djtip

-
Reaction score
2
Hi All,

As a new member and newly qualified I guess you always get the things you haven't seen before in your early jobs.

So just picked up a small job of a new socket - spurred off existing RCB protected ring - so no prob there.

But also can I wire up this bathroom mirror with 2*internal 18W fluorescent lamps being used as a decorative cover over the hole in the wall where the CU is installed. The DNO fuse and meter and on the outside of the property.

At present the mirror is just hooked over a bar and lifts off to get to the CU and RCB, so not permanently fixed.

My solution is to hinge the mirror onto the wall on the left and fit a catch on the right thus making it into a door, so it is now fixed yet capable of being opened to reset the RCB should it trip.

I plan to put a switched FCU adjacent to the hinges but fixed to the building fabric. I will then use flexible cable (to BS6500 or &919) from the FCU into the mirror and restrain it appropriately near the hinge on the back of the mirror so that the cable forms a nice loop.
Given that the 'door/mirror' will only be opened occasionally and that the cable is not accessible when the door/mirror is in its normal closed position I do not plan to put any additional flexible conduit round the cable. The manufacturer's internal wiring, grommets and access points will all be used.

I think this comlies with chapter 52 of the regs, specifically 521.9.

Can anyone see any issues with this?

Dave
o
 
Re: when is a bathroom mirror not a mirror - or use of light in a hinged cupboard doo

The RCB is generally referred to as an RCD (residual current device) or occasionally RCCB (residual current circuit breaker).

You may be able to avoid complications if you install a 5A socket on the wall nearby and put a 5A plug on the mirror thingy thus making it a portable appliance instead of a fixed appliance.
 
Re: when is a bathroom mirror not a mirror - or use of light in a hinged cupboard doo

So, the CU is installed in a hole in the wall? Is this in a bathroom then, or is the bathroom mirror just a mirror to cover the hole? If so, why does it need power?
I am somewhat confused by this thread...
 
Re: when is a bathroom mirror not a mirror - or use of light in a hinged cupboard doo

The RCB is generally referred to as an RCD (residual current device) or occasionally RCCB (residual current circuit breaker).

You may be able to avoid complications if you install a 5A socket on the wall nearby and put a 5A plug on the mirror thingy thus making it a portable appliance instead of a fixed appliance.
Good thought, not part of the fixed wiring then.

You could use the very flexible silicone cable to give more leeway for flexing, but it may well be overkill. Other than that it is slightly unconventional but should be OK.
Make sure that the cable will not catch on anything as the door is closing.
 
Re: when is a bathroom mirror not a mirror - or use of light in a hinged cupboard doo

It has 2 lights as per post

I would take Marvo s suggestion, especially considering that the flex will be swinging back and forth and moving the fixed wiring for access would not be the usual practice for an installation
 
Re: when is a bathroom mirror not a mirror - or use of light in a hinged cupboard doo

So, the CU is installed in a hole in the wall? Is this in a bathroom then, or is the bathroom mirror just a mirror to cover the hole? If so, why does it need power?
I am somewhat confused by this thread...
I read it as being a bathroom type mirror but not being installed in a bathroom. Obviously if it is in a bathroom things may get considerably more complicated.
 
Re: when is a bathroom mirror not a mirror - or use of light in a hinged cupboard doo

I read it as being a bathroom type mirror but not being installed in a bathroom. Obviously if it is in a bathroom things may get considerably more complicated.

Yes, this is not a bathroom, but the client would like the light to work (for putting on makeup, possibly).

I like Marvo's suggestion as it means I don't have to fit hinges, so will probably go with that.

Thanks for all your feedback everyone.

Dave
 

Reply to when is a bathroom mirror not a mirror - or use of light in a hinged cupboard door in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm working on a site in the UK where a joinery company will be installing bespoke vanity cabinets. The cabinets will have MDF/mirrored doors with...
Replies
4
Views
983
Hi, I live in a property built in 1911. It has had asbestos artex applied to every ceiling in the house. I am currently creating a new...
Replies
1
Views
2K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Hi Everyone! You all seem like a friendly bunch and google keeps referring me back to here but I still cannot find any solid answers so...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock