Hi, Thanks in advance for any advice!
I was called out to a client’s swimming pool, as there was a fault on the pool lights. I found that someone had installed 2 x 12 volt 300 watt lamps, recessed underwater into the pool walls, using 10mm cable in parallel so that there are 2 neutrals and 2 lives at the transformer. Neither light was working. I found that the transformer situated in the pool plant room was 40 meters away from the furthest of the 2 pool lights, which seemed an excessive distance to me. I also found that a 50 Amp fuse had been fitted in between the secondary 12-volt side of the transformer and the lights and this had burnt out, so causing the problem. My question is this, is the calculation to measure voltage drop on a 230-volt AC circuit the same that I must use to calculate the voltage drop on a 12-volt AC circuit? The reason I ask is because when I use the normal formula i.e.
4.4 (volt drop per A per mtr for 10mm cable) x 25A (load of 1 x 300w lamps) x 40 (cable run in meters) - Divided by 1000 = 4.4 volts
I can't imagine that this can be right as even using 16mm cable with a Vd/A/mtr of 2.8 the volt drop would still be 2.8 volts.
in fact using this formula I would need to fit the transformer no more than 5 meters away to achieve a volt drop of no more than 3%
(4.4 x 25 x 5) / 1000 = 0.55 volts = load voltage of 11.45 volts
Although I've not worked on pool lights before, I have seen many pools where the plant room is 10 or 15 meters away so I’m guessing that I need to alter the equation for 12 volt systems but not sure how.
Again, many thanks for any help, Phil.
I was called out to a client’s swimming pool, as there was a fault on the pool lights. I found that someone had installed 2 x 12 volt 300 watt lamps, recessed underwater into the pool walls, using 10mm cable in parallel so that there are 2 neutrals and 2 lives at the transformer. Neither light was working. I found that the transformer situated in the pool plant room was 40 meters away from the furthest of the 2 pool lights, which seemed an excessive distance to me. I also found that a 50 Amp fuse had been fitted in between the secondary 12-volt side of the transformer and the lights and this had burnt out, so causing the problem. My question is this, is the calculation to measure voltage drop on a 230-volt AC circuit the same that I must use to calculate the voltage drop on a 12-volt AC circuit? The reason I ask is because when I use the normal formula i.e.
4.4 (volt drop per A per mtr for 10mm cable) x 25A (load of 1 x 300w lamps) x 40 (cable run in meters) - Divided by 1000 = 4.4 volts
I can't imagine that this can be right as even using 16mm cable with a Vd/A/mtr of 2.8 the volt drop would still be 2.8 volts.
in fact using this formula I would need to fit the transformer no more than 5 meters away to achieve a volt drop of no more than 3%
(4.4 x 25 x 5) / 1000 = 0.55 volts = load voltage of 11.45 volts
Although I've not worked on pool lights before, I have seen many pools where the plant room is 10 or 15 meters away so I’m guessing that I need to alter the equation for 12 volt systems but not sure how.
Again, many thanks for any help, Phil.