Which table do you use in BS7671 for volt drop for LSF Twin and Earth? There does not appear to be a table for LSF cable. 4D5 refers to the grey PVC cable and is not the right one to use for the white LSF. Any help would be appreciated.
If you visit any cable manufacturer website it will say that the LSF cable is rated at 90c. Thermosetting insulated and thermoplastic sheathed.
Ok thanks mega man. Now which table would you use to calculate the current carrying capacity of LSF twin and earth which has thermosetting insulation and thermoplastic sheath with an operating temp of 90c?
You can only run a cable at 90degrees if the items it connects too are also rated to 90degrees.
If you visit any cable manufacturer website it will say that the LSF cable is rated at 90c. Thermosetting insulated and thermoplastic sheathed.
I understand what you are saying but my calcs need to be spot on and need to use the correct table. Regarding your point on operating temp of equipment. I totally agree. Most distribution board manufacturers state that their equipment is rated at 70c. However a cable rated at 90c is still ok to use. Just because you use a 90c cable it does not mean that it will be 90c at the point of termination into accessories.
Think i know that, I really can't see your point now, we are talking miniscule differences and seeing as your cables won't be operating at 90C, the 70C tables will be giving you the more realistic/accurate values of mV drop to be expected...
Think i know that, I really can't see your point now, we are talking miniscule differences and seeing as your cables won't be operating at 90C, the 70C tables will be giving you the more realistic/accurate values of mV drop to be expected...
It won't no, but the 90c table with XLPE insulation will allow a greater CCC and therefore will give a greater mV drop. All be it a pretty miniscule one....
2.5 is 18mv/a flat twin 70oC
2.5 is 16mv/a 90oC
I cant find a table for lsf twin though only multicore lsf
I give up!! lol!!