Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. angel While you're here, would you mind checking out our Electrician's Insurance section to see if we could save you a few quid? - Specifically our Van Insurance Deals and Public Liability Insurance Deals. Thanks for supporting the forum! angel

    5% Discount from Electrical2Go.co.uk for ALL members! - Click Here

  3. Forum for Trainees.

    If you are a trainee and haven’t already applied to join our trainee forum then click HERE The trainee forum is a closed area of the forum where the Forum Mentors will freely share their vast experience within the industry. 

    Dismiss Notice

Discuss Voltage test on 110 transformer in the Periodic Inspection Reporting & Certification area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Jabbajaws
    Offline

    Jabbajaws Electrician's Arms

    Hi All,

    I did a voltage test on the output side of a 110 transformer, the other day, due to a 110 SDS drill that kept cutting out. It turned out to be a loose connection in the drill, but l was somewhat confused by the voltage readings l was getting from the transformer itself.

    L - N = 110V
    L - E = 110V
    N - E = 90V

    During training l was taught that there should be no voltage between Neutral + Earth when taking a voltage reading.

    Is this normal for 110 transformers or is there a problem?
    Not very experienced with transformers, so any input much appreciated. Thanks.
     
  2. i=p/u
    Offline

    i=p/u Electrician's Arms

    i thought you should be getting 55v to earth, showws how much i know
     
  3. telectrix
    Online

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you should get 55V L/E and N/E. ( the N is not actually N ) it's really L1 and L2. the centre of the secondary TX winding is connected to the supply earth, so you should have 55-0-55.
     
    • Like Like x 1
  4. Archy Styrigg
    Offline

    Archy Styrigg Electrician's Arms

    Location:
    Manchester
    Your typical Yellow tranny has a 110V 2ndary winding centre tapped to earth.
    So, as our i=p/u says, +/-55v to earth. They don't have neutral as such.
    I'm confused by your readings. Sould be getting 110 across Line pins and 55 bot lives to earth.

    Either the trannies knackered or you're measuring incorrectly.
     
  5. Jabbajaws
    Offline

    Jabbajaws Electrician's Arms

    Thanks Archy. It was only a quick test with my voltage indicator. I havent used my 17th edition meter on it for an accurate reading but l will do as soon as l get chance. Thanks.
     
  6. Engineer54
    Offline

    Engineer54 Guest

    You should actually be using a pukka voltage tester, for your ''Accurate'' voltage readings, rather than your 17th MFT... Voltage indicator type testers that show you the voltage within an indicated band range, don't cut it these days... Is this the type of volt meter you was using??

    What you should be seeing is ....

    L1 - L2 = 110V
    L1 - E = 55V
    L2 - E = 55V
     
    Last edited by a moderator: Feb 19, 2012
Loading...
Similar Threads - Voltage test transformer Forum Date
Advice on Voltage Testers please. Electrical Tools and Products Yesterday at 11:49 PM
Fluke Product Recall affecting T1xx series voltage testers Electrical Tools and Products Oct 20, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job