Class 0 and 01 )
Class 0 and 01 Equipment is Allowed Only in VERY Specific Locations .
Such Equipment should NOT be Used in Normal Commercial . Industrial or Domestic Environment .for Completeness, an Explanation of these Two Types of Appliance is Included below .
Class 0 Equipment
Class 0 item of Equipment has Protection against Electric Shock that RELIES upon BASIC INSULATION Only. There is No Supplementary or Reinforced Insulation . There is ↔ No Provision for the Connection of Accessible Conductive Parts ↔ if any . to the Protective Conductor in the Fixed Wiring of the Installation . in the Event of FAILER of the BASIC Insulation Reliance is Placed Upon the Environment in which the Equipment is Installed . An Example of Class 0 Equipment is Certain Older Style Mains Powered Series-Connected Christmas Tree Lights where the Lights are Interconnected by a Bell Flex Type Cable ( Insulated but not Sheathed )
Class 01 Equipment
Class 01 item of Equipment has at Least Basic Insulation throughout . the Equipment is Provided with an EARTHING TERMINAL
The Equipment has a Power Supply Cord without a Protective Earthing Conductor . The Equipment is Fitted with a Pug without an Earthing Contact , which Cannot be Introduced into a Socket-Outlet with an Earthing Contact
Class 01 Equipment is Specialist Equipment and NOT for Common USE .
* ‘cable trunking’ means a manufactured enclosure for the protection of cables, normally of rectangular cross section,
* ‘circuit breaker’ means a mechanical switching device capable of making, carrying and breaking currents under normal circuit conditions and also of making, carrying for a specified time, and breaking currents under specified abnormal circuit conditions, such as those of short circuit.
* ‘circuit protective conductor’ means a protective conductor connecting exposed conductive parts of equipment to the main earthing terminal.
* ‘connector’ means a device which is provided with female contacts and is intended to be attached to the flexible cable connected to the supply.
* ‘danger’ means a risk of bodily injury or loss of life or health from shock, burn, asphyxiation or other causes.
* ‘duct’ means a closed passage way formed underground or in a structure and intended to receive one or more cables which may be drawn in.
* ‘earth electrode resistance’ means the resistance of an earth electrode to earth.
‘earth fault loop impedance’ means the impedance of the earth fault current loop (phase to earth loop) starting and ending at the point of earth fault.
* ‘earthed’ means connected to the general mass of earth in such a manner as will ensure at all times an immediate discharge of electrical energy without danger; when applied to electrical equipment, all phases short-circuited and effectively connected to earth.
* ‘earthing conductor’ means a protective conductor connecting a main earthing terminal of an installation to an earth electrode or to other means of earthing.
* ‘enclosure’ means a part providing an appropriate degree of protection of equipment against certain external influences and a defined degree of protection against contact with live parts from any direction.
* ‘equipment’ means electrical equipment. ‘equipotential bonding’ means electrical connection putting various exposed conductive parts and extraneous conductive parts at a substantially equal potential.
( 17th Edition ↔ Main Protective Bonding Conductor ↔ Old 16th Edition equipotential bonding’ ) if you are Not Sure Look up p/32 Regs
‘extra low voltage’ means voltage normally not exceeding 50Vroot mean square alternating current or 120V direct current, between conductors or between a conductor and earth. ( Regs p/31 )
* ‘fault protection’ means protection against dangers that may arise from indirect contact with live parts of the installation (contact with an exposed conductive part that is not normally live but has become live under fault conditions).
* ‘high voltage’ means voltage normally exceeding low voltage. ‘H.V. enclosure’ means a substation, standby generator house, distribution centre and a room or other enclosure wherein high voltage apparatus is installed. “Danger” notice shall be permanently affixed outside H.V. enclosure access doors.
* ‘installation’ means electrical installation.
* ‘live’ means electrically charged.
* ‘live work’ means electrical work on or near any live conductor. This is anywhere a worker is exposed to energised conductors, terminals, busbars or contacts.
* ( Regs Part 1 p/12 ) ↔ ‘low voltage’ means voltage normally exceeding extra low voltage but normally not exceeding: between conductors, 1000V root mean square alternating current or 1500V direct current, or between a conductor and earth, 600V root mean square alternating current or 900V direct current. ( Regs / Part 2 /Definitions ↔ p-31 ) **** ( Frequencies 50Hz , 60Hz , 400Hz ) -&-s
* ‘overhead line’ is defined in the Electricity (Wiring) Regulations as a conductor that is placed above ground and is suspended in the open air.
* ‘PELV (Protective Extra-Low Voltage)’ means an extra-low voltage system which is not electrically separated from earth, but which otherwise satisfies all the requirements for SELV.
* ‘permit-to-work’ means an official form signed and issued by a responsible person to a person having the permission of the responsible person in charge of work to be carried out on any earthed electrical equipment for the purpose of making known to such person exactly what electrical equipment is dead, isolated from all live conductors, has been discharged, is connected to earth, and on which it is safe to work.
* ‘powertrack system’ means an assembly of system components including a generally linear assembly of spaced and supported busbars by which accessories may be connected to an electrical supply at one or more points(pre-determined or otherwise) along the powertrack.
* ‘protective conductor’ means a conductor used for some measures of protection against electric shock and intended for connecting together any of the following parts :-
(i) exposed conductive parts,
(ii) extraneous conductive parts,
(iii) main earthing terminal,
(iv) earth electrode(s),
(v) the earthed point of the source, or an artificial neutral.
( Type of Protective Conductor : 543.2.1 . A Gas/Pipe ,an Oil/Pipe, Flexible or Pliable Conduit , Support/Wires or Other Flexible Metallic Parts , or Constructional Parts subject to Mechanical Stress in Normal Service , shall NOT be Selected as a Protective Conductor )
* ‘residual operating current’ means residual current which causes the residual current device to operate under specified conditions.
* ‘restrictive conductive location’ means a location comprised mainly of metallic or conductive surrounding parts, within which it is likely that a person will come into contact through a substantial portion of their body with the conductive surrounding parts and where the possibility of preventing this contact is limited.
* ‘rising mains’ means that part of the installation which is used for distribution of electricity throughout any building normally used for multiple occupation. ‘screen’ means an effective means of identifying or shielding the safe working area from a source of danger.
* ‘SELV’ (Separated Extra-Low Voltage) means an extra-low voltage which is electrically separated from earth and from other systems in such a way that single fault cannot give rise to the risk of electric shock.
* ‘short circuit current’ means an overcurrent resulting from a fault of negligible impedance between live conductors having a difference in potential under normal operating conditions.
* ‘socket outlet’ means a device, provided with female contacts, which is intended to be installed with the fixed wiring, and intended to receive a plug.
Take for example, wall-mounted socket-outlets and switches. They now have to be installed 450 to 1200 mm above the floor in dwellings, and 400 to 1400 mm in buildings other than dwellings. As such, they are far more visible than ever before, undergone a Part M makeover.
RCD - now ( virtually ) mandatory in homes.
Whilst residual current devices RCD have been in use for many years, the new 17th Edition requires electricians to consider the use of RCDs in many more applications than the current standard requires in order to improve building protection.
The basic function of an RCD is to trip and disconnect the supply of electricity in the event of an earth fault in order to prevent electric shock and fire risk. It does this by detecting the imbalance of currents between the live and neutral lines caused by a fault to earth. Drawing attention to the importance of using RCDs in the right context and with the right equipment, the IEE Wiring Regulations provides guidance on how RCDs should be incorporated in new builds.
30mA RCD protection for ALL sockets:
Additionally, all socket outlets rated at 20A or below within a domestic building will require 30mA RCD protection*. This means that all ring main circuits from consumer units will either need to be fed from the RCD side of a traditional split load board or have individual residual current breakers with overload ( RCBO ) ways.
Because the RCD is sensitive to current imbalances, it is not practical to fit just one device to protect an entire house. If a fault develops within one circuit, all circuits would be switched off immediately. By using individual and grouped RCD protected ways in combination with one another, the required protection can be provided whilst maintaining continuity of supply to other non-affected zones within the installation
Class 0 and 01 Equipment is Allowed Only in VERY Specific Locations .
Such Equipment should NOT be Used in Normal Commercial . Industrial or Domestic Environment .for Completeness, an Explanation of these Two Types of Appliance is Included below .
Class 0 Equipment
Class 0 item of Equipment has Protection against Electric Shock that RELIES upon BASIC INSULATION Only. There is No Supplementary or Reinforced Insulation . There is ↔ No Provision for the Connection of Accessible Conductive Parts ↔ if any . to the Protective Conductor in the Fixed Wiring of the Installation . in the Event of FAILER of the BASIC Insulation Reliance is Placed Upon the Environment in which the Equipment is Installed . An Example of Class 0 Equipment is Certain Older Style Mains Powered Series-Connected Christmas Tree Lights where the Lights are Interconnected by a Bell Flex Type Cable ( Insulated but not Sheathed )
Class 01 Equipment
Class 01 item of Equipment has at Least Basic Insulation throughout . the Equipment is Provided with an EARTHING TERMINAL
The Equipment has a Power Supply Cord without a Protective Earthing Conductor . The Equipment is Fitted with a Pug without an Earthing Contact , which Cannot be Introduced into a Socket-Outlet with an Earthing Contact
Class 01 Equipment is Specialist Equipment and NOT for Common USE .
* ‘cable trunking’ means a manufactured enclosure for the protection of cables, normally of rectangular cross section,
* ‘circuit breaker’ means a mechanical switching device capable of making, carrying and breaking currents under normal circuit conditions and also of making, carrying for a specified time, and breaking currents under specified abnormal circuit conditions, such as those of short circuit.
* ‘circuit protective conductor’ means a protective conductor connecting exposed conductive parts of equipment to the main earthing terminal.
* ‘connector’ means a device which is provided with female contacts and is intended to be attached to the flexible cable connected to the supply.
* ‘danger’ means a risk of bodily injury or loss of life or health from shock, burn, asphyxiation or other causes.
* ‘duct’ means a closed passage way formed underground or in a structure and intended to receive one or more cables which may be drawn in.
* ‘earth electrode resistance’ means the resistance of an earth electrode to earth.
‘earth fault loop impedance’ means the impedance of the earth fault current loop (phase to earth loop) starting and ending at the point of earth fault.
* ‘earthed’ means connected to the general mass of earth in such a manner as will ensure at all times an immediate discharge of electrical energy without danger; when applied to electrical equipment, all phases short-circuited and effectively connected to earth.
* ‘earthing conductor’ means a protective conductor connecting a main earthing terminal of an installation to an earth electrode or to other means of earthing.
* ‘enclosure’ means a part providing an appropriate degree of protection of equipment against certain external influences and a defined degree of protection against contact with live parts from any direction.
* ‘equipment’ means electrical equipment. ‘equipotential bonding’ means electrical connection putting various exposed conductive parts and extraneous conductive parts at a substantially equal potential.
( 17th Edition ↔ Main Protective Bonding Conductor ↔ Old 16th Edition equipotential bonding’ ) if you are Not Sure Look up p/32 Regs
‘extra low voltage’ means voltage normally not exceeding 50Vroot mean square alternating current or 120V direct current, between conductors or between a conductor and earth. ( Regs p/31 )
* ‘fault protection’ means protection against dangers that may arise from indirect contact with live parts of the installation (contact with an exposed conductive part that is not normally live but has become live under fault conditions).
* ‘high voltage’ means voltage normally exceeding low voltage. ‘H.V. enclosure’ means a substation, standby generator house, distribution centre and a room or other enclosure wherein high voltage apparatus is installed. “Danger” notice shall be permanently affixed outside H.V. enclosure access doors.
* ‘installation’ means electrical installation.
* ‘live’ means electrically charged.
* ‘live work’ means electrical work on or near any live conductor. This is anywhere a worker is exposed to energised conductors, terminals, busbars or contacts.
* ( Regs Part 1 p/12 ) ↔ ‘low voltage’ means voltage normally exceeding extra low voltage but normally not exceeding: between conductors, 1000V root mean square alternating current or 1500V direct current, or between a conductor and earth, 600V root mean square alternating current or 900V direct current. ( Regs / Part 2 /Definitions ↔ p-31 ) **** ( Frequencies 50Hz , 60Hz , 400Hz ) -&-s
* ‘overhead line’ is defined in the Electricity (Wiring) Regulations as a conductor that is placed above ground and is suspended in the open air.
* ‘PELV (Protective Extra-Low Voltage)’ means an extra-low voltage system which is not electrically separated from earth, but which otherwise satisfies all the requirements for SELV.
* ‘permit-to-work’ means an official form signed and issued by a responsible person to a person having the permission of the responsible person in charge of work to be carried out on any earthed electrical equipment for the purpose of making known to such person exactly what electrical equipment is dead, isolated from all live conductors, has been discharged, is connected to earth, and on which it is safe to work.
* ‘powertrack system’ means an assembly of system components including a generally linear assembly of spaced and supported busbars by which accessories may be connected to an electrical supply at one or more points(pre-determined or otherwise) along the powertrack.
* ‘protective conductor’ means a conductor used for some measures of protection against electric shock and intended for connecting together any of the following parts :-
(i) exposed conductive parts,
(ii) extraneous conductive parts,
(iii) main earthing terminal,
(iv) earth electrode(s),
(v) the earthed point of the source, or an artificial neutral.
( Type of Protective Conductor : 543.2.1 . A Gas/Pipe ,an Oil/Pipe, Flexible or Pliable Conduit , Support/Wires or Other Flexible Metallic Parts , or Constructional Parts subject to Mechanical Stress in Normal Service , shall NOT be Selected as a Protective Conductor )
* ‘residual operating current’ means residual current which causes the residual current device to operate under specified conditions.
* ‘restrictive conductive location’ means a location comprised mainly of metallic or conductive surrounding parts, within which it is likely that a person will come into contact through a substantial portion of their body with the conductive surrounding parts and where the possibility of preventing this contact is limited.
* ‘rising mains’ means that part of the installation which is used for distribution of electricity throughout any building normally used for multiple occupation. ‘screen’ means an effective means of identifying or shielding the safe working area from a source of danger.
* ‘SELV’ (Separated Extra-Low Voltage) means an extra-low voltage which is electrically separated from earth and from other systems in such a way that single fault cannot give rise to the risk of electric shock.
* ‘short circuit current’ means an overcurrent resulting from a fault of negligible impedance between live conductors having a difference in potential under normal operating conditions.
* ‘socket outlet’ means a device, provided with female contacts, which is intended to be installed with the fixed wiring, and intended to receive a plug.
Take for example, wall-mounted socket-outlets and switches. They now have to be installed 450 to 1200 mm above the floor in dwellings, and 400 to 1400 mm in buildings other than dwellings. As such, they are far more visible than ever before, undergone a Part M makeover.
RCD - now ( virtually ) mandatory in homes.
Whilst residual current devices RCD have been in use for many years, the new 17th Edition requires electricians to consider the use of RCDs in many more applications than the current standard requires in order to improve building protection.
The basic function of an RCD is to trip and disconnect the supply of electricity in the event of an earth fault in order to prevent electric shock and fire risk. It does this by detecting the imbalance of currents between the live and neutral lines caused by a fault to earth. Drawing attention to the importance of using RCDs in the right context and with the right equipment, the IEE Wiring Regulations provides guidance on how RCDs should be incorporated in new builds.
30mA RCD protection for ALL sockets:
Additionally, all socket outlets rated at 20A or below within a domestic building will require 30mA RCD protection*. This means that all ring main circuits from consumer units will either need to be fed from the RCD side of a traditional split load board or have individual residual current breakers with overload ( RCBO ) ways.
Because the RCD is sensitive to current imbalances, it is not practical to fit just one device to protect an entire house. If a fault develops within one circuit, all circuits would be switched off immediately. By using individual and grouped RCD protected ways in combination with one another, the required protection can be provided whilst maintaining continuity of supply to other non-affected zones within the installation