Hi just after some advice
Some friends just had a new kitchen fitted, but as far as I can tell there is no main water bonding, I believe that it has to be about 600mm from the ground or there abouts.
If it’s not there will the kitchen need to come out to fit one
 
Hi just after some advice
Some friends just had a new kitchen fitted, but as far as I can tell there is no main water bonding, I believe that it has to be about 600mm from the ground or there abouts.
If it’s not there will the kitchen need to come out to fit one
Regulation BS7671 544.1.2 Without quoting verbatim, bonding is to be applied to the consumers side of the meter where practicable, with 600mm of the meter outlet union, or point of entry to the building, if the meter is external.
Was the Electrical work certified by the Electrician, main bonding should be mentioned on the certificate, but then again if Kevin the Kitchen fitter did the Electrics I would doubt very much if any such certificate was issued.
 
Hi just after some advice
Some friends just had a new kitchen fitted, but as far as I can tell there is no main water bonding, I believe that it has to be about 600mm from the ground or there abouts.
If it’s not there will the kitchen need to come out to fit one
Where are you in the UK?
 
It was done by Phil the kitchen fitter.
The pipe coming in a don’t no, without moving the kick board which has been sealed in.
I thought the main earthing you needed was the water supply and the gas, unless the house was all in plastic pipes.
How do you test with a multimeter if there is no cable??
In yarm in the north east
 
It was done by Phil the kitchen fitter.
The pipe coming in a don’t no, without moving the kick board which has been sealed in.
I thought the main earthing you needed was the water supply and the gas, unless the house was all in plastic pipes.
How do you test with a multimeter if there is no cable??
In yarm in the north east

Your profile suggests that you are a fully qualified electrician.

This is very basic stuff.

You wouldn't use a multimeter to test, test the pipe back to the MET.
 
youmeasure between your MET (main earthing terminal and the copper pipe on your side of the stop cock. if resistance value is > 22 k Ohms, then it's not extraneous. if i't < 1 ohm, then it's bonded anyway.
 
It was done by Phil the kitchen fitter.
The pipe coming in a don’t no, without moving the kick board which has been sealed in.
I thought the main earthing you needed was the water supply and the gas, unless the house was all in plastic pipes.
How do you test with a multimeter if there is no cable??
In yarm in the north east
Anthony, firstly it's not earthing water and gas, it's called main bonding.
Sounds like your Kitchen Fitter didn't know much about Electrics, so there was no certificate then? In order to test to see if the pipes have been bonded a Multimeter will not be applicable
These two videos will go some way to explain.
 
You can test between a local earth connection i.e. a socket outlet and the water service. Provided it's verified that this has a good MET connection. Saves getting the wander lead out!
 
You can test between a local earth connection i.e. a socket outlet and the water service. Provided it's verified that this has a good MET connection. Saves getting the wander lead out!
Sorry Willy, don't agree with your suggestion, far to many Parallel earth paths to make an appraisal as to whether the pipe is bonded.
 
Anthony, firstly it's not earthing water and gas, it's called main bonding.
Sounds like your Kitchen Fitter didn't know much about Electrics, so there was no certificate then? In order to test to see if the pipes have been bonded a Multimeter will not be applicable
These two videos will go some way to explain.
Not seen John Ward before - Very clear and comprehensive presentation!
 
The earthing system has not been stated. If it's TNCS then testing to a local socket or other earth is not sufficient to verify compliance. If the service requires bonding then it will have to be in 10mm minimum which can only be verified by a combination of testing and visual inspection.
 
The earthing system has not been stated. If it's TNCS then testing to a local socket or other earth is not sufficient to verify compliance. If the service requires bonding then it will have to be in 10mm minimum which can only be verified by a combination of testing and visual inspection.
Although this test would prove if the water service was not extraneous and therefore not need bonding.
 

Reply to Water pipe earthing.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
973
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
952
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
196

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock