I might be overlooking something that's right under my nose but opinions would be much appreciated. I visited a customer today with a detached garage supplied with power from a 13a RCD fused spur in the conservatory [spurred off RFC].
The RCD is 'tripping' randomly so I went to investigate.
The unit in question must be around 15 years old or more and immediately I found that the test button did nothing, a test at a garage socket also failed at x1 and x5 and the RCD refused to operate and I then found the same with the load disconnected testing at the spur itself. [SFCU in case of pedantry].
So after isolating and doing an insulation resistance test at 250v with everything switched on in the garage [freezer and lights] which showed around 40 Megohms L-E & N-E I fitted a brand new BG Nexus RCD SFCU, upon powering up the test button worked perfectly but in the garage both my tester and Kewtech plug in socket tester are showing L-E reversed !
With the supply and load cables connected together everything is fine [Highest Zs is 0.79 at the furthest garage socket].
So I have another replacement unit to fit tomorrow, it has to be that, right ?
I can't think of anything else which could cause this but opinions are most welcome even if I'm being dumb.
Sorry about the long winded tale !
The RCD is 'tripping' randomly so I went to investigate.
The unit in question must be around 15 years old or more and immediately I found that the test button did nothing, a test at a garage socket also failed at x1 and x5 and the RCD refused to operate and I then found the same with the load disconnected testing at the spur itself. [SFCU in case of pedantry].
So after isolating and doing an insulation resistance test at 250v with everything switched on in the garage [freezer and lights] which showed around 40 Megohms L-E & N-E I fitted a brand new BG Nexus RCD SFCU, upon powering up the test button worked perfectly but in the garage both my tester and Kewtech plug in socket tester are showing L-E reversed !
With the supply and load cables connected together everything is fine [Highest Zs is 0.79 at the furthest garage socket].
So I have another replacement unit to fit tomorrow, it has to be that, right ?
I can't think of anything else which could cause this but opinions are most welcome even if I'm being dumb.
Sorry about the long winded tale !