Hi,
I know how to calculate volt drops on radial ccts, As a ring main is a loop and you ignore any spurs is there a voltage drop or is it considered to perfect or near perfect mains voltage regulation!.
How do you,or dont you verfiy votage regulation on a ring main when certifing that you have checked volt drops.
Perhaps you just have to accept the max length and Zs rules for a ring main

If I am missing something please excuse me for wasting your time.
Greeny
 
Hi,
I know how to calculate volt drops on radial ccts, As a ring main is a loop and you ignore any spurs is there a voltage drop or is it considered to perfect or near perfect mains voltage regulation!.
How do you,or dont you verfiy votage regulation on a ring main when certifing that you have checked volt drops.
Perhaps you just have to accept the max length and Zs rules for a ring main

If I am missing something please excuse me for wasting your time.
Greeny

It's near enough impossible to calculate volt drop at any particular point on a ring.

This is why they quote max. circuit lengths in BRB.

Calculating volt drop on a lighting circuit is pretty much impossible as well:)

The only circuits that you can accurately calculate are single load radial circuits e.g. cooker, shower,

immersion etc.
 
You're right the calc for VD on a ring final is different to a radial type circuit.....

As long as the maximum circuit lengths specified in BS 7671 are adhered to (checked when end to end resistances are measured) then your VD will be well within limits as the maximum circuit lengths are calculated primarily using the VD constraint.
 
If you need the formula its Max Length = Voltage Drop x 1000
--------------------------------------------------mva/m x Design Current


Chris

dashes for correct layout only
 
Last edited by a moderator:
If you need the formula its Max Length = Voltage Drop x 1000
--------------------------------------------------mva/m x Design Current


Chris

dashes for correct layout only


Not quite correct for a Ring Final mate.....

Lvd =

______4 x max permitted vd x 1000_
_________Ib x (mV/A/m) x Ct______

Which gives....4 x 11.5 x 1000 / 26 / 18 / 1 = 98.3M.
 
Last edited by a moderator:
Hi,
I know how to calculate volt drops on radial ccts, As a ring main is a loop and you ignore any spurs is there a voltage drop or is it considered to perfect or near perfect mains voltage regulation!.
How do you,or dont you verfiy votage regulation on a ring main when certifing that you have checked volt drops.
Perhaps you just have to accept the max length and Zs rules for a ring main

If I am missing something please excuse me for wasting your time.
Greeny

Voltage drop may be evaluated by measurement or by calculation and is not normally required during the initial verification of an installation. 612.14

This is another confusing reg so when has it to be verified on an EIC if it is not normally required to be verified. Reading that reg you could put non applicable in the relevant box.

Anybody any ideas on this?
 
We were having this very conversation only the other day.

If it doesn't have to be verified on initial verification then when does it????

Yet another contradiction in ol' red.....cant wait for the ammendments....:rolleyes:
 
Fresh off my exams today and our lecturer told us it would normally only be calculated on periodic inspection. I am super green though, but that's what we were told.
 

Reply to Verification of volt drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hi, I'm currently doing my assignment for 2357 and was just making sure I'm calculating the cable length for the lighting circuits right. As...
Replies
1
Views
2K
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
hi This is just a starter because I haven't done any measurements yet (I was a guest there) and what I can do will be restricted as this has never...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock