oracle

-
Esteemed
Arms
Reaction score
413
Since the dawn of time, people have been portraying things that they sell as more than what they are.

Last few years, you could buy 16th Edition testers, 17th Edition CCU's, etc. The only thing that is XXth Edition is the Regs, but already they are offering 18th Edition test kit.

They can call it anything they want, but that doesn't make it so. The newer kit may do things a bit faster, or have more ranges, but the requirements for test kit are BS 61010 and BS 61557.

They even called CCU's 17th Edition, when it's how you equip and install that will determine whether your installation COMPLIES with the current edition of BS7671.

CCU's are made to a different BS standard anyway. If your kit has regular calibration checks it's good for the job, you don't have to renew it every time the Regs change.
 
Last edited:
Same as selling Part P as a qualification, it's no wonder there's confusion on these things.

But if you do pass an examination or complete a course in Part P then that is a 'qualification' isn't it? Same as pass an examination or complete a course in BS7671. What's the difference?
 
But if you do pass an examination or complete a course in Part P then that is a 'qualification' isn't it? Same as pass an examination or complete a course in BS7671. What's the difference?
I agree, but there are many newbies 'doing their part P' who believe that makes them a qualified electrician. I suspect many college courses perpetuate that myth. Unlike 7671 part P is a document that can be downloaded, read and understood in 10 minutes by any electrically competant person.
 
I agree, but there are many newbies 'doing their part P' who believe that makes them a qualified electrician. I suspect many college courses perpetuate that myth. Unlike 7671 part P is a document that can be downloaded, read and understood in 10 minutes by any electrically competant person.

Never having done the Part P course I don't know what involved.
It may be a simple exam but my point is that it's still classed as a qualification. If the college, or whoever, miss-sell the course then they need their arse kicking. (which I can't see happening...)
 
In a lot of wholesalers I’ve seen these “Site Guides”
upload_2018-9-24_9-56-12.png
whilst I’m not quiestioning their content they are not these
upload_2018-9-24_9-57-11.jpeg
I’m just wondering how many have bought the above thinking they have the latter.
 
In a lot of wholesalers I’ve seen these “Site Guides”
View attachment 44440
whilst I’m not quiestioning their content they are not these
View attachment 44441
I’m just wondering how many have bought the above thinking they have the latter.
The "Site Guide" is I believed published by the NICEIC as one f their guides, not as good as the IET OSG in my opinion. Tried to fob me off with a copy at the NICEIC cinema presentation, got the OSG at ELEX last week.
 
I agree, but there are many newbies 'doing their part P' who believe that makes them a qualified electrician. I suspect many college courses perpetuate that myth. Unlike 7671 part P is a document that can be downloaded, read and understood in 10 minutes by any electrically competant person.
A while since I did mine but the Part P element was never sold a an electrical course as such but rather a required element in a suite of courses required to be eligible to apply to be assessed to join a CPS.

There was little doubt that the Part P element was an explaination and assessment of the building regulations relevant to electrical installations. Alongside the then 17th edition and inspection and testing allowed successful candidates to have the knowledge to apply to join a CPS.

It did not cover practical skills.

part P has become a colloquialism bit like someone calling their Dyson. Hoover.
 
The "Site Guide" is I believed published by the NICEIC as one f their guides, not as good as the IET OSG in my opinion. Tried to fob me off with a copy at the NICEIC cinema presentation, got the OSG at ELEX last week.
quite but this is being sold in packages alongside the 18th which I think is a little naughty.

I have pointed this out, mostly to blank expressions.
 
A while since I did mine but the Part P element was never sold a an electrical course as such but rather a required element in a suite of courses required to be eligible to apply to be assessed to join a CPS.

There was little doubt that the Part P element was an explaination and assessment of the building regulations relevant to electrical installations. Alongside the then 17th edition and inspection and testing allowed successful candidates to have the knowledge to apply to join a CPS.

It did not cover practical skills.

part P has become a colloquialism bit like someone calling their Dyson. Hoover.
My Mrs calls ours Oleg
 
What I dont undersrand is why the NICEIC state its for installations upto 100amps? What changes if you go above that?
Hi Dillb
The OSG from the IET states the 100Amp max as well, introductions page 11
And I quote "this guide is restricted to installations"
a) at a supply frequency of 50hz
b) at a nominal voltage of 230Vac single phase or 400/ 230 Vac 3 phase
c) supplied through a distributors cut-out having a fuse rated at 100A or less to one of the following standards
BS 88-2
BS 88-3
BS88-6
BS 1361 TYPE 2
 
Last edited:
Hi Dillb
The OSG from the IET states the 100Amp max as well, introductions page 11
And I quote "this guide is restricted to installations"
a) at a supply frequency of 50hz
b) at a nominal voltage of 230Vac single phase or 400/ 300 Vac 3 phase
c) supplied through a distributors cut-out having a fuse rated at 100A or less to one of the following standards
BS 88-2
BS 88-3
BS88-6
BS 1361 TYPE 2
Have no idea why it double posted, can the Mods delete one for me, don't want to be accused of raising my post count.
 
Hi Dillb
The OSG from the IET states the 100Amp max as well, introductions page 11
And I quote "this guide is restricted to installations"
a) at a supply frequency of 50hz
b) at a nominal voltage of 230Vac single phase or 400/ 300 Vac 3 phase
c) supplied through a distributors cut-out having a fuse rated at 100A or less to one of the following standards
BS 88-2
BS 88-3
BS88-6
BS 1361 TYPE 2

Then the IET version covers installations up yo 300A??
 

Reply to When is the 18th Edition not the 18th Edition? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I'm working sub contract for a plumbing company installing Air source heat pumps, they have there MCS audit coming up and have asked if...
Replies
4
Views
1K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
469
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
631
Hi guys I’m at one of the funny times in my career where I can’t decide on what I want to do. I’m wondering if one of you experiences folks can...
Replies
0
Views
149
Experienced Electrician, C&G 236 Parts 1 & 2, AM 1 & 2 18th Edition Am 2. (JIB Gold Card) I've been out of the trade for some time, but did a...
Replies
2
Views
835

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock