer. Also he wants me to supplementry bond the bathroom and cap all my cable chases with steel capping:mad:.

I have tried to argue but he is being awkward.

I have explained that all chases are in the safe zones and although not 50mm in the wall (engineering bricks:eek:) are protected by RCD's.

He has rebooked for today and is coming along with his foreman and the building inspector.

His excuse is that I am the 1st 17th in the area and I am the test case for them to get to grips with the new regs!


Anybody else experiencing similar problems
 
Ask them why the've not done the 2382-20, they've had long enough to get it sorted.
If you've installed to the 17th ed thats not a problem & you are within your rights to stand your ground.

His excuse is that I am the 1st 17th in the area and I am the test case for them to get to grips with the new regs!
This isnt your problem.
 
Cheers for the support guys,

The rebooked inspection went well.

The foreman walked in saw the new dual 30ma board and said that it had passed 1st fix.

I asked why it had been so awkward and he replied 'coz it this long for the NICEIC to get back to us'.

I am glad that I can can get registered after this!!!:D
 
i can understand some sparks not up to speed
on the 1st of july i passed mine in june if the course had been full
it may have took me into july but someone who is basicly employed by local goverment should not be inspecting 17th edition work when they only hold 16th well done for sticking to your guns
 

Reply to unqualified council inspection! in the Canada area at ElectriciansForums.net

Similar Threads

Here we go again, another job that has had a council inspection, different council to last time but still perplexing. The problem with these jobs...
Replies
14
Views
1K
i have faild napit annual assessment with silly mistake of using on consumer unit type AC rcd instead of Type A rcd. i bought type A rcd but they...
Replies
6
Views
692
Hi All, this forum was incredibly helpful when I last posted. I'm a girlfriend (hoping to level up soon) to a man who is just starting his...
Replies
47
Views
3K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock