● “ Continuity of Protective Conductors “ ( Dead Test ) ( Guides Note -3 ) GN-3

Instrument , Continuity Tester ( Set on Low Ohms Scale )
( Multimeter can be Used to Measure the Voltage between two Positions )

612.2.1 No Load Voltage between 4 / 24V
Short Circuit Current of not Less than 200mA ( Ia Ief )

Earth Loop Impedance Test to Verify Continuity ( Measures Résistance of Conductors’ )

● “ Continuity Ring Final Circuit Conductors “ ( Dead Test )

Instrument , Continuity Tester ( ( Set on Low Ohms Scale )

612.2.2 No Load Voltage between 4 / 24V
Short Circuit Current of not Less than 200mA ( Ia Ief )

(1) Test is Undertaken to Ensure that all Conductors of the Ring Final Circuit are Continuous ,
(2) Conductors’ have Not been Bridged Creating Multiple Loops ,
(3) That all Connections are Electrically and Mechanically Sound ,

Step 1 , Isolated and Disconnected from The Supply

Step 2 , Phase & Neutral Conductors are Now Cross Connected so that the Outward Leg of the Phase Connects to the
Neutral and the inward Leg of the Phase Connects to the Outward Leg of the Neutral
Readings are Now taken between Phase and Neutral at each Socket
Readings at each Socket Outlet should be within 0.05Ω of each Other
(i) Failure to be within this Limit would Highlight Loose Terminations
(ii) Significant Increase at a Socket would Indicate that it is a Spur , Bridges within the Circuit would be Indicated by a
Gradual Decrease on the Return Leg

Step 3 , Phase & CPC Loops are now Interconnected so that the Outward Leg of the CPC Connects to the inward Leg
Of the Phase and the inward Leg of the CPC Connects to the Outward Leg of the Phase ,

(iii) Measured Value may be Recorded as ( R1 + R2 )

● “ Polarity “ ( Dead Test )

Instrument , Continuity Tester ( Set on Low Ohms Scale )

612.6 No Load Voltage between 4 / 24V
Short Circuit Current of not Less than 200mA ( Ia Ief )

It must be Confirmed by Test , Every Fuse and Single-Pole Control and Protective Device is Connected in the Line Conductor Only ,
612.6 (ii)
Contact Bayonet and Edison Screw Lampholder(s) have the Outer or Screwed Contacts Connected to the Neutral ,
The Phase Conductor is Connected to the Centre Termination of an Edison Screw Lampholder Only , ←←

612.6 (iii)
Wiring has been Correctly Connected to Socket-Outlets and Similar Accessories ,

(i) All Sockets Polarities’ are Correct ,
(ii) That the Polarity of the Incoming Supply is Correct / Before the Supply is Energised ,
Your Checking to Ensure the Supply Authorities Polarity is Correct ,

Acceptable to Place a Temporary Bridge Between Phase & Earth in the Consumers Unit ,

(i) Test between Switched Live & Earth at the Ceiling Rose to Confirm Polarity
(ii) Operate Switch to Confirm Polarity
(iii) HSE Guidance Note GS-38 ↔ Electrical Equipment
→ You Should always Prove Isolation ← (iv) Use a Proving Unit
Then Test for Circuit is Dead , then Prove GS-38 it still Works
(v) Once the Supply is Energised Correct Polarity of the Incoming Supply may be Established Using An Approved
Approved Voltage Tester at the Mains , ( after Proving that GS-38 Voltage Indicator is Working )

(vi) Remember to Remove your Temp link , Phase & Earth

Once the Inspection & Testing has been Completed it is then of Vital Importance that the Relevant Documentation is Completed
Three Signatures’ are Required on the Electrical Installation Certificate , ( Three Signatures are still Required )

(i) Designer (ii) Installer (iii) Tester

Appendix 6 , (ix) When making Out and Signing a Form on behalf of a Company or Other Business Entity ,
Individuals should State ( for Whom they are Acting ) 632.3

Electrical Installation Certificate ,
To be Used When One Person is Responsible for the Design , Construction , Inspection & Testing of an Installation

Electrical Installation Certificate
This Certificate is Intended to be Issued Only for a New Electrical Installation or for New Work Associated with an
Addition or Alteration to an Existing Installation ,
It should Not have been Issued for the Inspection of an Existing Electrical Installation , A “ Periodic Inspection Report “
Should be Issue for such an Inspection ,

There are Three Main Reasons why we Certificate an Installation ,
(i) Addition to an Installation (ii ) an Alteration to an Installation (iii) New Installation

Which Certificate is Issued the Original should be Given to the Person Ordering the Work and a Duplicate by the Contractor , 632.1

Particular Care should be Given when Completing the Extent and Limitations Details of Periodic and Close Liaison ,
With the Client , is Essential at this Time , This is to Ensure that the Client is Fully Informed of what will and what Not be Tested ,
( All must be Negotiated with the Client )

631.2 Upon Completion of the Periodic Inspection & Testing of an Existing Instillation ,
Periodic Inspection Report , Shall be Provided , such Documentation shall Include Details of the Extent of the Installation & Limitations
Of the Inspection & Testing Covered by the Report , Together with a Record of the Inspection and the Results of Testing ,

621.4
The Extent and Results of the Periodic Inspection & Testing of an Installation , or any Part of an Installation , shall be Recorded ,

Person Ordering the Work : Periodic (i) First Periodic Test – Designer / Installer
(ii) Further Periodic Test – Tester / Inspector
(iii) Extent & Limitations Agreed with / Person Ordering The Work ,

Periodic Inspection Report
Notes , (5 ) p-339
The Extent and Limitations “ Box should fully Identify the Elements of the Installation that are Covered by the Report and
Those that are Not this Aspect having been Agreed with the Client and Other Interested Parties before the
The Inspection & Testing is Carried Out ,

The “ Extent and Limitations “ Box should fully Identify the Extent of the Installation Covered by this Report and any Limitations on the Inspection & Tests the Contractor should have Agreed these Aspects with you and any Other
Interested Parties ( Licensing Authority , Insurance Company , Building Society etc , before the Inspection was Carried Out

4118.3
Where a Circuit-breaker is Used the Maximum Value of Earth Fault Loop Impedance ( Zs ) shall be Determined by the
Formula in Regulation 411.4.5 Alternatively , the Values Specified in Table 41.4 may be Used instead of Calculations
For the Nominal Voltages ( Uo ) and the Types and Ratings of Overcurrent Device listed therein ,

What is the Maximum Earth Fault Loop Impedance Allowed when Using a 32A Type C
Circuit Breaker Giving s Disconnection time of 5sec , the Nominal Voltage to Earth ( Uo ) is 55v ↔ 41.6 ( 0.17Ω )



PS is this Helping anybody Please let me Know ,
When I don’t hear anything My Computer does Hand Stands , Amberleaf :D
Keep at it Chaps there’s always tomorrow ,

The On Site Guide & Guidance Note 3 :D

Contain Detailed Information on how to Carry Out a Series of Electrical Tests on an Installation ,
612.2.1 Continuity of Protective Conductors ( Dead Test ) GN- 3
612.2.2 Continuity of Ring Final Circuit Conductors’ ( Dead Test ) GN- 3
612.3. Insulation Résistance ( Dead Test ) GN- 3
612.6 Polarity ( Dead Test ) GN- 3 By Continuity Methods
612.7 Earth Electrode Résistance ( Dead Test ) GN- 3 Battery ,

612.9 Earth Fault Loop Impedance ( Energized ) GN- 3
612.11 Prospective Fault Current ( Energized ) GN- 3
612.13. Functional Testing ( Energized ) GN- 3

In Addition to an Inspection these Test form the Basis of any Electrical Commissioning Process of an Electrical Installation ,

There are Two Main Types of Test / Commissioning Undertaken there are Initial Testing ,
And Periodic Testing , as the Name Suggests Initial Testing is Undertaken to Ensure the Installation is Safe and in Compliance with BS-7671 Prior to being Handed Over to the Client ,

Whilst a Periodic “ Report “ is Undertaken at Regular Intervals whilst the Installation is in Service to Ensure the Installation
Remains Safe and Fit for Use ,

The Sequence of Electrical Tests Undertaken Differs Slightly Between the Two ,
 
Last edited by a moderator:
RCD is Provided for Supplementary Protection Against Direct Contact its Operating Current must Not Exceed 30mA
( Must Operate in the Time Not Exceed 40mS at Residual Current of x5 its Rated Current )

Additional Protection RCD ( 612.10
The Verification of the Effectiveness of the Measures Applied for Additional Protection is Fulfilled by Visual Inspection & Test
Where RCDs are Required for Additional Protection the Effectiveness of Automatic Disconnection of Supple by RCDs shall
Be Verified Using Suitable Test Equipment According to BS-EN 61557-6 to Confirm that the Relevant Requirements’ are Met ,

612.1
The Tests of Regulations 612.2 / 612.13 Where Relevant , shall be Carried Out and the Results Compared with Relevant Criteria

30mA RCD

Test Button to Select 30mA

Half Current ( 15mA ) Test , 0º ≈ Positive Half Cycle ( RDC should Not Trip ) ½
Half Current ( 15mA ) Test , 180º Negative Half Cycle ( RDC should Not Trip )

Full Current ( 30mA ) Test , 0º ≈ Positive Half Cycle ( RDC should Trip ) x1 40mS
Full Current ( 30mA ) Test , 180º Negative Half Cycle ( RDC should Trip )

Five times Current ( 150mA ) Test , 0º ≈ Positive Half Cycle ( RDC should Trip ) x5
Five times Current ( 150mA ) Test , 180º Negative Half Cycle ( RDC should Trip )

100mA RCD 0º or ( Positive ) 180º ( Negative )

Test Button to Select 100mA

Half Current ( 50mA ) Test , 0º ≈ Positive Half Cycle ( RDC should Not Trip ) ½
Half Current ( 50mA ) Test , 180º Negative Half Cycle ( RDC should Not Trip )
Full Current ( 100mA ) Test , 0º ≈ Positive Half Cycle ( RDC should Trip ) x1
Full Current ( 100mA ) Test , 180º Negative Half Cycle ( RDC should Trip ) RCDs Remember L to E fault

Note that the Five Times Current Test is Not Required for a 100mA RCD

State Four Items of Electrical Equipment that would Require Functional Testing
( Functional Checks ) 612.13
(i) RCDs
(ii) Circuit Breakers
(iii) Isolators’
(iv) Cooker , Switches

Devices Used for Isolation , Switching for Mechanical Maintenance , Emergency Switching & Functional Switching , T/ 53-2 p-117
PS , Breakers can Now be Used as Primarily as Switches’ ,

Domestic Electricians read up on your ( TT Systems ) Uncle Sam is Watching

If Any Test Indicates a Failure to Comply , that Test and any Preceding Test , the Results of which may have been Influenced
By the Fault Indicated , shall be Repeated after the Fault has been Rectified ,

The Tests of Regulations 612.2 Continuity of Conductors to 612.6 where relevant , shall be Carried Out in the Order before the Installation is Energised , Where the Installation Incorporates an Earth-Electrode ,
the Test of Regulations 612.7 Shall also be Carried Out Before the Installation is Energised , GN-3 ( TT Systems ) or

Some Methods of Test are Describe in IEE Guidance Note 3 Inspection & Testing ,
Other Methods Are Not Precluded Provided they give Valid Results ↔ it is in the Regs , 2008 17th p-157

The Tests of Regulations 612.2 Continuity of Conductors to 612.6 where relevant , shall be Carried Out in the Order before the Installation is Energised , Where the Installation Incorporates an Earth-Electrode ,
the Test of Regulations 612.7 Shall also be Carried Out Before the Installation is Energised , GN-3 ( TT Systems ) or

Note that the Five Times Current Test is Not Required for a 100mA RCD

State the Action to be Taken Regarding the Earthing Conductor Before Measuring the Résistance of an Earth Electrode
GN-3 ( Earth Electrode Testing )
(i) DO NOT DISCONNECT any Protective Conductors BEFORE Isolating the Supply ←←← think about this One
(ii) Disconnect Earthing Conductor at ( MET ) ↔ Link in D/B , to Avoid Parallel Earth Paths

State Two Reasons why it is Necessary to Measure External Earth Fault Loop Impedance at the Origin of an Installation ,
GN-3 ( Determining Ze )
(i) To Verify an Earth Connection
(ii) The Value is Equal to or Less than the Value Determined by the Designer ,

State the Test Voltage and Minimum Acceptable Value of Insulation Résistance for the Following Circuits ;)
(i) 400v 3 Phase Motor ( 500v dc 1.0MΩ )
(ii) 760v Discharge Lighting Circuit ( 1000v dc 1.0MΩ )
(iii) 45v FELV Circuit ( 250v dc 0.5MΩ

Identify one other Test that is Automatically Preformed when undertaking a Ring Circuit Test
GN-3 ( Continuity of the Ring Final Circuit ) 612.2.2
Polarity , 612.2

Identify the Test that should be Applied to Verify Polarity after the Supply is Energised ,
GN-3 ( Polarity )
Test to Verify Correct Polarity of the Incoming Live Supply , ( Test Made at the Origin Using Approved Voltage Indictor GS-38 )

State the Correct Sequence for Under taking an Insulation Résistance Test florescent Light
Circuit Containing two-way Switching
GN-3 ( Insulation Résistance Testing )
(1) Supply Must be Isolated ( Dead Test )
(2) All Lamps Removed
(3) Insulation Résistance Test between Line Conductors and Neutral
(4) Insulation Résistance Test between Line Conductors and CPC
(5) Two-Way Switches’ Operated During Test ,

State items of Equipment / Components that may Need to be Removed prior to Carrying out a Test for Insulation Résistance
On a Circuit 612.3
GN-3 ( Insulation Résistance )
Pilot or Indicator Lamps
Dimmer Switches
Touch switches

Under what Circumstances would it be Appropriate to Issue a Single Signature Electrical Installation Certificate
GN-3 ( Certificates )
Where Design , Construction Inspection and Testing is the Responsibility of One Person ( in the Regs ,

State the Necessary Action that should be taken by an Inspector on Discovering a Damage Socket-Outlet
With Exposed Live Parts During a Periodic Inspection & Test
GN-3 ( Required Competence )
Make an Immediate Recommendation to the Client to Isolate the Defective Part

State the Formula Used to Calculate Impedance ( Zs ) at the Furthest Point within a Circuit
GN-3 ( Earth Fault Loop Impedance ) 612.9
( Zs = Ze + R1 + R2 )
Where Ze is by Measurement or Enquiry
And ( R1 + R2 ) by Measurement ,

State the Maximum Recommended Value of Résistance for an Earth Electrode p-50 Note 2
GN-3 ( Earth Electrode for RCDs )
(i) Electrodes having Resistances’ in the Excess of 200Ω will Require Further Instigation , :eek: ↔ “ Houston we have a problem “
(ii) Note , Electrodes Resistances Obtained in Excess of 200Ω May Indicate Unstable Soil Conditions

Formula for Estimating Energy Consumption :eek:
You can Use this Formula to Estimate an Appliances Energy Use ,

( Wattage x Hours Used per Day ÷ 1000 = Daily Kilowatt-Hour ( kWh ) Consumption .
( 1 kilowatt ( kW ) = 1,000 Watts )

Multiply this by the Number of Days you Use the Appliance During the Year for the Annual Consumption ,
You can then Calculate the Annual Cost to Run an Appliance by Multiplying the ( kWh ) per Year by your
Local Utility’s Rate per Year by your Utility’s Rate per ( kWh ) Consumed ,

Note : To Estimate the Number of Hours that a Refrigerator Actually Operates at its Maximum Wattage ,
Divide the Total Time the Refrigerators’ is Plugged in by Three Refrigerators’, Although “on” all the Time ,
Actually Cycle On and Off as Needed to Maintain Interior Temperatures ,

Window Fan ,
( 200 Watts x 4 Hours / Day x 120 Days / Year ) ÷ 1000
= 96 ( kWh ) x 8.5 % / ( kWh ) £ 8.16 Year - ( 200 x 4 x 120 Div 1000 ( 96 x 8.5 = 8.16 )

Computer / Monitor
( 120 + 150 Watts x 4 Hours / Day x 365 / Year ÷ 1000
= 394 ( kWh ) x 8.5 % / ( kWh )
= £ 33.51 / Year


Standard Light Bulb 4 Hour a Day 100 Watt £ 14.60 per Year
Low Energy Light Bulb 4 Hour a Day 18 Watt £ 2.63

Aquarium = 50 – 1210 Watts
Clock Radio 10
Personal Computers ( CUP / Awake / Asleep = 120 / 30 or Less
Monitor – Awake / Asleep = 150 / 30 or Less
Laptop – 50
Refrigerator ( Frost Free , 16 cubic feet ) = 725

Cost per year
This I hope this will Help you Lionel ,
 
Last edited by a moderator:
17th BS-7671 : 2008 ♫ ♫ ♫ Old to New
GN3
The Requirement for 40mS at a Residual Current of x5 Operating Current comes from Regulation 415.1.1 when the RCD is used

The Use of RCDs with a Rated Residual Operating Current , Not Exceeding 30mA and Operating Time Not Exceeding 40mS
Residual Current x5 is Recognised In a.c Systems as Additional Protection ,
( Provision for Basic Protection / Provision for Fault Protection ) Right One ,

Protection Against Electric Shock ( Chapter 41 p-44 17th

16th BS-7671 2001: ←←←
They are Still a lot of Old Notes and Stuff from the Internet , :(

( i) Protection in Use Without A Fault ( Now Designated Basic Protection Was Referred to as Protection Against ( Direct Contact
(ii) Protection Under Fault Conditions ( Now Designated Fault Protection Was Referred to as Protection Against ( Indirect Contact

PS , Supplementary Protective Bonding Conductors’ is Complementary Measure for “ Fault Protection “

Functional Testing 612.13 / RCD Testing Detail a “ Quarterly Test “ , Regulation 514.12.2 Domestic Electricians

MCB's to BS EN 60898 RCBOs to 61009-1 for disconnection times of 0.4 & 5 sec

411.3.2.2 the Maximum Disconnection time Sated Table 41.1
( Shall be Applied to FINAL RING CIRUITS NOT EXCEEDING 32Amps TN-systems 0.4 sec ONLY ) ;)

411.3.2.3
In A TN-System , a Disconnection time ( 5sec Final Ring Circuits EXCEEDING 32Amps ONLY ) ;)

The Maximum Disconnection Time TN-Systems ( 230v to Earth 0.2 sec Only ) ;)

Remember to Keep You ( Earth Impedance Ω Zs Very Very Low ) :eek:

Protection Against Electric Shock ,
( That Live Parts , Such as Energized Conductors , Must Not be Accessible )
( The Conductive Parts which are Accessible , Such as Metal Enclosures of Equipment or Metal Pipes , Must Not be Live )
Must be Achieved both in Normal Conditions ( No Faults on Electrical Systems )

(i) By Touching Live Parts at Different Potential , Max , Touch Voltage of 50 Volts
(ii) A Live Part and Earth Potential ,

● Standards Documents , BS / British Standards ( EN / European Standards ( ISO / Worldwide British Standards ,

For the Apprentice , :eek:

( Moulded-Plug ) a Non-wiriable Plug , the Manufacture of Which is Completed by Insulating Material Moulded Pre-Assembled
Component Parts and the Terminations of Flexible Cord ,
( Fuse Plug ) a Plug having Provision for a Replaceable Cartridge Fuse Link ,

Terminal , a Means by which the User can Make an Electrical Connection between the Appropriate Flexible Cord and the
Conducting Parts of the Plug Without the Use of Special Purpose Tools ,

( Screw-Type-Terminal )
A Terminal in Which the Connection is Made Direly by Means of Screws or Nuts of any Kind or Indirectly through an
Intermediate Metal Part such as a Washer , Clamping Plate or Anti-Spread Device on Which the Screw Bears Directly ,

Example of Screw-Type Terminals ,
A Pillar Terminal is a Terminal in which the Conductor is Inserted into a Hole or Cavity ,
Where it is Clamped Under the Shank of the Screw or Screws ,

A Screw Terminal is a Terminal in Which the Conductor is Clamped Under the Head of the Screw ,

A Screw Terminal is a Terminal in Which the Conductor is Clamped Under a Nut ,

( Clamp-Type ) Screwless Terminal ,
A Terminal in Which the Connection is Made by Clamping the Conductor of Flexible Cord between two Metallic Surfaces
Without the Use of a Screw ,

( Fuse Carrier ) A Movable or Removable Part Designed to Carry , Retain , Cover and / or Remove the Fuse Link ,

Classification ,
(i) Rewirable or Non- Rewirable
(ii) For Normal Use or Rough Use ,
(iii) Fitted with Screw or Clamp Type ( Screwless ) Terminals ,

(i) for Screw Type Terminals the Clamping Screw Shall be Tightened with Torque to Two-Thirds of the Appropriate Value ,
(ii) for Clamp-Type ( Screwless ) Terminals the Connection shall be Made in Accordance with the Manufacturers Instructions ,

The Résistance between the Earthing Terminal or Termination and any Other Nominated Metal Part shall Not Exceed 0.05Ω

“ Fundamental Principles “ :D

Protection for Safety 131.

Fundamental Reason for Inspecting & Testing an Electrical Installation is to Determine Whether a New Installation is Safe To be Put into Service ,

Following Statements
(i) Installations Must be Inspected and Tested on Completion and also During Erection
(ii) The Purpose of the Inspection is to Verify Equipment is Correctly Selected and Erected in Accordance with BS-7671
(iii) Precautions shall be Taken to Avoid Damage to Property During Inspection & Testing 131.1

131.1
The Requirements of this Chapter are Intend to Provide for the Safety of Persons , and Property against Dangers & Damage
Which May arise in the Reasonable Use of Electrical Installations ,

Or Whether an Exciting Installation is Safe to Remain in Service Until the Next Inspection is Due ,
● If it is Verified that New Installation , Work fully Complies with the Current Requirements’ BS-7671 Standards ,
● All Equipment Must be Suitable for its Intended Use ,

Initial Verification Chapter 63 ( Inspection & Testing ) Construction Inspection and Testing of the Installation shall ,
Which takes Account of their Respective Responsibilities for the Safety of that Installation , 632.3 / 632.1

Visual Inspection is Necessary Before Testing to Check Whether ( There is Adequate Access to Switchgear ,

Any Faults or Defects Indentified During an Initial Verification should be ( Made Good before Issuing the Certificate ,

632.4
Defects or Omissions Revealed During Inspecting & Testing of the Installation Work

During Inspection of a Distribution Board Containing Exposed Conducive Parts it Should be Verified that ,
( The Door can Only be Opened with a Key or Tool , 416.2.4. (i) )

Before Commencing an Initial Inspection and Test , the Inspector should have Copy of the ( Inspection Specification ,
the Following should Accompany the Inspection and Test Certificate ( Copies of the Inspection & Test Schedules ,

Initial Verification
Is Intended to Ensure that the Electrical Installation is Safe to but into Service , and that it is Likely to Remain in Such a Condition at Least Until the First Periodic Inspection ,

Something to Read , :confused: :eek:

Electrical Contractors that Issue Inaccurate or Misleading Certificates or Reports
Are Liable to Criminal Prosecution by Trading Standards Officers
Under the Trade Descriptions Act 1968 or Other Relevant Legislation ,

The Term “ Inspector “ is Used to Describe a Person Responsible for Inspecting & Testing an Electrical Installation ,
All Persons Carrying Out the Inspecting & Testing of Electrical Installations Must be Competent to do So ,
This May come up in the Future ,

Safe Working Procedure ( Regulation 12 ) ;)
Means for Cutting of the Supply and for Isolation

611.1
Inspection shall Proceed Testing and Shall Normally be Done with that Part of the Installation under Inspection Disconnection from the Supply ,

Precautions for Work on Equipment Made Dead ( Regulation 13 )
Adequate Precautions shall be Taking to Prevent Electrical Equipment Which has been Made Dead
In Order to Prevent Danger while Work is Carried Out on or Near that Equipment becoming Live ,
( Electrician Must Carry Out Safe Isolation Procedure )

Open the Means of Isolation for the Circuit(s) to be Inspected

416.2.4
Where it is Necessary to Remove a Barrier or Open an Enclosure or Remove Parts of Enclosures
What you are Verifying at the Same Time ,
( Top of CU , IP4X 416.2.2 ( the Sides of the CU must Conform to IP2X 416.2.4 (ii)
( IP Rating for RCCBs / RCBOs / RCDs ( Front Plate is IP4X / Screw IP2X ( BS Finger Test )

Compliant with GS-38 with Regards to Test Leads
Prove the Correct Operation on a Suitable Voltage Test Instrument Against a Known Source

Test , with the GS-38 Voltage Test Instrument All Conductors of the circuit(s) you are Working on to Confirm that there’s No
Live Supply to the Equipment your Working On ,

Prove the Voltage Test Instrument Against the Know Source to Check that it was Functioning Correctly

Remember GN-38 Electrical Test Equipment / Test Equipment for Circuits with Rated Voltages Not Exceeding 650 Voltages

BS-EN 61010 GN-38
Equipment Included in Scope ,
This Part of IEC 61010 Specifies General Safety Requirements’ for Electrical Equipment Intended for Professional , Industrial Process ,
BS-EN 61557
Electrical Safety in Low-Voltage Distribution Systems up to 1000V a.c / 1500V d.c Equipment for Testing Measuring ,

Proving Unit for on Site-Testing and Verification of Electrical Test Equipment
Proving Unit Produces 690v AC / DC to Enable Voltage Indicators to be Checked
Unit is Suitable for Indicators with 230v / 415v ,
 
Last edited by a moderator:
Electrical Installation Certificate is to be Used Only for the Initial Certification of a New Installation , or of New Work
Associated with an Alteration or Addition to an Existing Installation , Carried out in Accordance with BS-7671

Electrical Installation Certificate
( Requirements for Electrical Installations BS-7671 IEE Wiring Regulations

Nature of Installation Work
● Three Boxes are Provided to Enable the Contractor to Identify the Nature of the Installation Work ( p-332 ) ,

● New / This box should be Ticked Only if the whole Installation has been Installed as New , or if a Complete Rewire is Carried Out ,

● An Addition ( to an Existing Installation ) this box should be Ticked if an Existing Installation has been Modified by the Addition of One or More New Circuits’ ,

● An Alteration ( to an Existing Installation ) this box should be Ticked where One or More Existing Circuits have been Modified or Extended , or Items such as Distribution Boards and Switchgear have been Replaced ,

Where Appropriate , both the “ Addition “ and the “ Alteration ” Boxes may be Ticked ,

There are Three Main Reasons why we Certificate an Installation ,
(i) Addition to an Installation (ii ) an Alteration to an Installation (iii) New Installation ,

Visual Inspection of a New Installation must be Carried out ,
During Erection and Before Testing ,

Requirement of the Inspection Checklist ,
Prescience of a BS Mark or Other Suitable Certification ,
Correct Selection of Cable and Protection Devices ,
No Visible Damage ,

Inspection Domestic Consumer Unit would Need Verification for ,
Identification of Conductors’ ,
Rating and Type of Protective Devices
Correct Connection of Single-Pole Devices

Domestic Electrical Installation Certificate Three pages , 3x1

Signatories :)
Two Options are Available for Certification of the Installation ( Domestic Electrician )
(i) Where the Design , the Construction and Inspection & Testing are the Responsibility of One Person ,

“ Electrical Installation Certificate “ Signatories

(ii) Collectively Certified in the Section Headed , p- 332 / p-333 ( When Three People are Needed )
(1) ( For Design ) (2) ( For Construction ) (3) ( For Inspection & Testing )
Alternatively , where Approved Contractor Issuing the Certificate has Not been Responsible for the Design
And / or the Inspection & Testing of the Electrical Work , Certification of the Three Signatories must be Carried Out
Separately using the Three “ Particulars of Signatories to the Electrical Installation Certificate Design “ Construction ” Inspection & Testing “ Respectively ,

17th New Regulations that all Socket-Outlets up to 20A , Used by Ordinary Persons need to be RCD Protected by a Device if
With a Maximum Tripping Current of 30mA ( 411.3.3 (i) , Additional Protection

Knowing the Earth Loop Impedance , it is Possible to Calculate the Value of the Prospective Fault Current ( PFC )
At any Point in an Installation to Ensure that all Installed Protective Devices are of Adequate Rating to Clear the Potential Fault
Current Level ,
The Earth Loop Impedance Test Measures the Résistance of the Path that a Fault Current would take between Line / Protective Earth
this Must be Low Enough to Allow Sufficient to Flow to Trip a Circuit Protection Device ,

100mA / 300mA RCDs are Really Protection Against Fire rather than Shock ,

Residual Current Device shall have a Rated Residual Operating Current ( I∆n ) not Exceeding 30mA and an Operating Time Not
Exceeding 40mS at Residual Current of 5 ( I∆n )

As Provided by BS-4293 ,
BS-7071: 1992 ( Specification for Portable Residual Current Device , Safety Plug 13A- Tripping Current 30mA / 10mA Tripping Time ( 30mS ) IP 44

Old ↔ RCD BS-7288 Protected Switched Socket-Outlet ( SRCDs : 1992 ) Red / Black :eek:
SRCDs Specification , Rated Current 13A , Rated Trip Current 30mA , Trip Time 30mS

New ↔ BS-7288
Power Breaker 2G RCD , Metal-Clad , Trips 40mS at 30mA Double-Pole ( BS-7288 , BS-1363 , BS-4293 , Passive Operation
Cross-References BS-1362 ( Domestic , Cartridge Fuses , p-229 ( BS-1363 Class I Equipment / 3 / 5 / 13Amp , p-229

1G DP RCD , ( Metal Clad )
For Use in Industrial and Domestic , 13A max Load Trips at 30mA - BS-7288 / 200mS

Tested According to Specification BS-7071:1992 and BS-1363 British Standards Institution

BS-EN 61008-1
BS-EN 61008-1 : 2004
If this comes up ( Old BS-4293 Withdrawn ) ↔ Now RCCBs , Residual Current Operated Circuit-Breaker , Remains Current , ( 41.5 ;)

BS-EN 61009-1
BS-EN 61009-1 : 2004
If this comes up ( Old BS-4293 Withdrawn ) ↔ Now RCBOs , Residual Current Operated Circuit-Breaker , Remains Current , ( 41.3 ;)
If this comes up ( Old BS-3871 Withdrawn ) ↔ Now BS-EN 60898 MCBs , 2003 Remains Current , ( 41.3 ;)
If this comes up ( Old BS-4293 ( Replaced by BS-EN 61008-1 , look in the Regs ,

For The Apprentices ,
Am trying to make it Easy for you to Understand , Amberleaf , :D

Domestic Electrical Installation Certificate ;)
Is Not Intended to be Issued to Confirm the Completion of the Contract ,

This Certificate is a Declaration of Electrical Safety which should be Issued before an Installation is Put into Service ,
Domestic Electrical Installation Certificate
Is to be Used Only for the Initial Certification of a New Installation ,
New Work Associated with an Alteration or Addition to an Existing Installation , Carried Out in Accordance with BS-7671

Certificate May Only be Used where Every One of the Following Conditions Apply ,

The Electrical Installation Work Relates to a Single Dwelling ( House or Individual Flat )

The Design , Construction , and the Inspection & Testing of the Electrical Installation work has been the Responsibility of One Person
Or Organization ,

The Installation Forms Part of a ( TT ) ( TN-S ) ( TN-C-S / PME - Systems ,
Each of which falls within the Scope of the Domestic Electrical Installation Certificate

The Protective Measure for Fault Protection is Provided Primarily by Automatic Disconnection of Supply ( ADS ) 415.1.1
Earthing & Protective Bonding Arrangements if Necessary for the Protective Measure Applied for Safety ,
131.8 Alteration or Additions to an Installation ,

Installation Work Falling within the Scope of the Domestic Electrical Installation Certificate ,
Contractor will Invariably have Assumed the Role of the Designer ,

This Certificate is a Declaration of Electrical Safety which should be Issued before an Installation is Put into Service ,
Domestic Electrical Installation Certificate
Is to be Used Only for the Initial Certification of a New Installation ,
New Work Associated with an Alteration or Addition to an Existing Installation , Carried Out in Accordance with BS-7671

RCD Test Instrument , Operating Time in Milliseconds when Subjected to a Test Current Equal to the Operating Current I∆n

Insulation Résistance Enter the Measured Values of Line / Line ( Only Applicable for Multi-Phase Circuit(s)

Insulation Résistance Line / Neutral Line / Earth Neutral / Earth

“ Inspection of New Installation Work “
BS-7671 Requires that Every Installation , and Every Alteration or Addition to an Installation ,
Is Inspected During Erection and on Completion Before being put into Service to Verify so far as is Reasonable Practicable ,

Initial Verification
It is a Requirement of BS-7671 that the Relevant Design Information is Made Available to those Carrying Out the Inspection & Testing of New Installation Work ,
Irrespective of whether the Design was Carried Out by the Contractor or by Another Party ,
610.2
The Results of the Assessment of the Fundamental Principles Section 131 , the General Characteristics Required by
Section 311 / 313 , together with the Information Required by Regulation 514.9.1 shall be Made Available to the Person(s)
Carrying Out the Inspection & Testing ,

Inspection
Verify , Comply with Appropriate British / European or Equivalent Product Standards , 133.1.1 / 133.1.2
Been Correctly Selected and Erected , Not Visibly Damaged , Defective or Deteriorated such that Safety is Impaired
Suitable for the Environment in which they are Installed

Chapter 41 Protection Against Electric Shock
Basic Protection – Means of Protection Against Electric Shock Under Fault-Free Conditions ,
Fault Protection – Means of Protection Against Electric Shock Under Single Fault Conditions ,

“ Protective Measure “ BS-7671 Must Consist of
(i) An Appropriate Combination of a Provision for Basic Protection and an Independent Provision for Fault Protection ,
(ii) An Enhanced Protective Provision which Provides both Basic and Fault Protection
 
Last edited by a moderator:
For the Apprentice ( this is all you need on BS-EN 61009-1 to help you understand something’s ) :rolleyes:
RCBOs BS-EN 61009-1 ( 41.3 )

● RCBOs ( Combined MCB / RCD ) Breaking Capacity ( kA ) BS-EN 61009-1 41.3
MCBs ( Breaking Capacity ( kA BS-EN 60898-1 ) 41.3

Devices are Intended to Protect People Against Indirect Contact ( Carelessness by Users )
Exposed Conductive Parts of the Installation being Connected to an Appropriate Earth Electrode and to Protect against Overcurrents
The Wiring Installations of Buildings and Similar Applications’ ,
May be Used to Provide Protection Against Fire-Hazards due to a Persistent Earth Fault Current ,

RCBOs
Having a Rated Residual Operating Current Not Exceeding ( 30mA ) 415.1.1
Also Used as a Means for Additional Protection in the Case of Failure of the Protective Means against Electric Shock ,

RCBO
6A / 30mA - 6kA type B
10A / 30mA - 6kA type B
16A / 30mA - 6kA type B
20A / 30mA - 6kA type B
25A / 30mA - 6kA type B
25A / 30mA - 6kA type B
32A / 30mA - 6kA type B
40A / 30mA - 6kA type B

RCBO
There are Important Differences when Using the Single-Pole RCBO most Commonly Used in the UK
( as Opposed to Two-Pole RCBOs Used in Europe )

With Single-Pole RCBOs Even when they have Tripped , the Neutral Wire is Not Interrupted so Operators may still Risk
Getting an Electric Shock ,

Two-Pole RCBOs Provide a Much Safer Solution as they Interrupt Both the Live & Neutral Wires ,

Primarily , the RCBO , a Residual Current Breaker with Overcurrent Protection , will Both Act as a Circuit-Breaker
And will Prevent Damage if there is an Overload Situation ,

For any Business or Operation , Safety is a Top Priority , a Two-Pole RCBO is the Circuit Breaker of Choice ,

Trip Current Settings , 30mA 100mA 300mA 500mA

Test Current Results
t∆ ½ I∆n RCBO Must Not Trip 0.5 / ½
t∆ x1 I∆n RCBO Must Trip Within 300mS ( BS-EN Only ←
t∆ x2 I∆n RCBO Must Trip Within 200mS ( BS- Only ←
t∆ x5 I∆n RCBO Must Trip Within 40mS 415.1.1

Harmonised Standards BS-EN 61008-1 / BS-EN 61009-1 ←
All the Device to Operate within 300mS at 100% I∆n

Previous Standards BS- 4293 has a Limit of 200mS ( When Testing )
x5 I∆n Remain Unchanged and are 40mS for all Standards ←

Regulations Appendix 3 table 3A RCD table p-243
 
BS- Rating Protection from Solids Protection from Liquids ;)

IP00 No Protection No Protection
IP01 No Protection Condensation
IP02 No Protection Water Spry < 15 degrees from Vertical
IP03 No Protection Water Spry < 60 degrees from Vertical
IP04 No Protection Water Spry from any Direction
IP05 No Protection Low Pressure Water jets from any Direction
IP06 No Protection High Pressure Water jets from any Direction
IP07 No Protection Immersion Between 15cm and 1m Depth
IP08 No Protection Long term Immersion to a Specified Pressure
IP10 Touch by Hands ( > 50mm ) No Protection
IP11 Touch by Hands ( > 50mm ) Condensation
IP12 Touch by Hands ( > 50mm ) Water spray < 15 degrees from Vertical
IP13 Touch by Hands ( > 50mm ) Water spray < 60 degrees from Vertical
IP14 Touch by Hands ( > 50mm ) Water spray from any Direction
IP15 Touch by Hands ( > 50mm ) Low Pressure Water jets from any Direction
IP16 Touch by Hands ( > 50mm ) High Pressure Water jets from any Direction
IP17 Touch by Hands ( > 50mm ) Immersion Between 15cm and 1m Depth
IP18 Touch by Hands ( > 50mm ) Long term Immersion to a Specified Pressure
IP20 Touch by Fingers ( > 12mm ) No Protection
IP21 Touch by Fingers ( > 12mm ) Condensation
IP22 Touch by Fingers ( > 12mm ) Water spray < 15 degrees from Vertical
IP23 Touch by Fingers ( > 12mm ) Water spray < 60 degrees from Vertical
IP24 Touch by Fingers ( > 12mm ) Water spray from any Direction
IP25 Touch by Fingers ( > 12mm ) Low Pressure Water jets from any Direction
IP26 Touch by Fingers ( > 12mm ) High Pressure Water jets from any Direction
IP27 Touch by Fingers ( > 12mm ) Immersion Between 15cm and 1m Depth
IP28 Touch by Fingers ( > 12mm ) Long term Immersion to a Specified Pressure

Rating Protection from Solids Protection from Liquids

IP30 Tools & Wires ( > 2.5mm No Protection
IP31 Tools & Wires ( > 2.5mm Condensation
IP32 Tools & Wires ( > 2.5mm Water Spray < 15 Degrees from Vertical
IP33 Tools & Wires ( > 2.5mm Water Spray < 60 Degrees from Vertical
IP34 Tools & Wires ( > 2.5mm Water Spray from any Direction
IP35 Tools & Wires ( > 2.5mm Low Pressure Water Jets from any Direction
IP36 Tools & Wires ( > 2.5mm High Pressure Water Jets from any Direction
IP37 Tools & Wires ( > 2.5mm Immersion between 15cm and 1m Depth
IP38 Tools & Wires ( > 2.5mm Long term Immersion to a Specified Pressure
IP40 Tools & small wires ( > 1mm ) No Protection
IP41 Tools & small wires ( > 1mm ) Condensation
IP42 Tools & small wires ( > 1mm ) Water spray < 15 degree from Vertical
IP43 Tools & small wires ( > 1mm ) Water spray < 60 degree from Vertical
IP44 Tools & small wires ( > 1mm ) Water spray from any direction
IP45 Tools & small wires ( > 1mm ) Low Pressure water jets from any Direction
IP46 Tools & small wires ( > 1mm ) High Pressure water jets from any Direction
IP47 Tools & small wires ( > 1mm ) Immersion between 15cm and 1m depth
IP48 Tools & small wires ( > 1mm ) Long term Immersion to a Specified Pressure

Rating Protection from Solids Protection from Liquids

IP50 Limited dust Ingress Protection No Protection
IP51 Limited dust Ingress Protection Condensation
IP52 Limited dust Ingress Protection Water spray < 15 degree from Vertical
IP53 Limited dust Ingress Protection Water spray < 60 degree from Vertical
IP54 Limited dust Ingress Protection Water spray from any Direction
IP55 Limited dust Ingress Protection Low Pressure Water jets from any Direction
IP56 Limited dust Ingress Protection High Pressure Water jets from any Direction
IP57 Limited dust Ingress Protection Immersion between 15cm and 1m depth
IP58 Limited dust Ingress Protection Long term Immersion to a Specified Pressure
IP60 Total dust Ingress Protection No Protection
IP61 Total dust Ingress Protection Condensation
IP62 Total dust Ingress Protection Water Spray < 15 degrees from Vertical
IP63 Total dust Ingress Protection Water Spray < 60 degrees from Vertical
IP64 Total dust Ingress Protection Water Spray from any Direction
IP65 Total dust Ingress Protection Low Pressure Water jets from any Direction
IP66 Total dust Ingress Protection High Pressure Water jets from any Direction
IP67 Total dust Ingress Protection Immersion between 15cm and 1m Depth
IP68 Total dust Ingress Protection Long term Immersion to a Specified Pressure
IP69k Total dust Ingress Protection Steam jet Cleaning

2.1 Learning Outcome ( 2392-10 ) Appendix 2 p-240 / 341 :D

Demonstrate an Understanding of the Construction , Design & Management Regulations 2007 ,

Statutory Instruments
2007 No 320 ,
Heath & Safety

The Construction ( Design & Management ) Regulations 2007
Made 7th February 2007
Laid before Parliament 15th February 2007
Coming into Force 6th April 2007

The Construction , Design & Management Regulations are Statutory ( LAW ) and Came into Force in their Present form on 6th April 2007

The Regulations Place a Duty on Virtually Everyone Involved in Construction work ,
Duty Holders have a Legal Duty to Ensure Heath & Safety Measures are Implemented and Adhered to ,
Workers on the Site Also have a Duty to Adhere to Heath & Safety Requirements , A Worker is Anyone Who Carries Out Construction Work ,
Alterations , Maintenance or Demolition , in Order to be Aware of Heath & Safety Requirements Workers must have a
Heath & Safety Certificate such as the CSCS Card ,

The Construction , Design & Management Regulations Requires a Heath & Safety File to be Prepared for a Particular Site ,
This is Produced by the Planning Supervisor and would Include :

(i) a Description of the Project ,
(ii) a General Statement of Heath & Safety Principles and Objectives for the Project ,
(iii) Information about Restrictions Which may Affect the Work such as , Neighbouring Buildings ,
Utility Services , Vehicle Traffic , Pedestrian Traffic & Work Activities of the Client ,

The Heath & Safety File Should be Available for Anybody to Access ,

Heath & Safety Executive ( HSE )

In Order to Ensure Heath & Safety is being Properly Implemented to Protect People Against Risk to Heath & Safety
At Work a Government Body Known as the ( HSE ) Police the Construction Industry ,
 
Last edited by a moderator:
Unit 2 ( Revision Points ) 2392-10 ;)
(1) the Electricity at Work Regulations 1989 ( EAWR ) are up to Date and Compulsory ,
(2) Before becoming Involved with a Dangerous Work Activity the Electricity at Work Regulations 1989
Requires a Person to have Sufficient Knowledge and Experience ,
(3) the Electricity at Work Regulations 1989 is Under the General 2 Umbrella 2 of the Heath & Safety at Work Act 1974 ,
(4) a Breach of Any Law, and in this Instance Electricity at Work Regulations 1989 can Result in a Fine and/or a Prison Sentence ,
(5) the Safe Use of Electricity in the Workplace is Everybody’s Responsibility ,
(6) BS-7671 :2008 Requirements for Electrical Installations ( 17th Edition ) are Non Statutory i.e. ( Not Law ) ↔ 114.1 ←
They are , However , A British Standard Code of Practise and May be Used as Evidence in Court of Law
In Order to Prove that Legal Requirements such as the Electricity at Work Regulations 1989 ( have been Met )
(7) the 17th Edition Wiring Regulations are Not Always a Practical Means to Ensure Electrical Work on Site is to the
Required Standard , a More Practical Approach may be to Use the IEE On Site Guide for Installations up to and Including
100 Amps e.g. Domestic ,
(8) Inspection & Testing Electrical Installations , to BS-7671 : 2008 helps to Insure that the Installation is Safe , Functioning and
Complies with the Legal Requirements ,
(9) the IEE Produce BS-7671 : 2008 and are Recognised by the Heath & Safety At Work Act 1974 , and -
the Electricity at Work Regulations 1989 Other Regulations such as the Control of Substances Hazard to Heath ( COSHH ) -
Regulations 2002 Do Not Recognise the IEE since it is Not Relevant to that Particular Area of Safety ,
(10) although BS-7671 : 2008 ( 17th Edition ) covers Installations such as a Room Containing a Bath or Shower , Swimming Pools and Fairgrounds it Does Not Cover Installations Such as Ships , Aeroplanes , Motor Vehicles and / Off-Shore Installations

(11) Regulations come into Force after they have been Laid before Parliament , for Example ,
The Construction , Design & Management Regulations were Laid before Parliament on the 15th February 2007
And came into Fore on the 6th April 2007 ,

(12) the Construction , Construction , Design & Management Regulations 2007 are Designed to Identify Hazards so that they
Can Ideally be Removed or at Least Minimised ,

(13) the Contractor , According to the Construction , Design & Management Regulations is a Business Involved in Construction ,
Alteration , Maintenance or Demolition ,

(14) the Contractor or Worker , According to the Construction , Design & Management Regulations 2007
Is Regarded as the Duty Holder ,

(15) the Heath & Safety File is a Requirement of the Construction , Design & Management Regulations 2007
Its Purpose is to Assist Anybody who Carries Out Work to Do so in a Safe Manner ,

(16) the Heath & Safety Executive ( HSE ) Guidance Booklet , Electrical Safety on Construction Sites ( HS(G) 141
Is Not Statutory ( LAW ) but a Guidance Note to Help to Ensure Electrical Safety on Construction Sites ,

(17) Risk Assessments are a Very Useful Tool in Dealing with Hazards , Once a Hazard has been Indentified it should
Ideally be Removed , if this is Not Possible or Practical it Should be Minimised ,

(18) it has been Found that the Most Common Risk of Electric Shock on Construction Sites is from the Use of Portable Electrical Equipment , it is therefore Important that this Equipment is Regularly Maintained ,

(19) the HSE Guidance Booklet , Electrical Safety on Construction Site HS(G) 141 Emphasises the Need for Risk Assessments to be Carried Out and to Carefully Plan any Operation Prior to Carrying it Out ,

(20) the Five Steps Involved with a Risk Assessment are to Look for Hazards , Decide who it Affects and how ,
Evaluate the Risk to see if More should be Done , Record your Findings and Review your Assessment ,

:D

Unit 3.1 2392-10 ;)
State the Human Senses that may need to be Employed During the
Initial Verification of an Installation ,

During the Initial Inspection it is Important to Use the Following Senses ,

(1) Sight ,
A Visual Inspection Very Important since it can pick up a Large Number of Faults , ( Being )
(i) Labelling ,
(ii) Incorrect Cable or Cable Size ,
(iii) Damage Equipment
(iv) Incorrect Rotation of Motors or Equipment ,
(v) Lights Not Functioning ,
(vi) Incorrect Protective Devices Rating ,

(2) Touch ,
Touching Parts may Show Faults such as ,
(i) Overheating ,
(ii) Loose Connections ,
(iii) Poor Fixings of such things as Accessories
(iv) Unexpected Vibration of Accessories or Equipment

(3) Smell ,
The Sense of Smell may Indicate ,
(i) Equipment Overheating
(ii) Cables Overheating Due to Overload ,
(iii) Loose Connections Causing Terminals to Overheat ,

(4) Hearing ,
Sound may Indicate Problems such as ,
(i) Unnecessary Arcing Due to Loose Connections ,
(ii) Vibration of Transformer Cores ,
(iii) Poor Contactor Operation Due to Dirt on Pole Faces ,

Why do we Inspect & Test Installation , ;)
Precise and Detailed Examination is Essential to Show a Customer that no Hazardous or Dangerous Condition Exists
Which could lead to Damage , Injury or Death ,

● It Provides an “ official “ Record of the Condition of an Installation on the Day it was Tested ,

See Signs of Arcing in Backbox and Evidence of Arcing on Conductor

BS-7671:2008
● Guidelines are Detailed in BS-7671:2008 part- 6 Chapter 61 ( p-156 )
● These Regulations Detail Both Visual & Instrumental Inspections & Tests for a New Installation ,
● Periodic Inspections & Minor Work Certification is Carried Out on Existing Installation
( Chapter 62 & 63 – see ( 131.8 Additions & Alterations’ to an Installation )

What Problems can be Encountered During Inspection & Testing
Loose / Missing / Snapped Conductors ,
Conductors Trapped by Securing by Screws
Screws through Concealed Cables
Incorrect Wiring
Incorrect Colour Identification
CPC Conductor has become Disconnected from Earth Terminal ( Accessory is Full of Dust / Debris )

● Cables Routing Incorrect
● Loss of Ring-Circuit Continuity
● Conductor Overheating
● External Effects Not taken into Consideration
● Damaged Enclosures
● Faulty Equipment Manufacture

When Inspecting & Testing an Electrical Installation ! Ask Yourself

● Does the Installation Conform to the Latest Edition of the Electrical Wiring Regulations
● Has the Work been Carried Out Correctly an to Specification
● Is the Installation Safe to Use , in your Opinion ?
● Do you have Steps , Spare Parts , Other Equipment Available ?
● Have you Thought about your Own Safety and that of Others Around you , when Inspection & Testing
● Have all your Instruments been Checked Recently ( are they within Calibration Date )
● are you Aware of the Purpose of the Installation and all Circuits Within it ?
● Are you Familiar with the Test Sequence , and which Tests are Required
● Do you have All the Information you need to Carry Out the Task
● Are you able to Contact Customers , Sub-Contractors , Architects , Designers , Contact Mangers , etc If Further info is Needed
if so you’re Ready to Start !!

Visual Inspection Checklist ( Regulation 611.3
● BS-Standards Inspection , Does Everything Comply ( 511.1 / 511.2 ↔ Compliance with Standards ,
● Principal Visual Inspection ( 17 Checks / Not all Applicable ) Section 611 Reg , 12 / EAWR 1989 ( Risk Assessment )
● Connections 526.1 to 526 .9
● Identify Conductors 514 .3
● Cable Routing 512 .2
● Conductor Sizing ( Random Selection 524 & 525 ) incl , Voltdrop Allowance
● Polarity of Switches 132.14
● Polarity of ES Lampholders 612.6
● Protection against Thermal Effects & Presence of Fire-Barriers 131.3 & 527.1
● Electrical Shock Protection ( Pasic Protection 411
● Electrical Shock Protection ( Fault Protection 411
● Prevention of Common Damaging Influences 515
● Isolation & Switching Arrangements 537 ( ps it could be Manual Operation )
● Presence of Undervoltage Protective Devices 445.
● Position & Identification of Protective Devices 132.14 and 514
● Labelling 514
● Equipment and Protective Measures to External Influences 522
● Suitable Access – Equipment 513
● Presence of Danger Notices 514
● Availability of Diagrams & Notices 514
● Correctly Erected and Assembly of Equipment ( 133 , 134 , - part 5
● Drawings , Diagrams , Records , ( Previous Work )

Inspection Checklist BS-7671:2008

Confidence in Yourself – Never be Afraid to Ask or Seek Guidance if Required ,

Socket -Tester ( Measure the Effectiveness of the Earth ) the Earth Fault Loop Impedance , :rolleyes:

Heath & Safety ( GS-38 ) Mains Voltage Tester ,
Battery - Proving Unit A.C / D.C 50V – 690V 230V / 400V

Voltage Indicators should always be Tested with a Proving Unit or a Known Live Source Before and After Use
Zero Adjust ( Null ) Test Leads Résistance ……………………. ( R2 / Socket Adapter ) 4mm Tips on Leads
( Live Circuit Warning )
 
Last edited by a moderator:
Measurement of External Earth Fault Loop Impedance ( Ze ) 2392-10 :rolleyes:

The External Earth Fault Loop Impedance “ Supply Characteristics ” and Earth Arrangements
To be “ Recorded “ on the Second page of both the “ (i) (ii)

(i) Electrical Installation Certificate
(ii) Domestic Electrical Installation Certificate
(iii) Periodic Inspection Report

( Ze ) is the Earth Fault Loop Impedance of that path of the System which is External to the Installation

Like the Maximum Prospective Fault Current ( Ze ) can Only be Measured by Testing at the Origin of the Installation

Before the Test ,

( Lock Off with Padlock ↔ Key in you Pocket at all Times )
( Warning Sign must be Placed at the ( CU )

Main Switch ( OFF ) ( Earthing Conductor Temporarily Disconnected )

● ( Check the Polarity Indicator for Correct Connection )

● The Earthing Conductor must be Disconnected from the Main Earthing Terminal ,
● Must be Separated from all Parallel Earth Paths such as Bonding and Circuit Protective Conductors’
● Purpose of this Test is to Prove that the Intended Means of Earthing is Present and of an Acceptable Ohmic Value ,

For Safety Reasons ,
It is Essential that the Entire Installation is Isolated from the Supply before the Earthing Conductor ( or if Necessary ,
Any Other Protective Conductors’ ) are Disconnected from the Main Earthing Terminal ,
And that the Installation Remains Isolated for the Duration of the Testing

Providing Unit must be Used 1st
To Test the Probes of the Voltage Indicator are Working all right on Mains Power
● Voltage Indicators should always be Tested with a Proving Unit or a Known Live Source Before and After Use
Test the Probes of the Voltage Indicator that there’s No Power on the Feed Side

● Three - Phase Systems ,
Three - Lead Version (i) Green - Lead on Earth (ii) Red - Lead on Brown (iii) Black -Lead on Neutral
Two - Lead Version (i) Green - Lead on Earth (ii) Red - Lead on Brown
● Single - Phase Systems ,
Two - Lead Version (i) Green - Lead on Earth (ii) Red - Lead on Brown

● Test Instrument ( Set on “ Loop “ 20Ω
Earth Fault Loop Impedance Tester , ( this is a Live Test )

TT Systems , Where the Means of Earthing for the Installation is Provided by an Installation Earth Electrode ( the Value of Ze )

Two Methods of Measuring the Résistance of an Earth Electrode are Recognised in ( IEE Guidance Note - 3 )
● Method 1 , Using a Proprietary Earth Electrode Test Instrument , ←
● Method 2 , Using a Earth Fault Loop Impedance Test Instrument , ( Ra ) ←

The Test gives you (Ze) – this is ( Ra ) for your Electrode + the Résistance of the Supply Transformer Electrode + the
Transformer Windings Impedance + the Résistance of the Supply Line Conductors from the Transformer to the Input Side of
The Installation Main Switch , 411.5.3

( Ze = ( Ra ) for your Electrode + the Résistance of the Supply Transformer Electrode + the Transformer Winding Impedance +
The Résistance of the Supply Line Conductor from the Transformer to the Input Side of the Installation Main Switch

Note 2 ↔ 411.5.3 where ( Ra ) is not know it May be Replaced by ( Zs )

Verify Compliance with BS-7671 , Earth Fault Loop Impedance is Required for Each Circuit that Relies on ( ADS )
As the Protective Measure , 415.1.1

Without a Sufficiently Low Earth Fault Loop Impedance , the Magnitude of the Earth Fault Current will Not be Sufficient to Cause
The Protective Device to Automatically Disconnect the Circuit within the Maximum time Permitted to Provide Protection ,

Ohmic Résistance in Accordance BS-7671 ,
Earth Résistance
Selective Earth Résistance
Soil Resistivity

● Earth Fault Loop Impedance Table for TT Systems ( 41.5 ) 411.5.3

Rated Residual Operating Current I∆n mA 30 100 300 500Ω
Ra at 50v Ω 1667 500 167 100

Regs fig 2.5 / 2.3 / 2.4 ;)

Earth Fault Loop ( Zs ) paths for a TT Systems ( Supply Phase / Supply Neutral - Earth Electrode which is Electrically Independent of the Source

Earth Fault Loop ( Zs ) paths for a TN-S Systems ( Supply Phase , Separate Neutral & Protective Conductors throughout the System

Earth Fault Loop ( Zs ) paths for a TN-C-S Systems ( Supply Phase / Neutral & Protective Functions Combined in a Single Conductor
Part of the System , ( PME ) Protective Multiple Earthing ,
 
Last edited by a moderator:
2392-10 ( TT Domestic :) Measurement of Installation Earth Electrode Résistance

Method ( 2 )
Using an Earth Fault Loop Impedance Test Instrument
“ Set – Loop “ 200Ω

Main-Switch Off
Red-Lead ( Incoming Supply Brown Phase , ( L ) 514.8
The Earth Fault Loop Impedance Test Instrument is Connected to the Supply ( Energised ) Side of the Main Switch ←

Black Lead ( Connected to Disconnected Earthing Conductor )

(1) Access to the Equipment is Not Restricted ,
(2) Before Access to the Inside of the Distribution Equipment , Safe Isolation can be Preformed , ( Regulation 12 )
(3) Basic Protection meets the Required Standards ( IP Codes IP2X / or Exceeds ) 416.2.4
(4) Terminal Insulated Covers inside the CU , can Not be Displaced

Two Types of Protective Devices for Disconnection of the Circuit is Required for TT Systems , Fault Conditions -
(i) RCD (ii) Overcurrent Protective Device , ( RCBO BS-EN 61009-1 / RCCB BS-EN 61008-1 ) 41.5

Where an Overcurrent Protective Device is Used Regulation 411.5.4 -
( Requires following Conditions to be Fulfilled ( Zs x Ia ≤ Uo ) 32A ÷ 230v = Ω
RCBO BS-EN 61009-1 / RCCB BS-EN 61008-1 ) 41.5

(i) you must have your Earthing Conductor Impedance Low Ω as Possible
(ii) 411.5.3 - RCD is Used for Earth Fault Protection , ( TT System 0.2sec final Circuits “ Not Exceeding ” 32A , 411.3.2.2
(iii) 411.3.2.4 - 1sec , Final-Circuits / Distribution Circuits “ Exceeding ” 32A ( Ra x I∆n ≤ 50V )
TT Systems Only be Achieved by Protecting Every Circuit with RCD 411.5.3

Where Requirements , Regulation 411.5.3 are Meet if the ( Zs ) 41.5 Final Circuit Protected by RCD , Standards have been Meet ,
Maximum Disconnection , 411.3.2.2 / 411.3.2.3 TN- Systems , 411.3.2.4 TT – Systems ,

Fault Conditions – ( Earth Fault Conditions “ Ohms “ ( 230 ÷ Zs = Amps

For the Apprentice :eek:
“ Continuity of Protective Conductors “ ( Terminology “ Dead Test ” )

GN-3

612.2.1
No Load Voltage between 4 / 24V a.c / d.c
Short Circuit Current of Not Less than 200mA ( Ia > Ief )

“ Test Prior to the Installation Being Energized “
Test Instrument : Set on Continuity ( 20Ω )
The Resistance of the Test Leads is Significant
If the Particular Test Instrument does Not have Provision for “ Correcting for the Resistance ” of the Test Leads Measure the Résistance of the Leads when Connected Together , the Measured Value to be Subtracted from the Test Readings ,
( Terminology “ Wander Lead )
Test Instrument : Most New Instrument have ( Null Button this will Zero Out the Lead Resistance )
Measuring the Résistance of the Protective Conductor
Disconnecting where Practicable any Conductive Paths which may be Connected in Parallel to a Connection from a Protective Conductor to an Electrically Continuous Systems of Pipework at One or More Points along the Protective Conductor
Such Parallel Paths could Lead to Incorrect Test Readings and may even Conceal the Fact that a Protective Conductor is Not Electrically Sound ,
Some Instillations , with those Incorporating Metal Conduit or Metal Trunking which is Fixed to a Metal Structure
It would be Impracticable to Attempt to Disconnect all Parallel Paths
In such Circumstances , the Continuity of a Protective Conductor may be Verified only by Inspection in Addition to Testing

( R1 + R2 ) Method
This Method is Applicable to Circuit Protective Conductors and Line Conductors
Testing Continuity of a Protective Conductor to a Lighting Point One-Way –

“ Main Switch OFF “ ( Securely Isolate the Supply ) ↔ Regulation 12
(1) Temporary Connection , at the Supply End of the Circuit , at the CU between the Line and CPC of the Circuit to be Tested
(2) “ Red Lead “ on the Switch Live Terminal ,
(3) “ Black Lead “ on the Earthing Terminal ,
Polarity Should be Verified at Both the Lighting Point & the Switch ( CU ↔Link-Out ↔ Light Point ↔ Light Switch )
The Electrically most Remote Point in this Particular Circuit will be the Switch , ( R1 + R2 ) Value Recorded for this Circuit
Will be Measured at the Ceiling Outlet between the Switch Line and CPC ,

Testing Continuity of the Protective Conductor at a Lighting Switch by Wander Lead Method -
( R2 ) Black Lead on Earthing Terminal , Red on Earthing Terminal in Switch ,
Continuity Testing of a Ferrous Enclosure Using Wander Lead Method -
Black Lead on Earthing Terminal from one Back-Box , the Other Back-Box , Red Lead , PS, if there’s a Lot work a Pair at a Time back to the CU , ( R2) Ps if Not A ↔ B at the same time you doing , “ Visual Inspection “

At The Same Time your Checking Correct Polarity / with Continuity ,

If you keep thing Like this you’ll be a Great Tester one Day , 2391

GN-3
Heath & Safety ( GS-38 ) Mains Voltage Tester , 2mm / 4mm Tips on Leads ( with Fuse )
Battery - Proving Unit A.C / D.C 50V – 690V 230V / 400V
Voltage Indicators should always be Tested with a Proving Unit or a Known Live Source Before and After Use
Live Circuit Warning

For Apprentice to work on :confused:

612.2.2
Continuity of Ring Final Circuit

The Cables of a Ring Final Circuit Start at the Outgoing Terminals of the Consumer Unit
Connect to all the Points in the Ring , and Return to the Same Outgoing Terminals Live ( Line & Neutral ) Conductors
must Form a Complete Unbroken Loop without Interconnections ,
as Must the Circuit Protective Conductor ( CPC )

“ Securely Isolate the Installation “ ( EAWR ) Regulations 12 / 13
On the Part or the Installation to be Tested , Measure the Résistance of the Line & Neutral Conductors Separately ( between Ends )

Note Readings :
● End to end Résistance of the Line ( Live ) Conductor ↔ R1
● End to end Résistance of the Circuit Protective Conductor ↔ ( CPC ) R2
● End to end Résistance of the Neutral Conductor ↔ Rn
● Remember ( Neutral is Classed as Live Conductor , Ring Circuit End to End
on Ring : 2 x Live Conductors 2 x Natural Conductors 2 x Circuit Protective Conductors ( 4 Live Wires all in ) 2 x CPC = 6

314.1 Every Installation shall be Divided into Circuits
314.4 Where an Installation Comprise more than One Final Circuit , ( this is a Requirement – Part P )

This will Indicate Whether or Not the Conductors are Continuous , ( R1 + Rn )
Line ( Live ) & Neutral Conductors Should have Equal Résistance ,
Line – 0.40Ω
Neutral - 0.40Ω
CPC - 0.20Ω ( twin & earth 2.5mm2 ( R1 ) 2.5mm2 ( Rn ) 1.5mm2 ( R2 )

Performing the Test :
Set the Instrument on Continuity 20Ω ( Low Ohms (Ω) Continuity Range )
“ Main Switch OFF “

(i) Red Lead on : One End of Leg Phase
(ii) Black Lead on : One End of Leg Phase

(i) Red Lead on : One End of Leg Phase ( Phase & Natural on Terminal Block “ Cross-Connected “ )
(ii) Black Lead on : One End of Leg Neutral
This Test Sequence also Verifies Polarity & Circuit Protective Conductor Continuity to all Points in the Ring Final Circuit ,

● Probes , Voltage Tester ↔ GS-38
● Insulated ↔ Fused ↔ Finger Guards
● Maximum of 2mm & 4mm Exposed Tips / Retractable Shrouds

The Top Part of a Distribution Board must Conform to ( IP4X ) ← 416.2.2
The Sides of a Distribution Board must Conform to ( IP2X / IPXXB ) ← 416.2.4 (ii)
 
Last edited by a moderator:
Insulation Résistance 2392-10 ;)

Precautions May be Necessary to Avoid Damage to Electronic Devices ,
The Presence of any Circuit or Equipment Vulnerable to a Typical Test should be Indicated in the Diagram or Schedule of Test Results ,

Before Proceeding with this Test, the Inspector should Ensure that for the Circuit to be Tested
● All Pilot or Indicator Lamps that are Likely to Interfere with the Test , By Proving a Path between Line & Neutral have been Disconnected
● all Items of Equipment which are at Risk of Damage from the Test Voltage have be Disconnected ,
● Incoming Neutral has been Disconnected so that there is No Connection with Earth ,

“ Securely Isolate the Installation your Going to Work On , EAWR - Regulation 12
This Test should be Carried Out with all Circuits Isolated from the Supply and Confirmed Dead ,

● Locking Off Devices / Padlock , ( Warning Sign(s) Danger : Do Not Use )
Voltage Indicators should always be Tested with a Proving Unit or a Know Live Source before and After Use ,

● GS-38 is a British HSE Guidance Document , it is Advisory , Not Mandatory ,
The Standard for Safety of Test Equipment is BS-EN 61010 -

“ Dead Test “
Insulation Résistance Test Instrument , ( MΩ )
Capable of Supplying the Test Voltage D.C. Indicated in ( Table 61 )
Single-Phase Installation ( Line ( Live ) to Neutral )

Three-Phase Installation -
Line 1 to Line 2
Line 2 to Line 3
Line 3 to Line 1
Test each Line in Turn to the Neutral :

Insulation Résistance is Measured Between Live Conductors ( Line & Neutral ) a Voltage is Applied to the Conductors
● Check that all Switches are Closed ( Two-way Switches should be Operated to include all Live Conductors in the Test ,

TT Systems : Earth Electrode
Test Method for a New Installation : Before Connection to the Supply is Energized ,
Black Lead : Link Together all Line Conductor & Neutral
Red Lead : Linked Conductor(s) & Protective Earth ( Remember the MEM Link on Earth )

● Disconnecting the Earth from Earthing Terminal if you Do Not have a ( MEM Link on Earth ) Parallel Paths ,

“ Insulation Résistance Values “
● 0.00 MΩ = Dead Short ,
● 0.08 MΩ = Low Insulation Résistance Fault ,
● ≥ 200 MΩ = Healthy Circuit ,

● This Test is used to Prove that the Circuit under Tests has No Dangerous Short-Circuits Prior to the Circuit being Made “ Live ,
( Insulation Résistance ) ↔ This Test Verifies ( Proves ) that the Insulation of the Cables in Good Order ,

Insulation Résistance Tests Give an Indication of the Condition of the Insulation on the Installation ,
Effective Insulation is Required to Provide Basic Protection and to Prevent Short-Circuits & Earth Faults ,

Measure and Recorded the Results onto : Schedule of Test Results ,

For “ Circuits ” Rated at More than “ 100A “ :rolleyes:

The Use of D.C. Test Current may Lead to a Value of ( Zs ) Which is Optimistically Low and May therefore be Unacceptable
In Such Cases , an Ohmmeter or Continuity Test Instrument which Supplies an A.C. Test Current at a Frequency of ( 50 Hz )
Should be Used , Alternatively , a Value of ( Zs ) should be Obtained by another ( Method ) ( Such as Direct Measurement by an Earth Fault Loop Impedance Test Instrument ,

Measurement of ( Zs ) at a Socket-Outlet Using an Earth Fault Loop Impedance Test Instrument ,

Testing should Only be Carried Out after a Thorough Inspection and Continuity Testing have Confirmed ,
So far as is Reasonable Practicable ,
That all Circuit protective Conductors , and Main / Supplementary bonding Conductors are in Place ,

This Test is Conducted with the Supply On , all Necessary Precautions Must therefore be Taken to Prevent Danger
Earth Fault Loop Test Instrument : ( Set on Loop - 20Ω

For Socket-Outlets , as a Minimum , Perform the Test on the Outlet , Which is Situated Electrically Furthest from the Origin of the Circuit ,
If this is Not Know , Test all Socket-Outlets , in the Circuit and Record the Highest Value , Proprietary Test Lead with a Fitted Plug should be Used ,

TN-S : 0.8Ω

( Zs ) m ≤ 0.8 x ( Uo / Ia ) 230 ÷ 24 , 0.8Ω x ( Zs 9.58 = 7.67Amp

“ Measurement Earth Fault Loop Impedance “

Generally Accepted that , Where the Measured Earth Fault Loop Impedance of a Circuit is Not Greater than 80%
Of the Relevant Limit Specified in BS-7671
The Impedance can be Expected to be Sufficiently Low Under Earth Fault Conditions to meet the Relevant Limit Specified in BS-7671
And for the Protective Device to Automatically Disconnect within the Time Specified

41.2 / 41.3 & 41.4 BS-7671
Give the Maximum Permitted Values of ( Zs ) for Different Type of Overcurrent Protective Devices &
Different Maximum Permitted Disconnection Times , Maximum Permitted Values Given in BS-7671
Are Based on the Conductors having been Heated up by the Passage of Load Current , which Increased their Résistance
Whilst Test Results are Usually Obtain when the Conductor Temperature is Lower ,
Correction Factors is Given in IEE Guidance Note 3 / 6
“ As a Rule of Thumb “ the Measured Values of ( Zs ) should Not Exceed ↔ 0.8 times ↔ the Relevant Values Given BS-7671 ( 41.2 & 41.4 )

It is Generally Necessary to Adjust the Values Obtained by the Test before Comparing them with the

the Limiting Values of Earth Fault Loop Impedance when Measured at Ambient Temperatures up to 20ºC
the Limiting Measured Values are 80% of the Values given in BS-7671 , Round Down ,

the Value to be Recorded in the Schedule of Test Results is the Measured Value ,

if the Protective Device is Not of a Type whose Maximum Permitted ( Zs ) Value is Given in BS-7671
then , as a Rule of Thumb , the Measured Values should Not Exceed ↔ 0.8 times ↔ the Value Given by the Formula
Appendix 3 BS-7671 p-243

Zs = Uo / Ia ( 230 ÷ 32A = 7.18Ω )

PFC ( 230 ÷ 1.16 = 198A )

2392-10
Domestic Electrician
New Installation your Using Cold Test Only OSG , 2D ( 80% )
 
Last edited by a moderator:
Thank you, more good reference material.

By the way, your spell checker seems to of thought you meant the french resistance....

and I thought that testing a test meter on a known live circuit was frowned on now?
 
Sorry about my Spell Checker , it was Made in Scotland
Broken my Glass , wearing my Wife’s Glasses , PS I like the word Résistance from Halo Halo
British Version ↔ Resistance )
When you mention about the Test Meter you open a can of Worms !!!!! do you take a Proving Unit Every time you use you Test Meter on Mains ?
Ps you never Know HSE may come up with that yet ???? Thank you Amberleaf
Doomed keep up the good work Mate , :D

Why Inspect & Test ;)

Inspection & Testing of Electrical Installations

The Electricity at Work Regulations 1989 is a Statutory Document :
It is a Legal Requirement that Statutory Regulations are Complied with ,
Not to Comply is a Criminal Offence and Could Result in a Heavy Fine and Evan Imprisonment to Extreme Cases ,

These Regulations to Ensure that Places of Work Provide a Safe , Well-Maintained Electrical Systems ,
A Simple way to Provide this is to Ensure that Newly Installed Circuits & Existing Installations are Tested on a Regular Basis ,
Electrical Test Certificates are Used to Record what has been Done and Confirm that the Installation Meets the Required Standard ,

British Standard for Electrical Installations is BS-7671
The Requirement for Electrical Installations , within this Standard , Regulation 610.1 States that “ Every Installation “ shall ,
During Erection and on Completion before being put into Service be Inspected & Tested to Verify , so far as Reasonably Practicable ,
That the Requirements of the Regulations have been Met “

Regulation 610.1 States that “ where Required , Periodic Inspection & Testing of Every Electrical Installation shall be Carried out in
Accordance with Regulations ( 621.2 to 621.5 ) in Order to Determine as far as is Reasonably Practicable, whether the Installation
Is in a Satisfactory Condition for Continued Service “ ,

Document P of the Building Regulations 2000 for Electrical Safety came into Effect on 1 Jan : 2005 And was Amended in April 2006 ,

The Purpose of this Document is to Ensure Electrical Safety in Domestic Electrical Installations ,

General ,
This States that Electrical work must Comply with The Electricity at Work Regulations 1989 and that any Installation or
Alteration to the Main Supply must be Agreed with the Electricity Distributor ,

Protection Against Flooding
The Distributor must Install the Supply the Supply Cut-Out in a Safe Place and Take into Account the Risk of Flooding ,
Compliance with The Electricity Safety , Quality and Continuity Regulations 2002 is Required , its Law

For the Apprentice ;)
This is all got to do with Testing ( this is a Start , all you need to know, ive broke it down )

“ Useful Piece of Equipment “

( R1 = R2 ) Socket Adapter
Socket -Tester ( Measure the Effectiveness of the Earth ) the Earth Fault Loop Impedance ,
This will Not Only be Useful for the Safe Isolation of Socket-Outlets ,
It can also be Used for Ring-Circuit Testing and the ( R1 = R2 )
Testing of Ring-Circuit / Radial-Circuit , Without having to Remove them from the Wall ,

Test-Socket-Adaptor ( R1 / Phase-Live ( R2 / Earth ( Rn Neutral

HSE “ GS-38 Leads “ should be :
Flexile and Long Enough , but Not to Long ,
Isolated to Suit the Voltage at which they are to be Used ,
Coloured where it is Necessary to Identify One Lead from the Other ,
Undamaged and Sheathed to Protect them Against Mechanical Damage ,

Measurement Equipment Used by Electricians when Working on or Investigating Power Circuits with a Rated Voltage Not Exceeding 650Volts ,
Heath & Safety ( GS-38 ) Approval Mains Voltage Indictor , ( Maintain Output Voltage for Extended Testing )
GS-38 Test Lamp Fused ( Range 80 / 500 Volts ( 230v / 15watt Pygmy Lamp )

“ The Probes should “
Have a Maximum of 4mm Exposed Tip ( Preferably 2mm )
Be HRC Fused at 500mA or have Current Limiting Resistors ,
Have Finger Guards ( to Stop Finger Slipping on Live Terminals )
Be Colour Identified ,

“ Locking Devices “ Padlock / and other Locking off Devices for MCBs ,

( Warning Notices )
( Live Circuit Warning )
( Danger Do Not Switch On )

Proving Units
Battery Powered Proving Unit , Essential for Safe Use of Voltage Indicators & Test Lamps ,
● Proving Unit Check : all Neon Lamps Located within the Testing Device illuminate for Duration of ( PROOF TEST )

Regulation 4(3) of the Electricity at Work Regulations 1989 Recommends that the Following Procedure be Adopted so that the Device Itself is ( Proved ) –

● Connect the Test Device to the Supply Which is to be Isolated ; this should Indicate Mains Voltage ,
● Isolated the Supply and Observe that the Test Device Now read ( 0V )
● Connect the Test Device to Another Source of Supply to “ Prove that the Device is Still Working Correctly ,
● Lock-Off the Supply and Place Warning Notices “ Only then should Work Commence on the Dead Supply ,

( EAWR ) Regulation 12
Means for Cutting off the Supply and for Isolation :
( EAWR ) Regulation 13
Precautions for Work on Equipment Made Dead :

You must make Absolutely Certain that you and you Alone are in Control of the Circuit to be Worked on
Proving the Circuit is Live you can Proceed as Follows ,

Step 1 , Ensure Voltage Indicator / Test Lamp is Working Correctly , ( Voltage Lights Lit )
Step 2 , Test Between “ All “ Live Conductors and Live Conductors and Earth ,
Using Test-Socket-Adaptor ( R1 / Phase-Live ( R2 / Earth ( Voltage Lights Lit )

Step 3 , Locate the Point of Isolate , Isolate and Lock Off , ( Warning Notices )

Step 4 , Test Circuit to Prove that it is the Correct Circuit that you have Isolated , ( No Voltage Lights Lit )
Using Test-Socket-Adaptor ( Test Between “ All “ Live Conductors and Live Conductors and Earth ) L/N/E ,

Step 5 , Check that the Voltage Indicator is Working by Testing it on a Proving Unit or Know Live Supply , ( Voltage Lights Lit )

Most GS-38 Test Lamps will Trip an RCD when Testing Between Live & Earth , :eek:
Better to Use an Approved Voltage Indicator to GS-38 as most of these do Not Trip RCDs , :rolleyes:
 
Last edited by a moderator:
thats very helpfull amberleaf but how does one remember all that for the 2391 holy grail exam? lol wot areas do you think i should mainly concentrate on regarding regs and gn3? i knw all the test equitment scales and voltages, certificates for periodic and miner works eic etc testing ring final ciruits insulation resistence polarity ze zs rcd pfc functional testing any help would be great cheers



Please posts your question in the main forums. Thanks.
 
Last edited by a moderator:
Supplementary Protective Bonding Conductors ( Where Required ) :rolleyes:

Supplementary Bonding is Required where Circuit Disconnection Times Cannot be Met ( Regulation 411.3.2.6 ) or
Where there is an Increased Risk of Electric Shock ,
Those Areas would be in Bathrooms , Swimming Pools & Other Special Locations ,

Where Disconnection Times Cannot be Met and the Effectiveness of Supplementary Bonding is Required to be Checked
( Regulation 415.2.2 ) a Simple Test is Required ,

Automatic Disconnection is by a Protective Device , Regulations give a Formulae -
( R ≤ 50V / Ia ) if the Circuit is Protected by an RCD , the Formulae Becomes ( R ≤ 50V / I∆n )

When this Formulae is Used , it will Ensure that Any Touch Voltage in the Bonded Area will Not Rise above ( 50 Volts a.c. )
Before the Protective Device Operates ,

The Formulae where a Protective Device is in Place for Automatic Disconnection of Supply ( ADS )
Step 1 , find ( Ia ) for a 5 seconds Disconnection Time ,
Device 32Amp BS- 88 fuse

Appendix 3 / BS-7671 fig 3.3A
32A Device a Current of 125 Amp is Required to Operate the Fuse ,
This Value Can also be Found by Using the Maximum ( Zs ) Value Found Table 41.4 ( 1.84Ω )

Calculation : Ia = Uo ÷ Zs ( Ia = 230 ÷ 1.84 = Ia = 125A
This Method Can be Used for all Protective Devices :

Now the Values Can be Used to Verify that the Area does or does Not Require Supplementary bonding to be Installed ,
( R ≤ 50V ÷ Ia ( 50 ÷ 125A = 0.4Ω ) is the Maximum Value Permitted between Exposed or Extraneous Conductive Parts ,
If when Measured it is found that the Résistance is Higher than 0.4Ω then Supplementary bonding will be Required
The Values of Résistance will Not be the Same for Different Ratings or Type of Protective Devices ,

Where an RCD is Installed to Protect the Circuit the Calculation to find out if Supplementary bonding is Required ,
R = 50v ÷ I∆n ( R = 50v ÷ 0.03 R = 1666Ω , ( 50v ÷ 30mA = 1.666Ω

Bonding is Not well-Understood by Joe Public ,
You have Travelled 20/30 Miles to Fit Kitchen / Completed Everything to Comply with Required Regulations ,
A few days later, however, and before you have been paid for the Work ,
You Receive Phone Call from your Customer Informing you that his Next door Neighbour has Spotted that you
Have Not Bonded the Sink , of Course your Customer will Believe that his Neighbour is Right and you have Forgotten Something ,

The Choice is your / Do you Try and Convince your Customer that his Neighbour is Wrong ,
Do You Travel back to the Job to Carry Out the Bonding to Ensure Big Bucks ,

Just Put a Couple of Earth Clamp and a Short Length of 4mm2 Earthing Round the Pipes ,
( Cheaper just to Use the Supplementary Protective Bonding in the First Place )

For the Apprentice : :D

2.5mm2 / 1.5mm2 / Twin & Earth Cable 22meters long ,
OSG 9A ( Résistance of Copper ) 2.5mm2 / Copper : 7.41

The Résistance / Phase Conductor , ( R1 )
R1 - 7.41 x 22m ÷ 1000 = 0.163Ω *

Divide the Largest Conductor by the Smallest to find the Ratio of Conductors ,
( how much Bigger is the Largest Conductor , ( 2.5 ÷ 1.5 = 1.67

2.5mm2 Conductor is 1.67 x Larger than 1.5mm2 Conductor , therefore , it must have 1.67 x less Résistance than 1.5mm2 Conductor ,
0.163Ω * x 1.67 = 0.27Ω ( this is the Resistance of 1.5mm2 Conductor ,

OSG 9A ( Résistance of 1.5mm2 Copper : 12.10mΩ ( 22meters of 1.5mm2 Copper ,
22 x 12.10 ÷ 1000 = 0.266Ω

Final Check : OSG 9A
Résistance 2.5mm2 / 1.5mm2 Cable , we will See that it has a Résistance ( 19 51mΩ ) per meter
22 meters of it will have a Résistance of ( 22 x 19.51 ÷ 1000 = 0.429Ω

The Résistance Value of 2.5mm2 ( 0.163Ω ) and the Résistance Value of the 1.5mm2 is ( 0.266Ω )

Add them Together : ( 0.163Ω + 0.266Ω = 0.429Ω ( Finally , 0.429Ω is the Résistance of our 2.5mm2 / 1.5mm2 -
Measured as One Cable ,

This beats tons of paper work ,

“ Insulation Résistance “ :rolleyes:

This is a Test that can be Carried Out on a Complete Installation , or Single Circuit
For This Case ,
Domestic , ( Single Circuit or Ring ) New Installation ,
The Test is Necessary to find Out if there is Likely to be any Leakage of Current Through the Insulated Parts of the Installation ,
A Leakage could Occur for Various Reasons ,

Good Way to Think of this Test is to Relate it to a Pressure -Test
We Know that Voltage is the Pressure where the Current is Located in a Cable ,
On a Low Voltage Circuit , the Expected Voltage would be around 230v a.c the Voltage Used in an Installation Test on a 230V -
Circuit is 500v d.c , Which is More than Double the Normal Circuit Voltage , therefore , it can be Seen as a Pressure Test Similar
To a Plumber Pressure Testing the Central Heating Pipes ,

Circuits between 0V – 50v a.c
Required Test Voltage , ( 250v d.c. )
17th Edition : ( 0.5MΩ )

Circuits between 50V a.c – 500v a.c
Required Test Voltage , ( 500V d.c. )
17th Edition : ( 1MΩ )

Circuits between 500V & 1000V a.c.
Required Test Voltage , ( 1000V d.c. )
17th Edition : ( 1MΩ )

Domestic Installations ,
Remember that Testing should be Carried Out from the Day the Installation Commences ( Regulation 610.1 )

“ Insulation Résistance “ :eek:
If for Some Reason , there is a Piece of Equipment Connected to the System that Cannot be Isolated from the Circuit Under Test ,
Do Not Carry Out the Test Between Line Conductors – Only Test Between live Conductor & Earth
This is to Avoid Poor Readings and Possible Damage to Equipment , this Test should Only be Carried Out on Individual Circuits ,
Not the Whole Installations , as it is Important to Test as Much of the Installation as Possible ,

Three Phase Sub-Mains is Tested the Results are : :eek:

L1 to Earth is 130MΩ
L2 to Earth is 80MΩ
L3 to Earth is 50MΩ
N to Earth is 100MΩ

If these Conductors were now Joined and Tested to Earth the Value would be as Given ,
Calculation ,
1 1 1 1 1
--- + --- + --- + --- + ---
R1 R2 R3 R4 Rt / N

( 1 1 1 1 1 )
--- + --- + --- + --- + --- = 19.92MΩ
130 80 50 100 0.05

Enter it this way into a Calculator : ( Remember the Button 1/X )

130X-1 + 80X-1 + 50X-1 + 100X-1 = X-1 = 19.92MΩ

This Value is Still Acceptable but Lower because the Conductors are in Parallel ,

Iceman , this is what you can face , :cool:
Swindon Massive , send email to Kev , 20 pounds C/D It’s a Must

A Ring Circuit is Protected by a 30A BS-3036 Semi-Enclosed Rewirable Fuse
Measured ( Zs ) 0.96Ω

( Final Circuits Not Exceeding 32A )

This is a Ring Final Circuit , Disconnection time has to be 0.4sec ( table 41.2 BS-7671
Maximum ( Zs ) / 30A Rewirable Fuse – 1.04Ω

Eighty per Cent of this Value must Now be Calculated , this can be Achieved by Multiplying it by ( 0.80. )
1.04 x 0.80 = 0.83Ω

The Measured Value for the Circuit must now be Lower than the Corrected Value if it is to Comply : BS-7671
Measured Value 0.96Ω
Corrected Value 0.83Ω

The Measured Value of ( Zs ) is Higher , therefore , the Circuit will Not Comply ,

Option one is the Preferred Method because it will give an Accurate Value whereas the Test in -
Option two will Include Parallel Paths and because of this will Often give Lower Readings ,

Option one should Always be Used for an Initial Verification as the First Reading will be Used as a Benchmark -
To be Compared with Results taken in Future Periodic Tests ,

On a Periodic Inspection Using Option two , a Higher Test Results is Obtained than on the Initial Verification ,
This would Indicate that the Circuit is Deteriorating and that Further Investigation would be Required ,

The Methods Described here must be Fully Understood by Anyone who is Intending to sit the ---- & ------
---- Exam on Inspection & Testing of Electrical Installations ,

For the Apprentice ;)
BS 7671 lists Five Types of Earthing System :

TN-S, TN-C-S, TT, TN-C, and IT.

T = Earth (from the French word Terre)
N = Neutral
S = Separate
C = Combined

I = Isolated ( The source of an IT system is either )

Connected to Earth through a Deliberately Introduced Earthing Impedance or is Isolated from Earth. All Exposed-Conductive-Parts of an Installation are Connected to an Earth Electrode. )

When Designing an Electrical Installation, One of the First things to Determine is the Type of Earthing system.
The Distributor will be Able to Provide this Information.

The System will Either be TN-S, TN-C-S (PME) or TT for a Low Voltage Supply given in Accordance with the
Electricity Safety, Quality and Continuity Regulations2002. Appendix 2 This is because TN-C Requires an Exemption
from the Electricity Safety, Quality and Continuity Regulations, and an IT system is Not Permitted for a
Low Voltage Public Supply in the UK because the Source is Not Directly Earthed. Therefore TN-C and IT
Systems are both Very Uncommon in the UK.
 
Last edited by a moderator:
Regs : 4E4A : :eek:

3 - Core Swa ( 3 x 95 Csa = 285mm2 Clipped Direct 289 Amp ( 300mm2 )
3 - Core Swa ( 3 x 70 Csa = 210mm2 Clipped Direct 238 Amp ( 300mm2 )
4 - Core Swa ( 4 x 70 Csa = 280mm2 Clipped Direct 238 Amp

2391 / 2392-10 my advice is to look through most of the Notes ive Downloaded / 1 / 5 pages , :cool:
This may help you to Jog your Memory , Ps – Put them all together and you have most of the Answers, like this ,
2391 will do a Lot off writing ,
BS 7671 Electrical forms

● Electrical Installation Certificate ( 3 Signatures )
Approved Contractor Issuing the Certificate has Not been Responsible for the Design – or the Inspection & Testing Off the Electrical Work ,
Certification of the three Persons must be Carried Out Separately Using ,
(1) Designer , (2) Constructor , (3) Inspector ,

● Electrical Installation Certificate ( 1 Signature ) 2392-10
( One Person is Responsible for the Design )

The Electrical Installation Certificates is to be used only for the Initial Certification of New
Installation or For an Addition or Alteration to an Existing Installation “
where NEW circuits have been Introduced “

The "Original" Certificate is to be given to the person ordering the work ( Regulation 632.1 ) A duplicate should be retained by the Contractor.

● Electrical Installation Certificate 2382-10 ( New Work Only

This Certificate is only Valid if accompanied by the Schedule of Inspections and the Schedule(s) of Test Results.

● EIC Schedule of Inspections ( Schedule of Circuit Details Continuation Sheet )
● EIC Schedule of Test Results ( Continuation Sheet )

● Minor Electrical Installation works Certificate

Twenty Short Questions , 2391 old Questions :confused:
Your working to this Principle , somewhere along the Line ,

(1) three Single Sockets have been added to a Ring Final Circuit : State
(a) Inspection & Testing Certificate that will need to be Completed ,
(b) Title in Law Given to the Inspection
(c) Legal Status of the Inspection
(2) an Engineering Works 18 years Old and is Due for Inspection and Test : State the
(a) Type of Inspection and Test Required ,
(b) Documents that must Accompany the Completed Certificate ,
(c) Circumstances under which the Type of Inspection and Test in (a) above may Not be Required ,
(3) State the Legal Status of the following
(a) BS-7671 : 2008
(b) Guidance Note 3
(c) HSE , GS-38
(4) Give One Example of Each of the Following
(a) an Exposed Conductive Part
(b) an Extraneous Conductive Part
(c) Direct Contact
(5) State Three Methods of Protection Against Indirect Contact
(6) State the Earthing Systems that Use the Following as Return Path
(a) Pen Conductor
(b) Cable Sheath
(c) General Mass of Earth

612.9 :cool:
Methods of Calculation of Earth Fault Loop Impedance from Given Data and Measurement of Conductor Résistance

The External Earth Fault Loop Impedance ( Ze ) can be Calculated Using the Supply Voltage & the Prospective Earth Fault
Current Value Measured at the Supply ,
( Ze ) = Supply Voltage ( Prospective Earth Fault Current )
Final Circuit Earth Loop Impedance ( Ze ) can be Calculated by Adding the External Earth Fault Loop Impedance ( Ze )
( to the R1 + R2 Value of the Circuit ,

General Rule of Thumb is to Multiply Tabulated Values by 0.8 before Comparing the Test Values Obtained During Test ,
Requirements of Regulation 411.4.5 or 411.5.4 ,

411.4.5 ( Zs x Ia ≤ Uo ) 230 ÷ 0.57Ω = 403A Earth Fault Conditions
( Zs ) Should Not Exceed 0.8 Times , Appendix 14
( Zs = Uo ÷ Ia , 230 ÷ 403 = 0.5 Ω

Earth Fault Loop Impedance Exceeds 0.8 / Uo / Ia ,
A More Precise Assessment of Compliance with Regulation 411.4.5 or 411.5.4 as Appropriate , may be Made (i) (ii) (iii) (iv) (v)
Note : Other Methods are Not Precluded ,

p-249 fig 3.4 Type B, MCB to BS-EN 60898 / RCBOs BS-EN 61009-1 , Overcurrent , 32Amp / 160A ( Zs ) 41.3
Ief / Zs ≤ Uo ÷ Ia ( Zs ≤ 230 ÷ 160A = ( Zs ≤ 1.437Ω
Max Loop Impedance , 32A – I 160A required ( 41.3 ( 32 / Zs 1.44Ω

RCBO , BS-EN 61009-1 Appendix 3 p-243
Zs = Uo ÷ Ia ( 230 ÷ 160 = 7.18
411.3.2 Specifies Max Disconnection Times for Circuits ,
Conditions for Automatic Disconnections Cannot be Fulfilled by Overcurrent Device ,

“ Fault Protection ”
Fault Protection can be Met by Meeting the Disconnection times Regs , 411.3.2
This is Achieved by Limiting Earth Fault Loop Impedance ( 41.2 41.3 41.4 )
411.3 Requirements for Fault Protection :
(1) 411.3.1.1
(2) 411.3.1.2
(3) 411.3.2
BS-88-22 80A ÷ 740A = 0.1sec ( PSSC ) Fig , 3.3a 80A 740A / 0.4sec ;
BS-88-22 - BS-88-6 : 41.4 - 40A / Zs / 1.35Ω ( Uo ÷ Zs = 170A / 230 ÷ 1.35 Ω = 170A ) 170A – 5sec Fig , 3.3b
40 ÷ 170A = 0.2 sec ( PSSC )

PS off to the Mother Land , 5 Days ,
Jason you have 5 Days Holiday , hit the 24-Pack ? , Amberleaf
 
Last edited by a moderator:
Old Notes some Revision : 2391 “ Iceman “ ;)
9A / OSG ( R1+R2 )
10mm2 / 4mm2 ( 6.44mΩ/M
( R1+R2 ) : 6.44 x 14.75 = 0.095Ω
( Zs ) Circuit - 0.095Ω + 0.7 = 0.795 ( 0.8 ) Ω
Max : ( Zs ) 45A BS-3036 : 3.2B ( 41.4 ) 5sec – 1.59Ω
C/f ( t ) 1.59 x 0.8 = 1.27Ω
As the Actual ( Zs ) is Lower
9A / OSG : 4mm2 Cooper Conductors ,
Résistance / 4.61mΩ / M
( R1+R2 ) Phase & CPC / 4mm2 – 9.22mΩ / M
( R1+R2 ) : 9.22 x 67 ÷ 1000 = 0.061Ω ( 0.61Ω ),
As it is a Ring ( 0.61 ÷ 4 = 0.15Ω ,
( R1+R2 ) Value 0.15Ω ,
( Zs = Ze+ R1+R2 ) 0.63 + 0.15 = 0.78Ω
As Max : permissible ( Zs ) is given 0.9 from OSG , “ No ( t ) ( Ci )
Sub / ( Ze ) from the actual ( Zs ) to find Max : permissible ( R1+R2 ) Value ,
( R1+R2 ) = 0.9 – 0.63 = 0.27Ω
Now Sub : actual ( R1+R2 ) Value from Max : permissible Value , ( 0.27 -0.15 = 0.12Ω )
Max : Résistance that our Spur could have ( 0.12Ω )
Length / transpose / Calculation :
( mV x Length ÷ 1000 = R )
Find Length transpose to : ( R x 1000 ÷ mV / Length )
Therefore : ( Length = 0.12 x 1000 ÷ 9.22 = 13meters ) :

2.5mm2 / 1.5mm2 ( Résistance 19.51m/Ω per meter .
( 5.8 meters of the Cable have ( Résistance 5.8 x 19.51 ÷ 1000 = 0.113
0.113 is ( Résistance of the Additional Cable , ( R1+R2 ) for this Circuit will now be ( 0.2 + 0.1133 = 0.313Ω )

9A / OSG ( 10mm2 Copper / Résistance 1.83mΩ x 22 ÷ 1000 = 0.4Ω ) *
By Calculation ↔ ( Zs = Ze+ R1+R2 ) or Use a Low Current Test Instrument , *

1/50 + 1/80 + 1/60 + 1/50 = 0.069 ( R = 1 / 0.069 = 14.45Ω ) *

Determining Touch Voltage : ( Ze ) x Rated mA - I∆n / RCD :eek:
TT / ( Ze ) = 200Ω ( Main RCD is Rated at 100mA
200Ω x 100mA ÷ 1000 = ( 20V )

For Circuit(s) having Conductors of up to 25mm2 Operating at Normal Frequency ( 50Hz ) Inductance may be Ignored
And it is Acceptable to Determine ( Zs ) Using the Formula
Rather than by Measurement Using an Earth Fault Loop Impedance Test Instrument , Zs = Ze+ R1+R2

Popular Question is “ When can ( Zs ) “ be Less than ( Ze ) given that ( Zs = Ze+ R1+R2 ) ( 239- ) ←

Testing and Measuring it ( Ze ) at Origin and ( Zs ) at the Furthest Point ( 239- ) ←
( Zs ) Test : Check the Continuity of the Earth

Earth Loop Impendence Test ,

( Ze ) is Part of the Earth Fault Loop Impendence External to the Installation ( the Impendence of the Supply )
( R1 ) is the Résistance of the Consumers Phase Conductor from the Origin of the Circuit to the Most Distant Part of the Circuit ,
( R2 ) is the Résistance of the Consumers Protective Conductor from the Origin of the Circuit to the Most Distant Part of the Circuit ,

( Zs = Ze+ R1+R2 )
( R1 ) is the Résistance of the Live Conductor :
( R2 ) is the Résistance of CPC

( Zs = Ze ) will give you ( R1+R2 ) approx ,

Therefore to find ( R2 ) in Isolation you need to know the Value of ( R1 ) and Subtract this from the Above or just Measure it Directly with a Meter ,
> ( Ze ) is the External Impedance Measured at the
> Incoming Point of the Supply at the Premises , it is
> the Résistance of the Phase Cable and the Return to
> the Transformer ,
( Zs = Ze+ R1+R2 ) is Measurable Via Method ( 2 ) Long Lead : ( Zs = Ze+ R1+R2 ) : ( R2 ) is a Measure of Résistance of CPC only Via Long-Lead ( Method ( 2 ) ( Ra ) is the Résistance of the Earthing Conductor :

( Ze ) on a TT Systems as this would be the Compete Earth Loop Path which would include ( Ra ) plus the Résistance
Of the Suppliers Electrode ,
The Impedance of the Transformer Winding and the Impedance of the Suppliers Phase Conductor

V = I x R so ( Ix R ) should be Less than 50V Touch Voltage :
Maximum ( I ) will be the Tripcurrent of the RCD Used being that it is a TT System
The ( R ) should be the Résistance from Earth to the Appliance etc . Including the Earth Rod ,
But as ( Zs ) would Include the Full Circuit , it will Obviously be Higher than half the Circuit Therefore if the Calculation Still
Remains Lower than 50V it will Obviously Remain below 50V if the Résistance Value is Used and Recorded
So yes ( Zs ) is not Strictly Relevant but it can be Used which is Good as it is an Easy Reading to Obtain ,
e.g. 100mA x 20Ω = 2Volts ( 100 x 20 ÷ 1000 = 2V = Touch Voltage )

TT System use the Touch Voltage System ( Described as the Alternative Method ) so the Résistance of the Live Conductor is Irrelevant ,

( Ze ) on a TT Systems as this would be the Compete Earth Loop Path which would include ( Ra ) plus the Résistance
Of the Suppliers Electrode ,
The Impedance of the Transformer Winding and the Impedance of the Suppliers Phase Conductor

V = I x R so ( Ix R ) should be Less than 50V Touch Voltage :
Maximum ( I ) will be the Tripcurrent of the RCD Used being that it is a TT System
The ( R ) should be the Résistance from Earth to the Appliance etc . Including the Earth Rod ,
But as ( Zs ) would Include the Full Circuit , it will Obviously be Higher than half the Circuit Therefore if the Calculation Still
Remains Lower than 50V it will Obviously Remain below 50V if the Résistance Value is Used and Recorded
So yes ( Zs ) is not Strictly Relevant but it can be Used which is Good as it is an Easy Reading to Obtain ,
e.g. 100mA x 20Ω = 2Volts ( 100 x 20 ÷ 1000 = 2V = Touch Voltage )

TT System use the Touch Voltage System ( Described as the Alternative Method ) so the Résistance of the Live Conductor is Irrelevant ,

( R1+R2 ) is the Résistance of the Circuit Phase Conductor & the Résistance or the Circuit Protective Conductor ,
One of the Dead Test i.e. Pre-Energization
Connect the Circuit Phase Conductor to Earth Rail , Either by Removing it from the MCB or by Using a Short-Linking Wire ,

At the Furthest Most Point of the Circuit Measure the Résistance between Phase & Earth ( CPC )
Using a Low Resistance Ohms Meter , this is your ( R1+R2 ) Value
The ( R1+R2 ) for Ring Final Circuit is Done Slightly Differently ,

( Ze ) is the External Earth Fault Loop Impedance to the Installation ( it is Measured in Isolation ) i.e. You need to Isolate the Supply ,
Disconnect the Earthing Conductor from the ( MET ) and Measure the Impedance between Phase and the Earthing Conductor using -
An Earth Fault Loop Impedance Tester ,
Once you have Completed the Test , Remember to Reconnect the Earthing Conductor before you Re-Energize !!1
( Zs ) is the Total Loop Impedance of the Circuit , it can be Done by Measurement at the Furthest Most Point of the Circuit or by -
( Zs = Ze+ R1+R2 )

( PFC ) is Basically the Maximum Current which can Flow in the System,
It needs to be Conducted at the Origin , for this you need to Conduct a ( PSSC ) Prospective Short Circuit Current Test :
Which is between Each Phase & Neutral / or Phase – Phase if 3 Phase )
( PEFC ) is between Each Phase & Earth -
The Highest Value is the Prospective Fault Current ( PFC ) ( Ze ) is the ( Z ) at the External Part of the Installation , that is Immediately after the Meters as Far as Practicable
( Ze ) Power Off , at your Mains ( or Only ) Isolator with all Bonds Disconnected ( also Check the Prospective current here ,
With Bonds Connected then Check Prospective Current Again ( it is Usually Higher Due to ( Parallel Paths ) -
This Highest Reading is the ( PFC )
Check ( R1+R2 ) on each Circuit Add to ( Ze ) then this gives the Calculated ( Zs )
When Energised ( With Bonds Reconnected of Course ) then Recheck that ( Zs = Ze+ R1+R2 ) or Less than Due to ( Parallel Paths ) -
This Confirms ( Zs ) Actually Does Exist ,

Also PH-PH in 3-Phase for a ( PFC ) or Double the Single Phase Readings ,

( Zs = Zdb+ R1+R2 )
Where the Distribution Board is at the Origin of the Installation , ( 239- )

2391 / this is a Written Exam , Use some off the Wording ,
 
Last edited by a moderator:
239x “ Wording “ Iceman ;)

The Insulation Resistance should be above 2MΩ
If it is Less than Further Investigation must be Carried Out as ( a Latent Defect may Exist ) *

In any Exam it is Vital that the Question is Read Carefully , Often it is better to Read a Question Several Times
To try and Understand what is being Asked

If the Question asks for a Fully Labelled Diagram , then Marks are Awarded for the Diagram and the Labelling ,
Where the Question Asks “ Explain with the Aid of a Diagram “ then a Diagram and a Written Explanation is Required ,

When the Question ask for a List then you will be Expected to List a Sequence of Events in the Correct Order , -
( Just a List with No Explanation ) if you are Required to State Something then a Statement is Required in No Particular Order ,

List the Sequence of Dead Tests :
(a) Continuity of Protective Conductors’ ( Including Main & Supplementary Equipotential Bonding : Test
(b) Continuity of Ring Final Circuit Conductors : Test
(c) Insulation Résistance : Test ( Remember the Wording , Use in the Right Contents )

State Three Statutory Documents Relating the Inspecting & Testing ( of Electrical Installations )
(a) The Electricity at Work Regulations 1989 ( No more No Less )
(b) The Health & Safety at Work Act 1974
(c)

Always try to Answer the Questions in “ FULL “ using the Correct Terminology :
For Example : if Asked “ Which is the Type of Inspection to be Carried Out on a New Installation”
The Answer must be : An Initial Verification ,
For the Document Required for Moving a Switch or Adding a Socket the Answer must be :
An Electrical Installation Minor Works Certificate , ( Not Just Minor Works )

The Initial Verification of an Installation or Circuit is Very Important and it must be Carried Out Correctly :
The Documentation for this Serves two Purposes ,
Firstly , it is a Certificate which should be Provided to Show that the Installation has been Installed Correctly and that it is Safe to Use
This Certification should Not be Issued Until the Installation has been Tested & the Results have been Verified as being Satisfactory ,

It would be a Pointless Exercise to just Inspect & Test an Electrical Installation when it is Completed – it is Vital that the
Installation is Inspected Regularly During the Installation and Before any Cables are Finally Covered Up ,

Remember ↔ that , When you Sign the Electrical Installation Certificate ,
You are Taking Responsibility for Every Part of the Installation that you Sign for
This should Not be Taken Lightly because , if an Accident Occurs Due too an Unsafe Installation ;
The Person who has Carried Out the Inspection & Test May Well be Held Responsible ,
( Remember Your Arse is on the Firing Line )

In Many Ways , Initial Verification Should be Easier than Carrying Out a Periodic Inspection on an Existing Installation
As the Person Carrying Out the Test should know their Way around it ,
Because they would have seen it as it was being Installed ,

PS : Use the Correct Terminology ←←←←
Insulation Résistance Test Instrument : ( NOT Megger )

Low Reading Ohms Meter ( Not Continuity Tester or millli Ohms Meter )

Electrical Installation Certificate / or ( EIC ) NOT Electrical Installation Report
Schedule of Test Results – ( NOT Schedule of Test or Schedule of Results )

Testing ( 3-Phase Induction Motor ) :D

There are Many Types of 3-Phase Motors but far the Most Common is the Induction Motor ,
It is Quite Useful to be Able to Test them for Serviceability

Before Carrying Out Electrical Tests it is Good Idea to Ensure that the Rotor Turns Freely
This may Involve Disconnecting any Mechanical Loads . The Rotor should Rotate Easily and you should Not be Able to hear any Rumbling from the Motor Bearings , if the Motor has a Fan on the Outside of it , Check that it is Clear of any Debris which may
Have been Sucked in to it , Also Check that any Air Vents into the Motor are Not Blocked ,

Generally : if the Motor Windings are Burnt Out there will be an Unmistakable Smell of Burnt Varnish
It is still a Good Idea to Test the Windings as the Smell could be from the Motor being Overloaded
Three Phase Motors are Made up of Three Separate Windings / in the Terminal box there will be ( Six Terminals ) as Each Motor Winding will have Two Ends , The Ends of the Motor Windings will Usually be Indentified as -
( W1 , W2 ; U1 , U2 ; or V1 , V2 ) The First Part of the Test is Carried Out Using a Low-Résistance Ohms Meter ,
Test Each Windings End – End ( W1 to W2 , U1 to U2 , and V1 to V2 ) The Résistance of Each Winding should be Approximately
The Same and the Résistance Value Will Depend on the Size of the Motor ,
If the Résistance Values are Different then the Motor will Not be Electrically Balanced and it should be Sent for Rewinding , if
Résistance Values are the Same , then the Next Test is Carried Out Using an ( Insulation Résistance Tester ) MΩ
Join W1 and W2 Together , U1 and U2 Together , and V1 and V2 Together ,
Carry Out an Insulation Résistance Test between the Joined Ends , i.e. W to U then W to V and then between U and V , -
Repeat the Test between Joined Ends and the Case , or the Earthing Terminal of the Motor ↔
( these Tests can be in any Order to Suit you )
Providing the Insulation Résistance is ( 2MΩ ) or Greater then the Motor is Fine , if the Insulation Résistance is above ( 0.5MΩ )
This Could be Due to Dampness and it is Often a Good Idea to run the Motor for a While before Carrying Out the Insulation Test -
Again as the Motor may Dry Out with Use :

To Reconnect the Motor Windings in Star : Join W2 , U2 and V2 Together and Connect the 3-Phase Motor Supply to -
W1 , U1 and V1 , if the Motor Rotates in the Wrong Direction , Swap Two of the Phase of the Motor Supply

To Reconnect the Motor Windings in Delta , Join W1 to U2 , U1 to V2 and V1 to W2 and then Connect the 3-Phase Motor -
Supply One to Each of the Joined Ends ,
If the Motor Rotates in the Wrong Direction , Swap Two-Phases of the Motor Supply ,

Test Instruments’ :cool:

Guidance Note GS-38
GS-38 is for Electrical Test Equipment Used by Electricians and Gives Guidance to Electrically Competent Persons Involved in
Electrical Testing , Diagnosis and Repair , Electrically Competent Persons :
Electricians , Electrical Contractors , Technicians , Mangers or Appliance Repairers

Voltage Indicating Devices
Instruments Used Solely for Detecting a Voltage Fall into Two Categories :
Detectors that Rely on an Illuminated Lamp :

Lamps are Fitted with a 15Watt Lamp , and Should Not give Rise to Danger if the Lamp is Broken , a Guard should also Protect it ,

Detectors that Use Two or more Independent Indicating Systems / One of Which May be Audible /
And Limit Energy input to the Detector by the Circuitry Used , Two-Pole Voltage Detector
i.e. a Detector Unit with an Integral Probe , an Interconnecting Lead and a Second Probe

These Detectors are Designed and Constructed to Limit the Current and Energy that can Flow into the Detector
This Limitation is Usually Provided by Combination of the Circuit Design Using the Concept of Protective Impedance , and
Current- Limiting Resistors built into the Probe , the Detectors are also Provided with in Features to Check the Functioning
Of the Detector before and After Use , The Interconnecting Lead and Second Probes are Not Detachable Components ,
These Type of Detectors’ do Not Require Additional-Limiting Resistors or Fuses to be Fitted Provided that are Made
To an Acceptable Standard and the Contact Electrodes are Shrouded

Voltage Indicating Devices :

Guidance Note GS-38
Lamps and Voltage Indicators are Recommended to be Clearly Marked with the Maximum Voltage which may be Tested by the
Device and any Short Time Rating for the Device if Applicable ,
This Rating is Recommended Maximum Current that should Pass-Through the Device for a Few Seconds
As these Devices are Generally Not Designed to be Connected for more than a Few Seconds ,
 
Last edited by a moderator:
239- ;) Calculation of the Maximum ( Zs ) of the Circuit Breakers’
It is Often Useful to be able to Calculate the Maximum ( Zs ) Value for Circuit Breakers without the Use of Tables ,
BS-EN 60898 Devices : ( 20A / BS-EN 60898 Device )
Type B / MCB Must Operate within 3 to 5 Times its Rating ,
( Worst Case Scenario Therefore ) we must Assume that the Device will Not Operate until a Current Equal to ( 5 ) times -
Its Rating Flows Through it ( Ia ) for a 20A Type B / MCB this will be ( 5 x 20A = 100A )

If we Use a Supply Voltage of 230volts – which is the Assumed Open Circuit Voltage ( Uo ) of the Supply -
Ohm’s Law can be Used to Calculate the Maximum ( Zs )
( Zs ) = Uo ÷ 100 = ( Zs ) = 230 ÷ 100 = 2.3Ω

To Check this look : BS-7671 / 41.3 ( the Value ( Zs ) 20A Type B / MCB = 2.3Ω

( 20A / BS-EN 60898 Device ) Type C / MCB Must Operate at a Maximum of 10 times its Rating ( In )
( 10 x 20 = 200A ( 230 ÷ 200 = 1.15Ω )
To Check this look : BS-7671 / 41.3 ( the Value ( Zs ) 20A Type C / MCB = 1.15Ω
Type D / MCB with a Nominal Operating Current ( In ) Must Operate at a Maximum of 20 times its Rating : -
( 20 x 20 = 400A ( 230 ÷ 400 = 0.57Ω )
To Check this look : BS-7671 / 41.3 ( the Value ( Zs ) 20A Type D / MCB = 0.57Ω
The Maximum ( Zs ) Values for a Type C are 50% of the ( Zs ) Value :
The Maximum ( Zs ) Values for a Type D are 50% of the ( Zs ) Value : of a Type C MCB ,

Maximum Earth Loop Impedance ( Zs ) for Fuses :
Fuses have to Operate at 0.4 or 5 sec Depending on the Type of Circuit which they are Protecting ,
To find the Maximum Permissible ( Zs ) Value for a Fuse , the Current Curves in Appendix 3 / Fig : 3.1

Find the Maximum Permissible ( Zs ) for a BS-1361 Fuse with a Rating of 20Amp with a Required Disconnection Time of 0.4 sec
( Look in Appendix 3 / Fig : 3.1 , the Left-Hand side of the Grid Represents the Disconnection Time )

From the Bottom Left-Hand Corner , follow the Line Upwards Until the Horizontal Line Representing 0.4 sec is Found
Follow the Horizontal Line across to the Right Until the Bold Line for a 20Amp Fuse is Found ,
From where the Horizontal Line Touches the Bold Line move Vertically Down the Page Until you meet the Bottom Line of the Grid ,
The Bottom Line Represents the Automatic Operating Current for the Fuse , it can be Seen that the Current Required is Around 130Amps
( The Table in the Right-Hand top Corner of the Page will Show this Value to be 135Amps )

( Zs ) = Uo ÷ Ia / ( Zs ) = 230 ÷ 135 = 1.7Ω
To Check this look : BS-7671 / 41.2 / ( Zs ) BS-1361 / 20A = 1.7Ω

( Do not Forget to Correct this Value for the Conductor Operating Temperature & Ambient Temperature : if Required ,

This Calculation can be Used for any Type of Protective Device :
Remember that the Disconnection Time for a Circuit Breaker will always need to be 0.1 sec

Comparing Maximum ( Zs ) & Measured ( Zs )
Unfortunately we Cannot Compare this Value Directly to any Measured ( Zs ) Values that we have :
This is because the Values given in BS-7671 for ( Zs ) are for when the Circuit Conductors’ are at their Operating Temperature -
( Generally 70ºC )

Assume that we have a Circuit Protected by 32A BS-EN 60898 Type B :
Measured ( Zs ) is 0.98Ω
5 x 32 = 160A ( 230 ÷ 160 = 1.44Ω )

The Measured ( Zs ) at 70ºC for the Circuit is 1.44Ω )
To find ¾ of 1.5 we can Multiply it by 0.8 ( 1.5 x 0.8 = 1.2Ω )

1.2Ω now becomes our Maximum Value : and we Compare our Measured Value Directly to it without having to Consider the Ambient Temperature or the Conductor Value :
In this Case it is , and the 32Amp Type B Device would be Safe to Use ,
 
RCBO : Double Pole ,
“ Earth Leakage “
“ Overload Protection “
“ Short Circuit Protection “
“ Over Voltage & Surge Voltage Protection “
“ Switch Line & Neutral for Increased Safety “
“ Will Replace Existing Earth Leakage Devices “

239- ;)

Why do we Need to Confirm Correct Polarity ?

Incorrect Polarity can Give rise to Danger in a Number of Ways :

(i) Parts of the Installation May Remain Connected to the Line Conductor when Switched off by a Single-Pole Device but , for all Intents and Purposes , will Appear to be Dead :
(ii) in the Event of an Overload , the Circuit-Breaker or Fuse Protecting that Part of the Installation would Disconnect the Neutral of the Circuit , Leaving the Load at Full Line Voltage ,
(iii) An Earth Fault Current Might Remain Undetected by Overcurrent Protective Devices

Re-Cap : :confused:

Electrical Installation Certificate -
Intended for New Installation Work ; including Alterations and Additions to Existing Installations ,
Domestic Electrical Installation Certificate -
Intended for New Installation Work ; including Alterations and Additions Existing Installations , in a Single Dwelling ( House or Individual Flat )
Minor Electrical Installation Works Certificate -
Intended for Minor Installation Work that Does Not Include the Provision of a New Circuit ,
Periodic Inspection Report : for an Electrical Installation -
Intended for Reporting on the Condition of an Existing Installation ,

Nature of Supply Parameters :

Provision is Made to Record the Supply Parameters which Comprise ,
Normal Voltage(s) U ( Line to Line ) : Uo ( Line to Earth ) ( in Volts )
This Parameter can Generally be Determined Only by Enquiry ,
For Public Supplies in the UK , U / 400V and Uo 230V – Two Phase / Three-Phase Supplies ,
And U – Uo are 230V – Single-Phase Supplies

Nominal Frequency , ( f ) / Hz
This Parameter can Generally be Determined Only by Enquire , ( in UK Nominal Frequency ; Invariably ( 50 Hz )

For the Apprentice ;) What is GS-38 "IEE Guidance Note 3: Inspection and Testing ,
Guidance Note GS38, published by the Health and Safety Executive ( HSE ), sets out in clear and concise terms the features that any instruments and meters should have if they are to be used to carry out electrical tests in accordance with BS 7671. In order to comply with the Electricity at Work Regulations 1989 it is critical that any competent person carries out electrical testing safely, and this guidance note draws attention to the risks of using test instruments that do not meet the GS38 standard. In brief, some of the requirements for test instruments include:
• The test probes should have finger guards, ideally 2mm or 4mm of exposed conductive tip (to prevent the user accidentally making contact with either the probes or live conductors under test) and should be fitted with a High Breaking Capacity inline fuse or fuse-and-resistor combination with a low current rating (to prevent the probes rupturing under high short-circuit currents and/or damaging the test instrument if incorrect range settings are used, typically drawing more than 500mA ).

• The test leads should be adequately insulated to suit the environment in which they’re being used, are coloured differently from each other so as to be distinguishable, are flexible, are capable of handling the maximum current range of the test instrument and are shrouded or sheathed to protect against mechanical damage, securely connect the leads to the test instrument and safeguard against the possibility of direct contact with live parts.
GS38 also Identifies Three Categories of Test Instruments, namely those that:
• Test for the presence of a voltage ( voltage detection )
• Measure Voltages
• Measure current and resistance ( as well as, in some cases, Inductance and Capacitance )

• Look at the test instrument, probes, leads and connectors for any obvious signs of physical damage. Have you stored the test instrument properly? Did you lend it out to someone that didn’t look after it ? Are there knots, kinks or cuts in the leads ? Is the case cracked ? Are the connections loose ?
• Look at the ratings on the test instruments, probes, leads and connectors to make sure they’re suitable for the job you’re asking them to do. Do you know what range you need to be using ?
• Does the test instrument have a calibration date on it? If you don’t know when the instrument was last calibrated, how can you be sure you’re getting the right readings ?
Before carrying out any actual tests, make sure you know all the procedures involved in carrying out safe isolation on the circuit(s) you intend to work on.
To sum up, GS38 has been designed both to keep both you and others safe and to try and define a clear standard that manufacturers can work towards to make sure electrical testing is carried out sensibly and safely. Although high-quality test instruments can be costly one-off purchases, keep in mind the cost of your own safety ! As with any tools, good quality instruments and meters pay for themselves many times over and being skilled in their use is a true measure of a Qualified and Competent Electrician .

For the Apprentice : some Revision , ;)
A 6A BS-EN-61009-1 RCBO with a Maximum Value of Earth Fault Loop Impedance of ( 1.92Ω is Type D )
( Part 4 : Protection for Safety , Regulation 411.4.7 ( 41.3 )

The Maximum Disconnection Time for a Circuit Supplied by a Reduce Low Voltage System Using a 110V Midpoint Earthed
Transformer is ( 5sec ) Part 4 : Protection for Safety , Regulation 411.8.3

Where Basic Protection and / or Fault Protection is Provided , Certain External Influences may Required Additional Protection
Provided by ( Use of 30mA RCDs ) Part 4 : Protection for Safety , Regulation 415.1.1

The Horizontal Top Surface of a Barrier or Enclose which is Readily Accessible shall Provide a Degree of Protection of at Least
( IPXXD or IP4X ) Top of CU : Part 4 : Protection for Safety , Regulation 416.2.2

The Symbol Used to Show that a BS-88 Device has a Motor Circuit Application is ( gM ) Symbols Used in the Regulations p-35 - 411.4.6

The Effectiveness of Protective Measures should be Considered with Regard to ( Maintainability ) -
Party 3 : Assessment of General Characteristics , Regulation 341.1

The Measure of Automatic Disconnection of Supply is Employed for a Circuit Supplying 13A Socket-Outlet Intended
For General Use by Ordinary Persons , which of the Following does “ NOT “ Contribute to the Provision of Fault Protection ,
( Reinforced Insulation ) Part 4 : Protection for Safety , Regulation 411.1 (ii)
(a) Protective Earthing (b) Main Protective Bonding Conductor (c) Additional Protection by RCD ( d) Reinforced Insulation ) ←←

Basic Protection may be Provided by : Basic and Enclosures to IPXXB or IP2X (Part 4 : Protection for Safety , Regulation 416.2.1 ,

Which of the Following need “ Not “ be Tested Under Fire Conditions to Ensure Compliance with Non-Flame Propagating Requirements :
( a) Cables : ( b) Protective Devices ←←← : (c) Conduit Systems : (d) Trunking Systems : Part 4 : Protection for Safety , Regulation 422.2.1

In the Event of an Earth Fault on the HV side of a Substation the LV Installation may be Affected by :
( Uf ) Part 4 : Protection for Safety , Regulation 442.2

A Cable Concealed in a Wall Outside the Prescribed Zone at a Depth of Less than 50mm Must :
( be Enclosed in Earthed Metallic Conduit ) Part 5 : Section & Erection of Equipment , Regulation 522.6.6

239- :confused: this may come up in the Future ,

“ Client Demand for a Continuous Supply “

Where the Client Does Not want Any Interruption in the Supply and it is Not Possible to Work on Effected Area during Normal Working Hours ;
Arrangements should be Made for a Planned Maintenance or Shut Down in Order for the Repair to be Carried Out Safely
 
Last edited by a moderator:
2392 - ;) Measurement of Prospective Fault Current Using a Two-Lead Instrument : ( Set , Loop – 20kA )

Take Particular Care During the Test Process ;as Fault Conditions are Most Severe at the Origin of an Installation ,
Where this Test is being Preformed ,

The Prospective Short-Circuit and Prospective Earth Fault Current are to be Measured ( or Determined by an Alternative Method )
At the Origin and at Other Relevant Points in the Installation ,
Note that a Measurement made at a Point in the Installation such as an Item of Switchgear fed by a Distribution Circuit would not be the Maximum for the Installation
The Earthing Conductor , Main Equipotential Bonding Conductors and Circuit Protective Conductors should all be Connected
During these Tests , because the Presence of these and any Other Parallel-Paths to Earth May Reduce the Impedance of the Fault Loop and so Increase the Prospective Fault Current , ( PFC )

The Instrument to be Used is an Earth Fault Loop Impedance Test Instrument , with or Without a Prospective Fault Current Range ,
A Set of Test Leads is Required , having Two or Three Probes to Suit the Requirements of the Particular Test Instrument ,

A Two-Lead Test Instrument Connected Across the ( Line and Neutral ) of an Incoming Supply ,Not that for Measuring a Line to Earth Value ,
The Instrument Must be Connected Across the Line and Main Earthing Terminal

Measurement of Prospective Fault Current Using a Three-Lead Instrument : ( Set , Loop – 20kA )
Three-Lead Instrument Connected Across the Line, Neutral and Earth of an Incoming Supply ,
Procedure :
Check that the Test Instrument , Leads , Probes and Crocodile Clips ; are Suitable for the Purpose ,
Select the Appropriate Range and Scale ( Prospective Fault Current 20 kA )
Observing all Precautions for Safety , Connect the Instrument to the Incoming Energised Supply to Measure a ( Line to Neutral Value )
Check the Polarity Indictor “ if Any “ on the Instrument for Correct Connection ,
Press the Button :
Record the Reading :
Repeat the above Steps ; as Appropriate , with the Instrument Connected for Measurement of the ( Line to Earth Value )

If the Test Instrument does Not have a ( Prospective Fault Current Range ) the Readings given by the above Procedure are
( Fault Loop Impedance in Ohms )
To Convert each of these Readings into a Prospective Fault Current ,
( Divide them into the Measured Value of Line to Neutral Voltage )
Measured Voltage : 230V / Measured Value of Fault Loop Impedance between ( Line & Neutral ) at the Origin = 0.05Ω
Maximum Prospective Short-Circuit Current ( Line to Neutral ) 230 ÷ 0.05 = 4600A / or 4.6kA

( This Value would have been Given Directly if the Instrument had a ( Prospective Fault Current Range )
The Same Procedure is Now Repeated , Taking Readings between ( Line and Earth ) to Determine the Maximum Prospective Earth Fault Current ,

The Higher of the Two Prospective Fault Current ( Line to Neutral or Line to Earth ) should be Recorded on the Certificate or Report ;
“ Warning “ Do-Not Test Between Lines with 230V Instrument :

Three Phase Supplies
Unless a Test Instrument Designed to Operate at 400V :
It will be Necessary to Calculate the Prospective Fault Current between ( Lines )
Where an Installation is Supplied by Two or More Phases , the Maximum Prospective Fault Current is Likely to be between ( Line Conductors )

The Prospective Fault Current Between Line can be Determined by Using the Measured Value of the Line to Neutral ( PFC )
Complex Relationship between the Line to Neutral and the Line / Line Values of Prospective Fault Current,
( tends to err on the Safe Side )
The Prospective Fault Current ( Line to Neutral )
( Line to Neutral Prospective Fault Current Multiplied by Two :
4.6kA x 2 = 9.2 kA

A Circuit-Breaker to BS-3871 will have an ( M ) Number Marked on it : :rolleyes:
This Indicates its Short-Circuit Capacity in kA
M4 Denotes 4000A ( 4 kA ) M9 Denotes 9000A ( 9 kA )
Fuses are Not so Straightforward :
BS-3036 - 1 kA to 4 kA ( Depending on Duty Rating )
BS-1361 – 16.5 kA
BS- 88 – 40 kA to 80 kA ( Depending on Duty )

Overcurrent Protective Devices having a Rated Current up to 50A Incorporated in a Consumer Unit Conforming to part 3 of
BS-EN60439 : 1991 ( Annex ZA of Corrigendum June 2006 )
Are Considered Adequate for a Prospective Fault Current of up to 16 kA ,
Provided the Consumer Unit is Fed by a Service Cut-Out having an ( HBC Fuse ) to BS-1361 Type II ,
Rated at Not More than 100A , on a Single-Phase Supply of Nominal Voltage up to 250V

Schedule of Works Required for “ FIRE PROTECTION in a 2-Storey Semi-Detached / Terraced House :eek:

“ To Provide Adequate Means of Escape in Case of Fire “

Provide and Fix a Half-Hour Door ( FD ) FD-30S to any Room Other than a Bathroom or Water Closet ( WC ) which Opens onto the Ground Floor
Hallway or First floor Landing , Conforming to British Standards ( BS ) BS 476: Parts 22,23 / 31.1 Installation to BS-8214:1990
This will Normally Include the Ground , Floor Kitchen , Ground Floor / Lounge / Dining Room & the Fist Floor Bedrooms ,
These should be Hung on Three Hinges , which Comply with BS-EN 1935 ( European Notation ) to Leave Gaps Not Greater than 4mm ( Millimetres )
To the Head and Stiles and Not More than 8mm at the Bottom ,
If a Production Size Fire Door will Not Provide a Minimum Overall Gap of 4mm & 8mm Respectively the Either :-
(a) a Single Strip of Hardwood Lipping may be Glued and Pinned to the Door Edges :
(b) a BS-476 Fire Door Blank May be Cut to Size and the Vertical Edges Finished with Hardwood Lipping as Above :

1.2 insert a Combined Intumescent Strip / Smoke Seal to Routed Edges of the Stiles and Top Rail of the Door ,
Alternatively the Strip can be Fitted to the Jambs and Head of the Frame or Lining ,

1.3 Door Stops Do Not Need to be Changed Providing they are Sufficient to Retain the Door , if New-Planted Stops are Fitted they Must be
Fixed by 38mm No 10 Screw at 230mm Centres

1.4 Provide and Fix the Following Ironmongery :
1 . Self Closing Device of an Approved Type ( Perko , Briton , Dorma or Similar )

Garden Gate Type Springs and Rising Butt Hinges are NOT Acceptable :
2 . Latch – Mortice Latch , Tubular Mortice Latch , Mortice Sash Lock , all Complete with Suitable Knob or Lever Furniture ,
Or Cylinder Rim Night latch , we Would Recommend the Fitting of a Combined and Latch Unit , This is Lockable from the Outside
With the Use of a Key , and on the Room Side bt Means of a Thumb Turn ,

Note : Locks Do Not have to be Provided on Internal Doors , However if they are Fitted they Must Meet the Above Specification :

1.5 Exit Doors which are Required to be Fastened During Occupation of the Premises must be Made to Open Easily and
Immediately from the Inside , without the Use of a Key ,

( Fire Signs )
2.1 Provide and Fix to all Doors, a Sign Stating ” FIRE DOOR KEEP SHUT “ in Minimum Lettering of 5mm
2.2 Provide and Fix to any Understairs Cupboard Door , or Cupboard Door Situated off the Ground Floor Hallway or Fist Floor Landing ,
A Sign Stating “ FIRE DOOR KEEP LOCKED “ In Minimum Lettering of 5mm

2.3 All Fire Safety Signs should Comply with BS-5499 : Part 1:1990
2.4 Fire Safety Check List Notices ( as Enclosed ) should be Provided and Sited on the Inner Faces of all the Doors ,
 
Last edited by a moderator:

Reply to ***Useful Information For The Working Sparky*** in the Australia area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
633
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock