Hi I read on an old thread from BruceB that voltage drop should be added to the local mains voltage to find out what the voltage will be at the output terminals of the inverter.

I have a situation on a 50kw system with 3 X SMA 15000TL where 2 work fine however the 3rd is generating a lot less than the other 2. The customer says it cuts out and I suspect it is because of upper voltage shut down.

The cable run is a good 200 meters so it could be cable drop but why are 2 out of 3 working?

Any solutions welcome.

Thanks
 
The basics that spring to mind are:
- measure output voltages at each inverter on a sunny day when all arrays equally illuminated to see if there is a difference;
- or make it dead and measure cable resistances to compare;
- log on with sunny explorer and check the grid protection parameters are set identically on each inverter.
Regards
Bruce
 
If the parameters have been factory set to something other that G83 (which for your use they should be at G59/2) you'll need a Grid Gaurd code from SMA to be able to login and see those parameters.
 

Reply to Upper voltage shut down in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
759
Good morning all. Before I start I am not an electrician and am relatively new to this topic. Current set up Axpert 5.5 Kw inverter, 7 x 420...
Replies
4
Views
1K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
873
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock