  1. gazzamikes
    Offline

    gazzamikes Electrician's Arms

    Location:
    Norwich
    Good evening everyone. Went to change my parents CU for them yesterday, I've never looked at the supply before, even when I lived there. I looked at the supply and there is no main earth? The only bonding there is. Is 10mm to the gas. First thought the gas was being used as earth but with connected ze 1.27 and with it disconnected 1.24 so this obviously isn't the case. They live in Norwich 1950's house along the biggest road through Norwich.

    Does the system require me to call dno for PME upgrade? I remember about two years ago looking the next doors for a rewire and am sure they where TN-C-S .

    What do you guys recommend?

    Thanks!
     
  2. gazzamikes
    Offline

    gazzamikes Electrician's Arms

    Location:
    Norwich
    Sorry Zs I mean guys
     
  3. Knobhead
    Offline

    Knobhead Guest

    A picture of the service head would be useful, otherwise we’re guessing.
    Not a good thing to do.
     
  4. gazzamikes
    Offline

    gazzamikes Electrician's Arms

    Location:
    Norwich
    Hi tony I didn't even think of a pic at the time I'll need to take one thanks
     
  5. gazzamikes
    Offline

    gazzamikes Electrician's Arms

    Location:
    Norwich
    It appears to be oval and cast?
     
  6. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    old cast iron cutout then here.....just your luck as DNO`s are changing em free of charge....so should be able to PME your supply at the same time....just leave a length of 16mm earth for em ready....and they should connect it into the neutral link in the new cutout when they come to fit it....
     
  7. gazzamikes
    Offline

    gazzamikes Electrician's Arms

    Location:
    Norwich
    That's great thanks for the help. So I can change board and test then retest when dno have done? Sorry for sounding imcompetant but never come across this it
     
Loading...
Similar Threads - What's going Here Forum Date
Triple light switch makes ticking noise - even after I replaced it. What's going on here? New Member Introductions Dec 27, 2017
Hive or Nest....what's your preference? Central Heating Systems Wednesday at 9:56 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job