  1. happyhippydad
    Offline

    happyhippydad Member Electrician's Arms

    Location:
    Gloucestershire
    My friend has a garage door that when opens turns on a floodlight.

    He know wants it to turn on another light in the garage as well as the floodlight.

    The problem is this garage light is already on a plate switch, if the garage light was simply connected to the control panel then the plate switch would then operate the flood light as well, this needs to be avoided. (see pic below)

    Does anyone have a simple solution? Is there anyway to allow the line current only to flow from the panel and stop the back flow of current to the panel from the plate switch?

    garage.jpeg
     
    Last edited: Feb 12, 2019 at 8:56 AM
  2. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    Contactor.
     
    • Agree Agree x 4
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    use a relay. energise with the plate switch, use 1 piair of contacts N/O to switch gaage light. at same time use a pair of N/C to isolate floodlight from switch.
     
    • Agree Agree x 1
  4. happyhippydad
    Offline

    happyhippydad Member Electrician's Arms

    Location:
    Gloucestershire
    I was just about to add, can I use a contactor or relay! However, having just dealt with domestic electrics I am unsure how these work or would be connected into the circuit. If anyone could expand a little that would be great, thanks.
     
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    230V coil relay. energise with switch.pick a set of contacts.feed to common, N/Oto garage light, N/C tobreak switch feed to flood.
     
  6. happyhippydad
    Offline

    happyhippydad Member Electrician's Arms

    Location:
    Gloucestershire
    I think a diagram may be needed..... RICHARD!! :D
     
  7. snowhead
    Offline

    snowhead Respected Member

    Location:
    Mildlands
    If the plate switch isn't being used as 2 way you can use that.

    Connect the light to Common,
    Feed from the control panel to L1
    Permanent feed to L2
     
    • Like Like x 1
  8. happyhippydad
    Offline

    happyhippydad Member Electrician's Arms

    Location:
    Gloucestershire
    Snowhead! That is so simple yet effective. Many thanks :)
    Ps.. It is being used as 2 way (I was just lazy in my drawing), however he never uses the other switch so I can just eliminate it.
     
  9. Lucien Nunes
    Offline

    Lucien Nunes Mercury Arc Rectifier Respected Member

    Location:
    London
    NOOOOO! Not this again! Is this the same door or another one?
    If the light supply and door opener supply are on different circuits you can't do this as it ties the two circuits together. Even if on the same circuit, the door opener cannot be isolated using its means of isolation; the neutral remains connected and the line is disconnected only by a functional switch. You must use a relay.
     
    • Agree Agree x 1
  10. Lucien Nunes
    Offline

    Lucien Nunes Mercury Arc Rectifier Respected Member

    Location:
    London
    15499851907194471441317316975983.jpg
     
    • Like Like x 2
    • Informative Informative x 1