0
Recently moved into a new house. Attached a picture of the state of the garage wiring.

There's a mains cable (pretty sure it's direct from the fusebox) going to a junction box. This is connected to a light switch, double socket (fridge/freezer and tumble dryer plugged in) and two light fittings.

I assume it's not part P compliant. Can I just replace it with a 2-way garage consumer unit, with a 32A MCD for the double socket and the 6A MCD for the lighting? And have it certified by an electrician?

20171110_095238(1).jpg
 
You'd be better off just adding a FSU for the lighting circuit.

What size breaker the incoming cable wired back to at the CU?
Is it RCD protected?
 
Last edited:
If you are concerned get a local spark to inspect the sub main and garage fuseboard.

Only then will you have facts.
 
Recently moved into a new house. Attached a picture of the state of the garage wiring.

There's a mains cable (pretty sure it's direct from the fusebox) going to a junction box. This is connected to a light switch, double socket (fridge/freezer and tumble dryer plugged in) and two light fittings.

I assume it's not part P compliant. Can I just replace it with a 2-way garage consumer unit, with a 32A MCD for the double socket and the 6A MCD for the lighting? And have it certified by an electrician?

View attachment 39224
i know a GOOD sparks in LEEDS. NICEIC Approved. honest and genuine, so you won't get ripped off. pm me if you want me to contact him for you.
 
i know a GOOD sparks in LEEDS. NICEIC Approved. honest and genuine, so you won't get ripped off. pm me if you want me to contact him for you.
Not some dodgy ginger bloke??? :D
 
Recently moved into a new house. Attached a picture of the state of the garage wiring.


View attachment 39224

I assume it's not part P compliant.o_O It should be assessed as to whether it complies with the IEE wiring regulations it has little to do with some obscure part of the building regs

Can I just replace it with a 2-way garage consumer unit, with a 32A MCD for the double socket and the 6A MCD for the lighting? No it needs to be assessed and modified with the Iee wiring regs in mind

And have it certified by an electrician? No,certification eg installation/minor works is for installers (be they electricians or the general public) to record work they carried out themselves
(there is now a scheme available for 3rd party notification procedure )


You could have a inspection report on any alterations you make,bear in mind if you do,this where that building reg Part p now becomes relevant
Is it notifiable or is it not ?
 
yeah, i've worked with him. good spark, good banter.
 
Looks to me that the wiring has been adapted over time.
Might find that the original cable is sized for lighting not power.
 

Reply to Unsafe garage wiring and consumer unit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
723
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
707
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi Wonder if any one could give a rough estimate for first fix electrics for a small 4x4 side extension? Would involve moving consumer unit same...
Replies
2
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
422

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock