Discuss Valves on a combi volt free in the Central Heating Systems area at ElectriciansForums.net

Reaction score
60
Hi all,

got a combi boiler with volt free switching for the central heating all working fine, I put a conservatory up and put underfloor heating in , I asked the plumber to put a value on the UFH pipe and the CH Pipe so I could control them separately , from a salas wireless programmable stat, so basically a s plan. I've come to wire it but having problem as the combi is volt free and I can't see how to open the valves without putting 230v to the boiler sw. Any ideas?
Cheers
grand
 
Wont the valves be opened by the stats controller and the paralleled micro switches signal the boiler with its own go signal of whatever voltage?
 
Wire it up as if its a standard 2 port system. You will need a 240v supply thru your stat to open the valve and the stat terminals on the boiler should go thro the valves switch, which would be volt free. It would be the same for both valves.
 
Wire the 240volt side to work the motor side of the valve, feed this from your wireless stat control box then wire the volt free contacts of the boiler onto grey and orange of the valve
 
I've done a lot of heating systems and you do have a bit of an awkward one there. Where is the valve in relation to the boiler? Close by?

Guys this is quite simple. The volt free contacts aren't in the boiler but in the external controls. There's a voltage of some sort coming out of the boiler hence the link you have to remove when fitting the external control.
wire the motor of the valve through a 240v supply via the room stat, blue neutral grey being switched feed from stat.
the grey wire in the valve connects to one of the external control connections in the boiler and the other connection is connected to the orange. This means that the volt fee contacts are in the valve across the switch. They are volt free when no voltage is connected to them but the boiler sends a voltage out of possibly 24v.
the second valve would be exactly the same connections and you can double up the orange and grey cables of both valves as this doesn't affect the switching of the valves independently
i hope this helps, you could draw the wiring out first to follow the switching and then you will probably have the light bulb moment good luck
 
Guys this is quite simple. The volt free contacts aren't in the boiler but in the external controls. There's a voltage of some sort coming out of the boiler hence the link you have to remove when fitting the external control.
wire the motor of the valve through a 240v supply via the room stat, blue neutral grey being switched feed from stat.
the grey wire in the valve connects to one of the external control connections in the boiler and the other connection is connected to the orange. This means that the volt fee contacts are in the valve across the switch. They are volt free when no voltage is connected to them but the boiler sends a voltage out of possibly 24v.
the second valve would be exactly the same connections and you can double up the orange and grey cables of both valves as this doesn't affect the switching of the valves independently
i hope this helps, you could draw the wiring out first to follow the switching and then you will probably have the light bulb moment good luck

youve lost me with your idea there.
 
youve lost me with your idea there.

Try this
from switch spur to a room stat, from room stat to brown and blue of valve
connect grey and orange of valve to external controls terminals in boiler after removing the link
230 volts from the spur via room stat turns valve motor which in turn makes the micro switch close in the valve
the micro switch is connected to the external controls terminals in the boiler.
and bang the boiler fires up (not literally bang)
 
So your connecting the switch wires of the valves together?

Nope the micro switch wires grey and orange are separately connected to each external control terminals in the boiler.
image that the first terminal in the boiler is a feed to a light switch (grey) and the 2nd terminal is connected to the switch line (orange) coming back from the switch
 
But if both valves are in the open position, voltage on the orange and you shut one valve it won't shut until you lose voltage to the other
You have two separate voltage sources, one from the switch spur and one from the boiler completely separate so that it doesn't matter what the valves do it will not affect each other
 
Jesus, I'm pleased you get It redvanman, the grey and the orange on a two port are separate to the 240v side hence giving you the boiler no volt side. Why do electricians find c heating so complicated!
 

Reply to Valves on a combi volt free in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
604
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
925
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock