    SP Networks are the DNO. Smallholding with single phase and 60 amp cable head fuse. What's the largest size likely to get approval?
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    normally 100A if you're lucky. anything over that, it's time to consider 3 phase.
     
  3. Scuba
    Offline

    Scuba EF Member

    Location:
    Glasgow
    Thanks for the response. What does that equate to in kW? Getting 3 phase in is out of the question.
     
  4. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    You're probably better off asking the DNO.

    I think Tel thought you meant what's the maximum size a single phase supply could be, as I thought you were asking the same thing until I noticed this is in the PV section so I assume you actually want to know what the max size of PV you could have is?
     
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    my bad. didn't read OP properly.
     
  6. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    I believe that for G83, the maximum is 16kW.
     
  7. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    Depends on the DNO. I have never been approved more than 5kw on single phase.
     
  8. Worcester
    Offline

    Worcester Trusted Advisor

    Location:
    Worcestershire
    We've got 2 17kW single phase PV systems in our village, very much DNO dependant and what else is on that phase from the substation.
    one installed in 2012 the other on 2015, different phases same substation, no other PV systems attached to those phases.

    if you get > 8kW you will have done well.
     
  9. Scuba
    Offline

    Scuba EF Member

    Location:
    Glasgow
    SP Networks are the DNO.
    It's an established smallholding with a single phase supply with a 60 amp cable head fuse.
    I'm trying to gauge the maximum size of solar panel array in kW likely to be approved. Roof space isn't a problem.

    Regarding a previous response of 5 kW on single phase, I recently got approval for a 10.9 kW array on a domestic house with single phase but 100 amp cable head fuse.
     
  10. TedM
    Offline

    TedM Electrician's Arms

    Location:
    .
    There is no real alternative to asking the DNO. Everything else is just guesswork, and it depends entirely on the local network circumstances.

    Most likely a smallholding has a dedicated transformer on to a 11kV 1-phase overhead line, and neighbours will all be on their own transformers as well, so that would be in favour of a larger connection.

    Some DNOs (e.g. WPD) publish interactive maps on their website that show possible connection limitations for distributed generation. But in the end, all you can do is ask them.
     
  11. Gavin A
    Offline

    Gavin A Electrician's Arms

    Location:
    Leeds
    Business Name:
    Leeds Solar
    60A feed, I doubt you'll get more than 16amps solar, but depends if they put in a bigger supply cable than that would indicate, length of cable, transformer, if the neighbours have any, whether the DNO engineer got laid the night before etc
     
  12. The Solar King
    Offline

    The Solar King Electrician's Arms

    Location:
    Edinburgh
    The people at SP Energy Networks are really helpful, and will also give you a verbal decision over the phone you can then work from for a G59 application.

    Biggest I had was a split phase at 18kW (9kw each phase), but that was with SSE and at 100amps.
     