Discuss Volt Stick Strangeness in the Canada area at ElectriciansForums.net

C

compaq

We got called to a house today for a minor works job.
TNC-S system, all electric night storage heating and immersion heaters.
While we were there we noticed our Volt Stick was lighting up on the pipework and cylinder in the airing cupboard.
The pipework was not live as we had been lent against it while working next to it.
The main bonding was in place to the water main, we tested continuity between the water main and the cylinder and pipework, it was fine.
The pipework was cross bonded fine.
We tested continuity between the main earthing terminal and the pipework, it was fine.
We then got interested and found that the Volt Stick only lit up on pipework in the immediate vicinity of the airing cupboard.
We then tripped off the mcb to each circuit in turn and found that the Volt Stick did not light up on the pipework when the lighting circuit was switched off.
We then pulled the lighting circuit out of the consumer unit and carried out insulation test on it, it was fine.
Carried out Ze, Zs tests, all fine.

Has anyone else experienced anything like this before?
 
mmm strange one! them volt sticks can be tempremental at the best of times but only getting the glow when the lighting circuit is energized! i was always lead to beleive the volt stick works on emf's and static when you rub it on ya trouser leg? could the pipework somehow be running in close proximity to a lighting cable and picking up some sort of emf this way??

rich
 
Thanks for your reply.
After talking about it today, we reckon that one of the pipes is resting heavily on one of of the lighting cables up in the roof.
Another sparky said that he had a similar volt stick light up on the fibreglass insulation in the roof, this was found to be caused by some flooring board squashing a lighting cable against a joist, when he removed the board, the volt stick stopped lighting up on the fibreglass.
Stange business isnt it.
 

Reply to Volt Stick Strangeness in the Canada area at ElectriciansForums.net

Similar Threads

I found myself needing to do some emergency plumbing at home this evening. I've got a small guest flat on my property which has been empty for...
Replies
1
Views
448
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
601
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
536
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
796

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock