Hi guys,

I've installed a new c/u for a swimming pool plant room (very small) consisting of circuits for a pump, electrics heater, pool and garden lighting and timer control for the heating/ filtration.

it has an RCD main switch. when commissioning everything worked fine although the pump had no water and was just fired up briefly to check operation. anyway, the pool guy comes back and connects up all the pipework and now when he switches the pump on the RCD trips. I went back and found the fault to be on the lighting circuit so I disconnected it.

Question:
Why would the RCD trip when the pump is started and has no fault but the lighting circuit does?

as always, thanks in advance.
 
Re: Wierd RCD tripping

neutral failt on the light circuit.
 
Re: Wierd RCD tripping

If you have an "up front" RCD, a fault on ANY of the circuits could trip the board - and yes turning on 1 circuit could affect another circuit - as you have seen!
 
Re: Wierd RCD tripping

just disconnected the lighting earth to find the fault. funny thing is that I could connect the earth for the lighting back once the pump was running! if I left the lighting earth connected and then started the pump it would trip every time. lighting circuit is totally dis'd now.

Have you dissed the lighting circuit neutral as well?
 
Re: Wierd RCD tripping

just disconnected the lighting earth to find the fault. funny thing is that I could connect the earth for the lighting back once the pump was running! if I left the lighting earth connected and then started the pump it would trip every time. lighting circuit is totally dis'd now.

Really?
 
Re: Wierd RCD tripping

Probably not the best way to fault find by possibly making the lighting earthing live.

It would be that the majority of the current will flow via the neutral so if at a 6A running current say 10mA was passing through the fault but at 20 or 30A start up current over 30mA would pass through the fault and trip the RCD.
 
Re: Wierd RCD tripping

you are correct but it was the easiest way and I was in my own so no danger of anyone else in the area. so even though the fault is on another circuit, some of the current flow from the pump neutral would go back down the earth fault as the neutrals are all connected at the same point. I get it now Richard. many thanks mate.


Probably not the best way to fault find by possibly making the lighting earthing live.

It would be that the majority of the current will flow via the neutral so if at a 6A running current say 10mA was passing through the fault but at 20 or 30A start up current over 30mA would pass through the fault and trip the RCD.
 
it was the easiest way and I was in my own so no danger of anyone else in the area

If you must test live (and in this case it wasn't necessary) it's much better to dis L & N than the CPC. Quite apart from possible hazards of a floating CPC, if the circuit is picking up an earth anywhere along its length, dissing the CPC won't localise the fault and will give a false negative result. But dissing L & N will always find the offending circuit.
 

Reply to Weird RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
758
I have a 20 amp gfci pool pump breaker that trips only when the pump is off during the night. Pool pump runs fine all day. I turn pump off...
Replies
2
Views
729
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock