Discuss Washing machine off boiler circuit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
2
Bonjour I'm a level 3 apprentice at the moment and have a side job to fit a double socket for a washing machine, only power is off a fuse spur supplying a gas boiler, which is also protected by a 13a, is this okay?
 
If the boiler requires a 13A fuse then I would say that it's not ok to add to this supply.
 
what cable/circuit supplies the boiler? it maybe possible to use the 13A FCU to feed the washing machine and then add a 2nd FCU (3A) to spur off to bolier. all depends on existing circuit arrangement.
 
what cable/circuit supplies the boiler? it maybe possible to use the 13A FCU to feed the washing machine and then add a 2nd FCU (3A) to spur off to bolier. all depends on existing circuit arrangement.
Haven't taken it off the wall yet but from what I know, it's off a 13a fuse, don't know what it's wired in yet but from the Spur to the Boiler it's 1.5mm flex, don't know what's going into the spur
 
Haven't taken it off the wall yet but from what I know, it's off a 13a fuse, don't know what it's wired in yet but from the Spur to the Boiler it's 1.5mm flex, don't know what's going into the spur
Depends how the boiler spur is wired, is it off of a RFC or a separate radial solely for the boiler?
 
Nothing wrong with asking questions , but you should have a think about it first before replying , it's okay to ask for pointers but it's not okay to ask someone to tell you how to do the job
 
Nothing wrong with asking questions , but you should have a think about it first before replying , it's okay to ask for pointers but it's not okay to ask someone to tell you how to do the job
Firstly as an apprentice do you expect me to know everything? How am I suppose to learn this trade without asking questions? Did you know how to do everything at 18?
 
Firstly as an apprentice do you expect me to know everything? How am I suppose to learn this trade without asking questions? Did you know how to do everything at 18?

Learning aside - do you have insurance to cover this work? have you told HMRC about your 2nd income? Certificates? Test equipment?
 
Firstly as an apprentice do you expect me to know everything? How am I suppose to learn this trade without asking questions? Did you know how to do everything at 18?
Adam, I suggest you join the Trainee Only section of this forum, get your head in a few books, watch the John Ward youtube videos and scour the internet for answers, then perhaps come here or the trainee section and post a suggested plan of action. Asking such elementary questions would suggest to most you have not tried to research this matter yourself and would like the answer served up on a plate. We are all still learning but perhaps you need to take responsibility for trying to find the answer to the basics first.
 
Don’t get to disheartened with the responses either Adam,this place is an absolute gold mine for training if you ask the right questions and as roly says do a bit of research first and you may find you don’t even need to ask the question, but do keep at it :)
 

Reply to Washing machine off boiler circuit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
457
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
814
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
206
Hi, apologies for the basic question In a radial circuit, is it permissable to spur off the supply side of an existing fused connection unit...
Replies
1
Views
306

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock