Discuss Vehicle charging. Earth rods in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Steve93

-
Trainee
Reaction score
15
Just a thought where do you guys put the earth spike in when you install car chargers? Local to the charger? What if it’s a driveway? Slabs block paving etc
 
All situation dependant. if the customer does not want the drive paving taken up then you can clip the earth cable to the house wall and run it to a more suitable spot. I have done one where i ran it along the wall above damp course layer, around the corner and into the flower bed. Customer went round afterwards painted the cable a stone colour! you can put it in conduit if the customer wants it.
Sometimes it cant be avoided though and customer needs to decide if the lifting and resitting of a drive is acceptable given the work they want doing.
Come 18th i am told the dubious practice of a rod not being practical on pme is going, so 99.9% of ev chargers will need a rod or two.
You also have to factor in the need for more than one rod and the distance between them.
Have you got the IET guide for ev installations?
 
Just a thought where do you guys put the earth spike in when you install car chargers? Local to the charger? What if it’s a driveway? Slabs block paving etc
Drill a hole in the slab, paving block, or as above.
 
All situation dependant. if the customer does not want the drive paving taken up then you can clip the earth cable to the house wall and run it to a more suitable spot. I have done one where i ran it along the wall above damp course layer, around the corner and into the flower bed. Customer went round afterwards painted the cable a stone colour! you can put it in conduit if the customer wants it.
Sometimes it cant be avoided though and customer needs to decide if the lifting and resitting of a drive is acceptable given the work they want doing.
Come 18th i am told the dubious practice of a rod not being practical on pme is going, so 99.9% of ev chargers will need a rod or two.
You also have to factor in the need for more than one rod and the distance between them.
Have you got the IET guide for ev installations?
Yeah I have the code of practice done the course yesterday just looking at situations where like I said drives etc. But I suppose there no easy way of doing it you need a rod no matter what whether it’s lift the drive or run it elsewhere I guess
 
Never have & probably never will install an EV charger. Never read the CoP etc.

However, I'm just curious. I know the current regs are a bit vague on PME use on 'outdoor' chargers. I came across this one the other day, and I note is states it can be used without installing a rod on a TN-C-S supply. Is this a common product?
 

Attachments

  • EV POD.pdf
    305.6 KB · Views: 20
All situation dependant. if the customer does not want the drive paving taken up then you can clip the earth cable to the house wall and run it to a more suitable spot. I have done one where i ran it along the wall above damp course layer, around the corner and into the flower bed. Customer went round afterwards painted the cable a stone colour! you can put it in conduit if the customer wants it.
Sometimes it cant be avoided though and customer needs to decide if the lifting and resitting of a drive is acceptable given the work they want doing.
Come 18th i am told the dubious practice of a rod not being practical on pme is going, so 99.9% of ev chargers will need a rod or two.
You also have to factor in the need for more than one rod and the distance between them.
Have you got the IET guide for ev installations?

An earth cable should not be clipped direct to bs7671 as its sheath does not have u/v protection. Should be in conduit. Tin hat.
 

Reply to Vehicle charging. Earth rods in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
937
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
275
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
3K
Hello all, I need to have an electric car charger installed but at the moment I'm puzzled about what my options are. My garage is at the back of...
Replies
4
Views
653
I will describe my problem in as much detail so you guys might be able to answer my question. I am never home, my Electric bill is $ 28 to $30 a...
Replies
23
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock