  1. TaffyDuck
    Offline

    TaffyDuck Electrician's Arms

    Just been asked to go and check out a new agricultural barn wired up by a builder. The barn is 350m from the house ( where they have fed it from a socket in the living room) and they have fed it with 1.5mm two core SWA." because its only a socket and a couple of lights".
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    no problem. fit a 110 socket and step up transformer. and some 110v site lights on a string.
     
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    top of me 'ed without looking up 13A would just about give a VD of 110V, so ideal for the odd 110V power tools.
     
  4. Mark_Burgess
    Offline

    Mark_Burgess Electrician's Arms

    Location:
    ..........
    Did you measure the VD, I'd like to know how accurate the book figure is to the real thing.
     
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    the book gives a VD of 130v at 13A, so i was close. like to know a real life figure. of course he could always DUCK out of this one
     
    • Like Like x 1
  6. TaffyDuck
    Offline

    TaffyDuck Electrician's Arms

    Well i only had my little fluke T100 on me, so no accurate reading, well below 200V though and I wasnt going to trudge quarter of a mile back down a hillside to get the megger but tel is about right. will get a proper reading at the end of the week but I make it, on paper a VD of 140V!!!!!!

    0.031 x 13 x 350
     
    Last edited: Feb 27, 2012
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    looks like 25mm will be needed as minimum. that will give around 6V VD at 10A.
     
  8. TaffyDuck
    Offline

    TaffyDuck Electrician's Arms

    I guessed at that onsite, 25mm 3 core x 350m = BIG MONEY and the will have to bury it again lol
     
  9. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    be cheaper to use a genny.
     
  10. TaffyDuck
    Offline

    TaffyDuck Electrician's Arms

    absolutely right, either way not my problem thank god. Whats 3c 25mm SWA at the moment £5 a meter at least I would think. Thats £1750.....ouch
     
    Last edited: Feb 27, 2012
  11. Dunc
    Offline

    Dunc Guest

    Just for giggles I'd like to see someone try making that off in to the back of a FCU! :p
     
    • Like Like x 2
  12. TaffyDuck
    Offline

    TaffyDuck Electrician's Arms

    lol, very true. Havent even added a bit for 3 x armoured resin joints, they will add a fair bit of VD to the system
     
  13. JD6400
    Offline

    JD6400 Forum Mentor

    Location:
    ?
    Now that connection in the back of the living room socket will be worth a photo ! :grin:

    (I must improve the speed of my typing , been beaten to it yet again !)
     
    Last edited: Feb 27, 2012
  14. SPARTYKUS
    Offline

    SPARTYKUS Electrician's Arms

    Location:
    Shropshire
    Can you get 200mm DG surface patressses
     
  15. HandySparks
    Offline

    HandySparks Forum Mentor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    Still, you could always leave the existing cable in as an independent lighting supply. You can fit up to 145W and stay within the 3% VD!

    Edit: You might have to put it on a 3A breaker to meet the Zs though.
     
    Last edited: Feb 27, 2012
Loading...
Similar Threads - Voltage drop taken Forum Date
Domestic Protection Against Voltage Disturbances Electrical Wiring, Theories and Regulations Thursday at 2:15 PM
New to forum, Is it just me!! how have I got Voltage?? New Member Introductions Jan 10, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job