rwb

hello all,
Just revieced a call from a colleague asking what maybe causing him to be getting a reading of 97 volt on the main incoming earth? would welcome any ideas sorry its a bit vague but this is about all the information that I have currently.
 
sounds like his main earth is floating. 97 volts, if he's got it right needs investigation urgently.
 
what is he using as a reference point? 97volts between the main earth and what?
 
Floating external earth or maybe an internal short. If they can isolate all of the circuits, get them to check it again once isolated and see if it's still present. Then check again once the circuits are back on (if it went and it's now back again it's an internal fault).
 
Floating external earth or maybe an internal short. If they can isolate all of the circuits, get them to check it again once isolated and see if it's still present. Then check again once the circuits are back on (if it went and it's now back again it's an internal fault).

The voltage was measure between the earth from the board and the suppliers earth block. When all MCB are turned off there is 0 volt but increase up to 97 as each circuit is turned back on.

Checked supply it is TNCS so could be the neutral causing backfeed down the earth.


WELLIES it is then
 
Last edited by a moderator:

Reply to voltage on earth in the Australia area at ElectriciansForums.net

Similar Threads

Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
975
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
737
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock