Discuss what do you think - C2 or C3 on an EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

pushrod

Rented property, with a fitted IP66 rcd socket outside for garden use. Tenancy agreement (to be signed by tenants) says only outside socket to be used in garden ie no extensions to be taken outside. Internal sockets are not rcd protected - what do you code them?
I would think C3 as an indication that they are safe but not to current regs. Have seen various discussions saying they should be C2 , but the presence of the outside rcd socket and its mention on the tenancy agreement makes me think it should be C3. Any thoughts?
 
Cheers. Only mentioned the tenancy agreement as they would have signed to say that they would only use the rcd protected for garden equipment. So if they then used an extension to the garden from an internal socket and electrocuted themselves (god forbid) it would be demonstrable that they were being numpties.
 

Reply to what do you think - C2 or C3 on an EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
513
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
796
Fun EICR at an HMO today, which was installed new 5 years ago (not particularly well!) Lots of niggly things that I'll sort, but in the kitchen...
Replies
61
Views
5K
Hi all, we got an EICR report done before tenanting our previous home having become "accidental landlords". See attached. The report came back...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock