Discuss Volt drop question in the UK Electrical Forum area at ElectriciansForums.net

P

Patrick Griffin

Hi everyone,

I am intending on working in the uk shortly, i am from ireland and dont have the uk regs presently.

I am trying to prepare for the exmas i will face and the cable calculations/volt drop calculations are something i cannot remember doing here in ireland in my college time so my understanding is rather weak. I have been googling away like mad today and i have 1 or 2 questions someone maybe able to answer for me, i have no doubt they are basic, for you, so here it goes..

The formula mVxAxM divided by 1000= VD

I understand that A=amps, M=metres but what does the 'mV' mean and where is its figure derived from? I am assuming its in the regs somewhere but what it stands for i have no idea.

Thanks in advance!!
 
Millivolts is the first thing i thought of too just didnt see how it was applicable here, however i do now, was a bit obvious infact.

In order to find the required mV in the recs what information do i need? Cable size and install method only?
 
you need to knowe the design current and the length. also the permitted VD. ( 11.5V except for lighting, which is 6.9V.) this will then give you a value for mV/A/m, which you then match to cable size from 4D1, as snowhead stated.
 
Hi Patrick..

Have a look in appendix 4 (BS7671) for the Volt Drop tables. They will give you mV figure you are looking for.

The actuall figure from the tables is mV p/Amp p/metre (i.e mV/A/m) so the figure is the amount of millivolts that will be dropped per amp per meter. You find the figure by using the correct table (based on whether it is single/multi core etc) and then it is based on the CSA of your cable.

Pop the figure into the equation you already have and that will give you your volt drop for that installation.

Maximum permissable VD for sockets is 11.5V and for light it is 6.9V.

Some worked examples for you:

http://www.tlc-direct.co.uk/Book/4.3.11.htm

Good luck.
 
Thanks lads, the penny is dropping.

Happyhippydad (love the username btw) thanks alot for the link, you simplified it beautifully!!

Cheers again appreciate it.
 
And remember to divide the multiplied figures by 1000. (the volt drop equation is in millivolts not volts)

Also remember to include the correction factor figures for your installation methods.
Sometimes the difference is quite a surprise to the final figures.
 
Last edited by a moderator:
With regard to correction factors, is it common practice to use these or would one just use an educated guess for the required cable size and use the volt drop formula to ensure that the volt drop isnt over the
maximum value?
 
With regard to correction factors, is it common practice to use these or would one just use an educated guess for the required cable size and use the volt drop formula to ensure that the volt drop isnt over the
maximum value?

You would follow the guidance and formulas laid out in appendix 4, section 5.

When burying a cable in insulation can halve it's CCC you can't rely on rule of thumb for accurate cable sizing.
 
How old is that? As I notice it is recommending a 4% (9.2V) volt drop when cables are fully loaded as opposed to the 3% (not lights) and 5% (lighting) currently required by 525.101 and Appendix 4 section 6.4.

Crikey, did not spot that...
Sorry for posting up misleading information, glad you are on the ball Richard ! I did think the Cr factor should have been Cf, but thought it was just a "napit anomaly" rather than outdated information.
 

Reply to Volt drop question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
587
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
836
I am working on a RV Park and I have a question. I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and...
Replies
0
Views
195

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock