Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss What's this object? in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Harry Worth
    Offline

    Harry Worth Guest

    Fuse board.jpg

    Hi all - Showing my ignorance/lack of experience here. I presume the main fuse for this system lurks inside the bulbous green box which has a seal on it. I need to pull the fuse to do some work on the system. There appears to be black slime oozing from this contraption. Any advice on how I isolate this system and what am I going to find when I snip the seal (ideally not Alien 5)

    Cheers, Harry
     
  2. Geoffsd
    Offline

    Geoffsd Guest

    Get the DNO - don't touch it.
     
    • Like Like x 1
  3. Harry Worth
    Offline

    Harry Worth Guest

    Wow - As bad as that. Could you let me know your thoughts - Thanks
     
  4. Plonker 3
    Offline

    Plonker 3 Guest

    It is sealed for a reason. The DNO are the only ones allowed break the seals so contact them, even tell them what you see there and they may send someone round as a emergency.
     
  5. Knobhead
    Offline

    Knobhead Guest

    Don’t touch it, get the DNO in to replace it. That is ancient, it will have porcelain fuse carriers that can disintegrate in your hand.
     
  6. NMc
    Offline

    NMc Electrician's Arms

    It looks like an old metal-clad cut-out and the black slime oozing from it will be the pitch from inside.

    If it is what I think it is the inside will not be the standard cartridge fuse but a piece of fuse wire wrapped around two posts

    Get the DNO out to check the leakage, if it is the old type they will or should change the cut-out and possibly fit you an isolation device
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    echo above posts. DNO job. don't even look art it funny. it's a right worm can for the unwary.
     
  8. mogga
    Offline

    mogga Just me Electrician's Arms

    This must be a record two days running guys knowing their abilities and seeking advice AND by the looks of it ACTING on advice given
    What you have is a very old cast metal cutout the fuse carrier will possibly be porcalain and shouldnt be touched due to reasons previouslty posted the black ooooozzzz is pitch and shouldnt be Ooozing this is a sign odf deterioration probably down to load it MAY also contain a small asbestos flash gaurd wadding
    CALL the DNO and tell them its smelling and oozing they will come out and replace it correctly with a nice new spangly series 7 cutout and probably an isolator for you to connect your tails to
     
  9. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    with some DNOs, if you have an isolator on site, they will fit it free. otherwise they may charge.
     
  10. Harry Worth
    Offline

    Harry Worth Guest

    Thanks everyone for the information. A big help in explaining to the guy I work with as to why we won't be tackling the job until the DNO has sorted it!
     
  11. Marvo
    Offline

    Marvo Admin and gender confused Staff Member Admin

    Location:
    South Africa
    I think this is a first. Everyone's in agreement.

    Just to buck the trend and return things back to normal I'm going to suggest you cut the seals forthwith pull out the rubber mat, Ray-Bans and the 10KV gloves and start investigating yourself.

    *Joking*
     
    • Like Like x 3
  12. Fin170
    Offline

    Fin170 Electrician's Arms

    Location:
    Devon
    Are those the ones some refer to as 'Coffin Incomers'?
     
  13. Knobhead
    Offline

    Knobhead Guest

    That’s weird! No arguing?

    The compound running out can be for a couple of reasons. The usual being heat from loading. The back and front of the cable spreader box used to be sealed with Kearns cement, over the years this dries and falls out.
    The oil used in the cable can soften the compound and force it out, this is when it gets dodgy. As the cable dries out due to oil loss it’s IR value falls, it can take years but the bang at the end of it is just as loud.
    At one time the old electricity boards tried wax instead of Trinidite compound, I’ve seen the wax bubbling in terminations, not a sight to inspire confidence.

    For once I’m saying “DON’T TOUCH”
     
  14. bradder
    Offline

    bradder Active EF Member

    porcelain fuse (some even have the neutral fused) + asbestos in the fuse carrier
     
  15. supasparxs
    Offline

    supasparxs Electrician's Arms

    Location:
    Leigh, Lancashire
    It's located on the feed side of the meter.
    The equipment is not your customers.
    Call the DNO
     
Loading...
Similar Threads - What's object Forum Date
So what's this all about Electrical Forum Feb 3, 2019
hikvision cameras duff. what's the crack? Alarms, CCTV and Security Systems Dec 17, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job