Discuss Voltage droop in the The Welcome Forum area at ElectriciansForums.net

K

Kris uk

Hi guys and girls I'm new to the forum and it's probably on here somewhere but could someone please tell me a simple way of calculating volt drop as I'm not having much joy with the Maths side of things and I've got my 2391-10 in two weeks as easy as possible plse
 
there's only 1 way. multiply the mV/m by the length then the current then divide by 1000
 
Hi & welcome. :)
 
the calculation gets more complex if all the load is not at the end of the circuit, say, a lighting circuit with the loads spaced along it. e.g. 10 lights, 100watts each. spaced along the run. VD at 1st light will be calculated at 1000watts for the length from source, 2nd VD will be 900watts fot it's length , etc. till the last will be 100watts at the full length of the cct.
 
There was a post re max length of ring final cct but I cant seem to find it.

The calc was Max VD x 4 x 1000 / Ib x mv/A/m can someone shed some light on this one?
 
The calc was Max VD x 4 x 1000 / Ib x mv/A/m can someone shed some light on this one?

that would give an approx. length of a 2.5mm RFC at 30A of 90m, which seems about right. not seen the formula before now, though.
 
there's only 1 way. multiply the mV/m by the length then the current then divide by 1000

It's not the only way.... ((R1+Rn) x 1.2) x Ib is another way (V = I x R)

The calc was Max VD x 4 x 1000 / Ib x mv/A/m can someone shed some light on this one?

that would give an approx. length of a 2.5mm RFC at 30A of 90m, which seems about right. not seen the formula before now, though.

It's in the Electricians Installation Design Guide. For a radial it is (MaxVD x 1000) Ă· (Ib x mV/A/m)
 
the mv/A/m values for say 2.5mm is 18. so can use this as your R1+R2 per meter of 2.5mm

so an immersion heater circuit would be 11.5 x 1000= 11500 / 13.04 x 18 =11500 / 234.72 = 48m length



It's not the only way.... ((R1+Rn) x 1.2) x Ib is another way (V = I x R)



It's in the Electricians Installation Design Guide. For a radial it is (MaxVD x 1000) Ă· (Ib x mV/A/m)
 
Can any one tell me how to calculate the milli volts per meter from theese measurements load current 45amps .circuit length 80m .live conductors 10mm.m ohm/m at 20 degrees c 1.83
 
Can any one tell me how to calculate the milli volts per meter from theese measurements load current 45amps .circuit length 80m .live conductors 10mm.m ohm/m at 20 degrees c 1.83

VD = (((R"1+R"n) x Cr) x L x Ib) Ă· 1000
VD = (((1.83+1.83) x 1.2) x 80 x 45) Ă· 1000 = 15.81V

Cr = Correction factor for 70°C
R"1 = mΩ/m of line conductor
R"n = mΩ/m of neutral conductor
 
tell me a simple way of calculating volt drop as I'm not having much joy with the Maths side of things and I've got my 2391-10 in two weeks as easy as possible plse

You asked for easy
:28:
Measure the voltage at the supply and deduct the voltage at the extremity,simples
:blush5:​
 
bloody 'ell ,des. you just made me choke on my beer.
 

Reply to Voltage droop in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
760
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hello everyone, I really hope this isn't an idiot question but boy, I'm out of my depth! I've spent about 3 weeks (not solid mind) trying to work...
Replies
13
Views
2K
This might be long so feel free to grab a brew. So, as some of you may know, i'm a 34 year old who has been dying to get into the industry. I...
Replies
66
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock