I am newly MCS accredited and have had a roofer approach me and ask me to install and commissiong a pv tile system(tiles are c21e solar tile, from solar centuray). It has 2 invertors, one invertor for18 of the tiles at 47 watt each and the other invertor for 12 tiles at 47 watt each.The 18 are west facing and the 12 south. I suspose i have a few questions, so here goes.

would you use 2 seperate 4mm cables to each invertor or just one and and isolate that ,
would you have all tiles on 1 string for each invertor, or a row of tiles per string (what advatages /disadvantages are there)
has anyone used these tiles
and what wuold you charge

I have a lot to learn , and would appreciate feed back

Chris
 
You should run each inverter off a seperate CB in the CU.

As for the string connections, which inverters are you using and are there any shading issues at the site?
 
there are no shading problems. Why would you use different strings, do they over ride each other? The invertors are a sunnyboy 1200 and a small one i had never heard off somthing 600 ( looks cheap and chinese)
 
( looks cheap and chinese)

Love this quote - nice one - if it looked cheap and was Japenese would it be any better? bearing in mind most of the stuf in our homes today comes from China.

I would ping Solarcentruary an email and ask them for the design, chances are they have already quoted this for the roofer and will have all the design spec on file.
 
No it wouldnt be any better , it would just be cheap looking and Japenese.Plus how do you know most of the stuff in my house comes from China ? or is it you with pre set ideas about chinese things?

Any way back to my questions, i will 'Ping' an email to solarcentuary and see what they say (hopfully not a chinese ping),

Thanks for your in depth reply , which has answered all my questions
 
The reason for splitting into strings is to combine and add V and A to get the best out of the inverter. At 47W per tile, you are probably looking at 1 possibly 2 strings depending on the operating voltage parameters of the inverter and the voltage output of the tiles.
 

Reply to what to charge to commistion a pv system for roofer, thoughts on solar tiles in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

My best mate has been medically retired from the prison service at the young age of 52 and has time on his hands :D He's looking at a 'plug in'...
Replies
7
Views
406
Hi, I have a 6kw PV with a 6kw Growatt battery and invertor. I have a solar iboost going to the hotwater tank. Recently I had a Ohme Home Pro...
Replies
2
Views
1K
Hi, So I'm replacing a small old off grid with a new 7.5kw off grid, & being poor seek best value for my mppt, after long searches I find this...
Replies
1
Views
609
Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
902
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock