I am at COLLEGE by the way, if your about to say join another trade or something lol. Also does RCD only operate if there is a earth leakage?
 
That would be an overload protective device, such as a fuse or MCB.
Yes RCDs only operate on earth leakage/earth fault.
A device that provides both overload and earth fault protection is known as an overcurrent device.
Such would be a fuse, MCB or RCBO.
 
I am at COLLEGE by the way, if your about to say join another trade or something lol. Also does RCD only operate if there is a earth leakage?

As above but

an RCD will operate on any difference between Live & Neutral currents through it.

The difference can be when current from live conductors is passing to earth,
or from one RCD live bus-bar to another RCD Live bus-bar,
 

Reply to What type of ADS is used for Short Circuit/Overload? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
677
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
764
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
724

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock