Discuss Voltage drop in the Australia area at ElectriciansForums.net

H

hogan

How do we calculate voltage drop on a ring final sockets only, Given the length of the circuit is 40 meters the cable is 2.5mm so therefore the amp per meter is 18, the mcb is 32 so is it 40 x 18 x 32 / 1000 = 23.04 but thats more than 5% = 11.5. Do we not use the mcb for socket outlets as we could not get a run bigger than 20 meters in 2.5mm.
 
table 7,1 page 40 osg gives you maximum lengths of cable for various circuits to account for maximum allowed volt drop....
saves time on calculations:)
 
Hi

In a ring circuit in effect two cables are run so your mv/A/m value is halved whereas the length of the cable to the farthest point is half the length of the cable in the ring giving you a multiplier of 4.

23.04/4 = 5.76V.

Dont forget the max circuit length for a 32A 2.5mm ring is 100mSq and they use the max volt drop to calculate this.

The current in a ring circuit isn't the same all the way round so technically you dont use the 32A rating of the breaker as the max would be 26A.

Hope this helps.
 

Reply to Voltage drop in the Australia area at ElectriciansForums.net

Similar Threads

Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
761
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
909

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock