Discuss Use an old cable for lighting circuit? in the Australia area at ElectriciansForums.net

D

DGClarke

Hi
We are rewiring a house, and know that we'll need a Part P inspection after the work is complete.

I wonder if we can use the exisitng feed for the upstairs lights (it runs nicely in the walls to the loft space through a long conduit run, so won't be trivial to replace.

The cable is 1960s vintage, is good quality PVC cable in grey with 1.5mm2 standed condictors and a solid earth.

The core colours are Red/Black. Cable is in good condition.

It seems daft to have to replace one perfectly good cable with another, just to change conductor colours if the Part P regulations don't REQUIRE us to to this.

Any advice gratefully received

Dave
 
Hi
We are rewiring a house, and know that we'll need a Part P inspection after the work is complete.

I wonder if we can use the exisitng feed for the upstairs lights (it runs nicely in the walls to the loft space through a long conduit run, so won't be trivial to replace.

The cable is 1960s vintage, is good quality PVC cable in grey with 1.5mm2 standed condictors and a solid earth.

The core colours are Red/Black. Cable is in good condition.

It seems daft to have to replace one perfectly good cable with another, just to change conductor colours if the Part P regulations don't REQUIRE us to to this.

Any advice gratefully received

Dave

Dave first things first.

Why are you rewiring in the first place?
Is somebody qualified (i.e. a Part P scheme member) rewiring the property?
Have the lighting cables had a Insulation test to check the condition of the cables?

Under Part P you will need an Inspection at first fix for sure.

I would suggest even without looking at the cable that it will need replacing.

You have to bear in mind you are talking about a 1960's, 48 years old cable that has been used and taking an electrical load on a day to day basis. Just because it may look good to you does not mean that it is good. It is very simliar to saying something that works and something that works safely.

I have personally taken out lighting circuits where the cables look ok in certain area's but in the loft they have been chewed away by squirrels and the like leaving a major fire hazard.

The insulation of all cables will break down over a period of time which is why the maximum recommended Periodic Inspection and Test Report on a domestic property is 10 years. If you have had this done then it will give an idea (at the date tested) of what condition the cable is in?

If you are looking to bring the property upto a safe standard then I would recommend that you replace all your properties cables if they are all in a 1960's condition.

It may seem like hassell, but worth it in the long run.

Hope this helps!

Warren
 
Warren

Thanks for the reply, and I take your (very valid) point about the age of the cable, and the quality of the insulation. For sure there have been rats in the loft in the past and they're certainly capable of knawing through cable. We will certainly replace it now that you have reminded me

We are rewiring because it needs it (bedrooms with only ONE single socket etc). There are a whole lot of new sockets/lights to install as well as changes to other parts of the system.

We will not be using a Part P electrician to do the work, as we can do this ourselves, even so far as doing the insulation check. We have the necessary equipment to do it.

We ARE going to apply to the local authority and pay to have the work inspected and certified as Part P compliant once it is complete. The building regs that we are submitting to the local authority will state that we are rewiring and that a Part P inspection is requested at first fix.

Thanks for your fast and informative response.

Dave
 
Dave,

No problem, glad to help.

Just a quick reminder that we are now working to the 17th Edition Wiring Regulations. i.e lighting cables buried less than 50mm from the surface require RCD protection.

Warren
 
Yes, we're going to use a 17th edition consumer unit, and we are aware of the safe zones for cables run in the walls.

I would like to ask one supplementary question if I may.

We are installing small halogen spot lights either side of the bed. The live and neutral come down vertically from the ceiling in plastic conduit to the light and then drops a further 12" or so, again in conduit to a switch/dimmer.

It seems to me that the tidyiest way to wire this is to strip the outer sheath for the last 12" or so and then run only the live inner wire to the dimmer. The neutal breaks out at the lamp, and then we run a separate switched live (brown colour again maybe) back to the lamp from the dimmer.

My son-in-law is against this. He wants to put sheathed cable in both segments. This will need a join in the live behind the lamp.

It seems to me that you'll end up with a really tidy solution with NO unneccessary joins if you run the unsheathed inners in the conduit.

I was wondering what if anything the regs say about that.
 
Sorry Dave I can't say that I would agree with that? :mad:

The sheath of the cable is there for protection and should be left in place.

Us sparkes get a right grilling for leaving bare earth wires any where (not that I do personally), so stripping and leaving a 'live' wire unprotected is a no-no.
 
Last edited by a moderator:
Sorry Warren, I certainly didn't mean BARE wires, live or earths.

But I guess you knew that and are telling me to leave the cable completely sheathed, even though we're running these conductors in conduit for protection.

OK. I'll shut up now, and take your good advice.

I think I might buy a Part P self training CD course and take the exam.

Thanks again.
 
I cant see the problem as long as you run a single core (insulated) cpc to the switch along with the switch wire and common, the conduit is sufficient means of protection for the cable and running singles in pvc conduit is normal practice.

like you say one less join :)

Is somebody qualified (i.e. a Part P scheme member) rewiring the property?

2 completely different things my friend;)
 
Can,t see any problem as long as the lighting circuit is on rcd as you stated,which it would be using 17th ed con/unit, but make sure that when you strip the T&E at the fitting u make sure that the cpc is sleeved g/y and also make sure that the upstairs lighting circuit is on the same rcd side as the downstairs ring main.
 
I cant see the problem as long as you run a single core (insulated) cpc to the switch along with the switch wire and common, the conduit is sufficient means of protection for the cable and running singles in pvc conduit is normal practice.

like you say one less join :)



2 completely different things my friend;)

Very, very true montybaber, lol.....it wasn't meant how it read.
 
DGClarke: my apologies for sounding rude, but you don't come across as confident enough to be doing this job. if you are tripping up at these hurdles then perhaps you might be biting off a bit more than you can chew

i know it would be hard to not get offended, but a full rewire is serious stuff and should be done by a competent person as throughout you will be the duty holder, you don't come across as sure of yourself, or what you are doing

again apologies if you are offended
 
i personally think he sounds like he's gonna be ok. he's just got a few questions about his new installation, that he obviously wants doing properly first time round.

competance is a fine line in reality, have a go harry down the road wouldnt even come on a site llike this and ask questions, he would lash his cables in, keep the existing upstairs lighting feed and probably not use grommets and also not inform labc.
i would recommend if not allready purchased that he maybe gets a copy of 17th osg just so he's got a good reference point. electrics half the time is just common sense, and generally just 3 wires, and the odd sw/wire.

good luck with the job matey, sure you'll be fine
 
Guys

Thanks for all your replies, I do appreciate it. I now have to persuade my son-in-law to do it my way (not easy).

Can someone clarify a point for me? What is "cpc"? It is obviously a term for the unsheathed earth wire (hence the g/y sleeving), but what do the letters stand for?.

I was going to ask ONE more question, but I think JohnnyB has already answered it.

Obviously all lights are RCD protected as are the rings, but I take it that the correct arrangement is for the downstairs ring and upstaris lights to share an RCD and vice versa.

This makes sense to me, so If I have a ring trip out I still have lights

You are all stars - thanks

UKSEL

I am NOT offended, but anyway thanks for being so diplomatic.

I have no concerns at ALL about doing this work. I have a degree in electronics, so the "electrical" aspects of this are NOT a problem. What is a problem is the REGULATIONS. I want to be sure that when we apply for an inspection it's going to pass.

I don't want to trip up on some tiny regulation that I didn't know about. This is why I was asking about running singles in conduit, and what the position was regarding old, but apparently servicable cable.

I understand why you posted though, and you can be forgiven for thinking that perhaps I'm not up to the task.

Maybe I'll take Sparkyork's advice and get a copy of the 16th edition doc

Sorry meant to say 17th edition obviously
 
Last edited by a moderator:
I hope you don’t live near me- building control won’t let anyone without 2391 do anything. I just had a chat over the phone to them today- there so helpful!
 
Guys

Thanks for all your replies, I do appreciate it. I now have to persuade my son-in-law to do it my way (not easy).

Can someone clarify a point for me? What is "cpc"? It is obviously a term for the unsheathed earth wire (hence the g/y sleeving), but what do the letters stand for?.

I was going to ask ONE more question, but I think JohnnyB has already answered it.

Obviously all lights are RCD protected as are the rings, but I take it that the correct arrangement is for the downstairs ring and upstaris lights to share an RCD and vice versa.

This makes sense to me, so If I have a ring trip out I still have lights

You are all stars - thanks

UKSEL

I am NOT offended, but anyway thanks for being so diplomatic.

I have no concerns at ALL about doing this work. I have a degree in electronics, so the "electrical" aspects of this are NOT a problem. What is a problem is the REGULATIONS. I want to be sure that when we apply for an inspection it's going to pass.

I don't want to trip up on some tiny regulation that I didn't know about. This is why I was asking about running singles in conduit, and what the position was regarding old, but apparently servicable cable.

I understand why you posted though, and you can be forgiven for thinking that perhaps I'm not up to the task.

Maybe I'll take Sparkyork's advice and get a copy of the 16th edition doc

Sorry meant to say 17th edition obviously

Dave

CPC = Circuit Protective Conductor. And you are correct regarding the RCD situation.

Warren
 
Hey guys, we've just performed the insulation test on the upstairs ring, and I'm certain we're just fine. The megger turned in a reading of about 2 Giga Ohms (2000 MOhms). The cable was separated from the consumer unit at the time of the test, and I was wondering if we ought to be performing the test with the wires connected and the MCB open.

Just for the record, what do the regs say? What is the lowest resistance that is acceptable?
 

Reply to Use an old cable for lighting circuit? in the Australia area at ElectriciansForums.net

Similar Threads

I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Hi all, I have a light in the under stairs cupboard which is controlled by a switch in the hall. The under stairs cupboard is being taken...
Replies
4
Views
1K
We are currently renovating an old house after recently moving in. Whilst purchasing the property we received written assurances that the original...
Replies
47
Views
5K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock