cable rating table F4(i) OSG . (50mm would just make it in free air).
 
Can I ask , so based on your information , if I needed to extend or rewire part of the ryfield mains cable , a suitable sized cable based on what’s there already would be 70mm ?
Sorry, but I haven't got enough info to say. We are going off one piece of info but, with any supply, there are many things to take into consideration, especially working on a 200amp 3 phase input.
 
Based on the pics on the other thread showing each phase feeding two 60/80A Series 7's, the design load on it is no more than 160A and might be as low as 120A. The upstream 200A fuses only need to protect it against fault, not overload. In that thread I think it's fairly clear the reds are not sheathed, and we can see in the above pic that the neutral is not.

With the extra pics to look at and the O/D measurement I'm not sure that the concensus we reached there, i.e. 19/.064 is correct. It could be 0.1 sq. ins., unfortunately I'm nowhere near my books of 1960s tables to look it up.
 

Reply to What size is this sheathed copper imperial cable? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top