  1. lucus
    Offline

    lucus Regular EF Member

    hi all hoprfully someone here can answer this question for me: i tested a sub mains today and i only got 0.35 KA is this normal for a submains as at the main mainsboard the pfc is 3.3 KA the main fuseboard has a rcd main switch so at the submain i had to use no trip pfc not sure is this makes and difference any imput would be great.
    regards
     
  2. Sintra
    Offline

    Sintra The Innkeeper Staff Member Admin

    Location:
    Belfast/London
    Did you test Zs at sub main and if so what was this reading.
     
  3. lucus
    Offline

    lucus Regular EF Member

    hi
    yes zs was 0.36 the submain is fed via a 6mm armoured cable
     
  4. marcusone
    Offline

    marcusone Electrician's Arms

    Location:
    Bristol
    Hi Lucus

    What was your Zs at the sub main ? It will be higher than at the origin so therfore the PFC will be lower.

    So as long as all protective devices throughout the installation have a breaking capacity equal to or more than the origin main protective device,then recording the origin PFC is good enough.

    Mark
     
  5. pevvers
    Offline

    pevvers Electrician's Arms

    Location:
    London
    That PFC would be for a Zs at the board at around 0.65 ohms. So not sure where you're going wrong there.... You should be getting a PFC of around 0.68kA if all correct.
     
Loading...
Similar Threads - very submain board Forum Date
Domestic installation advice very old property Electrical Wiring, Theories and Regulations Thursday at 9:01 AM
Water, water everywhere........ Electrical Forum Feb 7, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job