Posting a message to the forum will remove the above advertisement

  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. Electrical 2 Go - Electrical Supplier and Electrical Wholesalers

    Please visit our prime electrical forum sponsor - they have the best tools at the best prices. If you find a price better somewhere else, call them or contact them, and they may be able to beat it for you. Especially on an order of a few items.

    Dismiss Notice

Discuss Volt drop in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Farmelectrics
    Offline

    Farmelectrics Farmelectrics Electrician's Arms

    Location:
    Wirral
    Business Name:
    Farm electrics
    Ok you do all your calculations to determine your volt drop and your calcs come back that the volt drop is just above the 5% allowed ok I no it dosnt conform to bs7671 and you should increase the csa of the cable to next size up but what effect or could some one explain in simple terms the problem we could face if we didn't
     
  2. plugsandsparks
    Offline

    plugsandsparks Electrician's Arms

    Location:
    Chesterfield
    Most obvious is that some fluorescents wont fire up or keep dropping out.
    TBH i often look at the supply voltage as well cos i keep coming across quite high voltages often in excess of 240, so a bit of drop is sometimes welcome.
    Not BS7671, i know, but how the DNo get away with supplying 253V makes 5% somewhat irrelevant.
    If your supply is already at the lower end e.g. 220 then you really dont want to drop anymore as lighting will be less effective, heating will take longer to work, but at least electronic equipemnt should be OK.
    Dont forget its also based on how much current you will pull in your calcs :)
     
  3. Knobhead
    Online

    Knobhead Guest

    -5% of +10% or -10% of 230V @ 2A or maybe 7.5A or it could be 6.584753A ? ? ? ?
    What was the question ? ? ? ?

    My brain hurts ! ! ! !
     
    • Like Like x 1
  4. Farmelectrics
    Offline

    Farmelectrics Farmelectrics Electrician's Arms

    Location:
    Wirral
    Business Name:
    Farm electrics
    Keep it simple tony lol
     
  5. Welchyboy
    Online

    Welchyboy Guest

    You can't really make any assumptions on the DNO voltage as this will fluctuate dependent on the load as well as your circuits
     
  6. kingeri
    Offline

    kingeri Electrician's Arms

    Location:
    Yorkshire
    I do voltage drop calcs at the nominal voltage of 230v. You can measure the DNO's voltage one day and find it to be different the next day! It's hardly a major issue in most cases, unless you have very long cable runs and/or huge loads.
     
Loading...
Similar Threads - Volt drop Forum Date
Volts drop when 2.5kW (ish) load switched on Electrical Forum Apr 21, 2019
Volt drop Question SWA Electrical Forum Mar 22, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job