Discuss Voltage Drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
9
We are all familiar with the requirements for measuring Zs and verifying that it is within the limits for the particular type of protective device. I use a single guide of 1.2 ohms as the maximum though there are of course many variations.

What we (I) have not been noting is (R1+ Rn) and the implicite voltage drop associated with it.

A quick calculation shows that if Zs for a ring circuit were 1.2, and we assume a generous 0.20 for Ze,
Then R1+R2 = 1.0, and assuming the circuit wired with 2.5/1.5 then R1 = 0.4 so (R1+Rn) = 0.8.

Now 0.8 ohms at 32A gives a voltage drop of 25.6 volts. MORE THAN DOUBLE that allowed for power circuits.

So should we be looking for a maximum Zs of 0.48 ohms to ensure the voltage drop requirement is satisfied?
 
If we use a standard ring circuit,we are constrained by the length we are permitted
I believe the standard ring circuit limits the length, to ensure that voltage drop is within limits without needing calculation to prove it

Table 7.1 of the on site guide, gives max lengths where voltage drop is the limiting factor
 
Last edited:
Its a good point but I don't believe the area limit will keep the Zs down. I have just counted the number of rings I have tested and found that ~ 60% have Zs > 0.5 ohms.
 
We are all familiar with the requirements for measuring Zs and verifying that it is within the limits for the particular type of protective device. I use a single guide of 1.2 ohms as the maximum though there are of course many variations.

What we (I) have not been noting is (R1+ Rn) and the implicite voltage drop associated with it.

A quick calculation shows that if Zs for a ring circuit were 1.2, and we assume a generous 0.20 for Ze,
Then R1+R2 = 1.0, and assuming the circuit wired with 2.5/1.5 then R1 = 0.4 so (R1+Rn) = 0.8.

Now 0.8 ohms at 32A gives a voltage drop of 25.6 volts. MORE THAN DOUBLE that allowed for power circuits.

So should we be looking for a maximum Zs of 0.48 ohms to ensure the voltage drop requirement is satisfied?

The maximum length of a ring wired in 2.5/1.5mm² (limited by voltage drop) is 106m from table 7.1 OSG

4*(11.5 * 1000) / 26 / 18 / 0.923 = 106m (Type B BS 60898 MCB)

This gives you a max Zs of 1.42Ω at 70°C or 1.13Ω when tested at 20°C (worst case TN-S) to ensure you are within voltage drop limits. Obviously, the lower your Ze is, the lower the max Zs will become with regards to voltage drop.

106 * ((19.51 / 1000) * 1.2) / 4 + 0.8 = 1.42Ω (70°C)

1.42 * 0.8(rule of thumb) = 1.13Ω (20°C)


This satisfies the max Zs value of 1.44Ω (70°C) / 1.15Ω (20°C) from table 41.3 of BRB
 
Last edited by a moderator:
Also just worked out that an R1+R2 of 1.0Ω on a ring circuit gives you a circuit length of 215m....

(1 x 4) ÷ (19.51 ÷ 1000) = 215m

...which is more than double what the maximum length from Table 7.1 OSG is for a ring circuit, and as such the voltage drop is more than double.
 
Last edited by a moderator:

Reply to Voltage Drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
722
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Hi, I'm currently doing my assignment for 2357 and was just making sure I'm calculating the cable length for the lighting circuits right. As...
Replies
1
Views
2K
Hi all, I am currently doing my 2391-52 and have been given a mock paper, one of the questions is around vold drop as per below, can someone...
Replies
20
Views
5K
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock