Discuss What do you code these? Commercial installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
No code for the mixture of manufacturers’ equipment, as that requirement doesn’t come into force until January the 1st.c3 for the mismatch of protective device brands
c3 for no ferrules on fine stranded SY
c3 for excess copper showing in that mcb
c3 for the use of SY where greases and heat are present if not deteriorated (also whats been done with the braid)
just my opinion anyway
526.9.1 Connection of multiwire, finewire and very finewire conductorssorry spin:
There is a requirement to suitably treat fine stranded conductors in screw down terminals.
SY cable isn't heat or grease retardant so may not be suitable in a kitchen environment.
& we can work to the 18th now.
Shouldn't there be a code for the fact that the circuit breakers aren't linked?
Only if they require linking, such as in a 3 phase motor where switching one MCB would leave the conductors live from the other MCBs.Shouldn't there be a code for the fact that the circuit breakers aren't linked?
Shouldn't there be a code for the fact that the circuit breakers aren't linked?
Switchfuses using cartridge fuses would not be linked.I thought about that,,, but then they aren't in switch fuses which just have cartridge fuses in...
526.9.1 Connection of multiwire, finewire and very finewireconductors
In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
It does not state “ferrules’.
A long standing practice for protecting such wires is to twist the exposed strands together and then fold them over.
In that case the code would be for not treating the fine stranded wires in accordance with Regulation 526.9.1.long standing practice it may be but in my book those methods do not prevent damage to the cores, either way it is clear in that picture no methods have been employed at all.
Does it require earthing?What are the odds on that SY braiding not being Earthed?
Pretty good I reckon
526.9.1 Connection of multiwire, finewire and very finewire conductors
In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
It does not state “ferrules’.
A long standing practice for protecting such wires is to twist the exposed strands together and then fold them over.
Whilst we are allowed to design, install and initially verify installations to the 18th edition, inspection and testing of existing installations should be conducted to the current edition.
No a ferrule is used to treat the end of a conductor.Hmmm, isn't a ferrule a terminal?
And, in BGB: BS7671:2008:Amd 1:
526.9.1 In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or
very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
No I haven't but I can tell you it's a Hager. I won't be going back as after pointing a few things out to the owner he has appointed another electrician to do the report.Have you got a picture with the lid on? Never seen that set up before.
The reason the hinges are nackard is because there is a water pipe obstructing the opening of the lid and it has been forcibly opened in the passed.I hadn't noticed the hinges look nackard in the photo too, and also there's a window for the breakers? how well does that fit? that thing is basically f****'d in so many ways
Reply to What do you code these? Commercial installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.