Festerfly

I've been asked to install and American TIG welder in a workshop at a site where i do some more normal commercial works.

The Welder requires a 400v Supply (no problem as TP supply nearby) but the current DB is a Hager unit for whichi can only find max MCB's of 63A. this welder requires something closer to 80A per phase.

My thoughts we're can i split the supply feed prior to the DB (or drop extra feeds out the bottom of the DB incomer) and send a second set of feeds into a TP 100A Switch Fuse ? this would then in turn run 25mm 3 core SWA (10 metres max) and down to a another Switched Disconnect located closer to the Welder and then hardwired into this?

or have a missed something vital or even overcomplicating things?

FFYI - the welder is a Miller Syncrowave 351 and the manual can be found here 351 Manual

This needs to be done friday evening after the workshop has closed to minimise downtime.

Cheers in advance!
 
Last edited by a moderator:
All sorted now.


Basically it's a 2 phase welder. It requires two phases (live) at 80A rated and then an earth. The supply board has a maximum Amp of 63A per phase MCB. So it cannot handle the current. The manufacturer suggested either exchanging the welder for an Invertor 3 phase version which runs at a meagre 13a per Line or replace the DB with one which can handle higher loads.

Appreciate the help though.
 

Reply to Welder Installation in the Canada area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
516
Hello all, I have discussed my power install before as i am sure a lot of you will remember as it is quite different to a normal setup. I have a...
Replies
9
Views
2K
I am drawing up a contract for a job in a domestic property which has a 3-phase Distribution Board and need to supply 3ph to a heat pump that's in...
Replies
3
Views
2K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock