  1. harry olee
    Offline

    harry olee Regular EF Member

    Location:
    north
    Should these be always housed in a wago cable retaining box if under plaster board?
     
  2. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi Harry - if you need a maintenance free jb then yes the MF marked Wagobox must be used along with connectors from either their 222 or 773 range. I also use the Ashley J803 which comes in one unit for a fiver. Hope that helps :)
     
  3. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    what do you mean by "under plasterboard"?

    The Ashley Hager J803 and J804 are better IMHO
     
    • Like Like x 1
  4. harry olee
    Offline

    harry olee Regular EF Member

    Location:
    north
    There is no "MF" mark on wago boxes though?
     
  5. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Ahh, there is if you look close :)
    (just ignore the baggy pants sticker)

    View attachment 35376
     
  6. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Awful things those Wago boxes.
     
    • Like Like x 1
  7. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    No they are not, best thing since sliced bread or round Bakelite joint boxes.
     
    • Like Like x 6
  8. Lucien Nunes
    Offline

    Lucien Nunes Mercury Arc Rectifier Trusted Advisor

    Location:
    London
    Wagos themselves come from Germany, are very good and can be used in 1001 situations. The Wagobox is an English accessory that represents our interpretation of what to do with Wagos, and it's not my favourite. It's difficult to get steel conduits into the entries (do you pull out the black bit for 25mm?), while there's not enough depth for MI seals so they have to stay outside. I never work with T+E so I can't say how well that fits in. But seriously, I don't like having the terminals inline with the cable entries - any movement of the cable in the clamp can put tension on the terminals - and there's no option to leave slack for retermination. If you look at a continental-style junction box done the proper way with the separated cable cores marshalled at the back then brought over themselves in a neat row at the front, you will see that it is impossible to stress the connections by moving the cables and there's lots of wiggle-room for maintenance, and it works just as well in adaptables and even BESAs. The Wagos are not locked in as they are in a Wagobox but if you building is shaking about enough for that to make a difference, you have more important things to worry about.
     
    • Like Like x 4
  9. Taylortwocities
    Online

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    So, you are not a fan then;)
     
  10. kingeri
    Offline

    kingeri Trusted Advisor

    Location:
    Yorkshire
    The whole MF thing is over the top IMHO, what's wrong with using MF connectors in a suitable enclosure of your choice? I would much rather use say an adaptable box of my choosing, making sure the cables are secured of course. The wagoboxes are too limiting as to their applications.
     
    • Like Like x 3
  11. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Blimey, never though of using a Wagobox for conduit, MI etc, or is that a have?

    Perfect for joining a few tw&e, don't think they were designed for anything else. Personally only use them for cables up to 2.5mm
     
    • Like Like x 3
  12. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    I quite like Wagoboxes; use a lot of them. But I do agree that they'd be so much better without the internal dividers that lock the Wagos in place. They make it harder to fit and risk stressing the connection.
     
    • Like Like x 1
  13. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    I see absolutely no reason why you can't put them in any suitable enclosure. It is a nonsense to suggest they are only MF if installed in one of those flimsy Wago boxes.
     
  14. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    I agree with you and Kingeri. I use the Line products enclosures, Wiska boxes, other adaptable boxes, and any enclosure I see fit for the purpose.
     
    • Like Like x 2
  15. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    No doubting the common sense of this.
    But apparently Mr Wago used their box and connectors together when being certified as MF. So neither is certified MF by themselves as I understand it.
     
  16. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    I agree but to me it is not the enclosure which is MF. How do you go about fitted half a dozen cables into one.
     
  17. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Heretic! You sound like one of those people who say "Never tried guinness 'cos I don't like it"
     
    • Like Like x 1
  18. PEG
    Offline

    PEG Trusted Advisor

    Location:
    Manchester
    If i had a situation where six separate cables were joined,i would not want it "MF",preferring to choose a better method,and making it accessible.

    .....Or....one i viewed during a recent rip-out,where an enterprising spark,had thrust four joined T&E cables,into a fresh,halved 350ml tube of silicone sealant,and zip-tied it to the studding.
    It looked like a fused stick of gelignite...
     
    • Like Like x 3
  19. LeeH
    Offline

    LeeH Insert witty monkey comment here. Electrician's Arms

    Location:
    Lincs
    I use them inside Wiska boxes. It's just MF as any other plastic box.
     
    • Like Like x 3
  20. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    ot line products "eggs". decent amount of space inside.
     
  21. Hellmooth
    Offline

    Hellmooth Electrician's Arms

    Location:
    Livingston
    Business Name:
    CM Electrical
    I'm the same, I use them pretty much anywhere I am making a connection that would normally be done with connector block or the like.
     
    • Like Like x 1
  22. stevethesparks
    Offline

    stevethesparks Electrician's Arms

    Location:
    Northampton
    That's too much like common sense. Maybe if you could find an adaptable box with the magic "MF" stamped on it, it would be fine ;)
     
  23. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    Wago boxes are good as they will fit through down light holes
     
    • Like Like x 2
  24. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    so will the line "eggs" (50mm diam.).
     
  25. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    That MF stamp is a nonsense.
     
  26. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Love Guinness, not awful like those Wago boxes:)
     
  27. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    When you put it that way, Guinness is always Good.
     
    • Like Like x 1
  28. Ib≤In≤Iz
    Offline

    Ib≤In≤Iz Electrician's Arms

    Location:
    Gloucestershire
    I have used the a couple of times, but if I need more space then a wiska box
     
  29. harry olee
    Offline

    harry olee Regular EF Member

    Location:
    north
    The wagobox enclosure i have purchased for lighting? is the "Wagobox Light" version embossed on the enclosure but there is no MF embossed on the the inside of the lid or elsewhere.
    It is smaller than the normal box but has cable restraints.

    http://www.screwfix.com/p/wagobox-light-junction-box/8423fhttp:
     
  30. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Do they restraints really restrain flexible cords.
     
  31. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    If you need MF then it's got be a Wagobox as per post #5, they're the ones that have been tested and certified and have the approval stamp.
     
  32. Hellmooth
    Offline

    Hellmooth Electrician's Arms

    Location:
    Livingston
    Business Name:
    CM Electrical
    Can you post a link can't find them?
     
  33. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
  34. 7029 dave
    Offline

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    Give me a J601 any day, Dave MF.
     
  35. Hellmooth
    Offline

    Hellmooth Electrician's Arms

    Location:
    Livingston
    Business Name:
    CM Electrical
  36. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    Yes I use them a lot. Mainly for lighting and mainly in lofts and behind downlight holes, so still accessible.
     
    • Like Like x 2
  37. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    I like using the Wagobox in loft space for lighting (when adding fancy luminaires, or Class 2 fittings). The box can be mounted on a vertical batten, so it's visible above the insulation, for when the next poor soul comes along :)
     
    • Like Like x 2
  38. kingeri
    Offline

    kingeri Trusted Advisor

    Location:
    Yorkshire
    I've done this a few times, a bit of wood poking up through the insulation with a JB on it, think last time I used a Hager/Ashley though. Seem to remember it was the height of summer and the loft space was scorching hot, couldn't get out of there quick enough.
     
  39. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Yep I know, love loft spaces, especially in the summer. :mad:
     
  40. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Well if you wanna get out of the loft quick like, use wago!
     
  41. harry olee
    Offline

    harry olee Regular EF Member

    Location:
    north
    I found it very difficult to close the normal wago box lid shut with 4mm twin and earth yet the cable retainer did not seem that secure with 1.5mm
     
  42. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    What size Wagos were you using?
     
  43. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    • Like Like x 1
  44. harry olee
    Offline

    harry olee Regular EF Member

    Location:
    north
    Normal ones not the light version
     
  45. harry olee
    Offline

    harry olee Regular EF Member

    Location:
    north