Discuss When to apply 1.2 factor to R1+R2... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
8
I'm just trying to get my head round R1+R2 calculations (predicted rather than measured). All seems very straightforward naturally, however, I'm just after clarification of something. For the 1.2 factor that is applied to adjust the resistance of conductors to operating temperature, I just want to understand in what scenario I need to apply this?

For example (and to try and give a more specific context), if I am doing an initial verification on a circuit and I calculate my R1+R2, I know that by applying my 1.2 factor will provide me with the predicted resistance at operating temp. However, when I then measure this (under dead test conditions), I don't have to apply the 1.2 factor to my result before noting on the schedule of test results do I? I would be using rule of thumb figures for my max Zs permitted, I don't know whether this would dictate how I did things.

Thanks in advance for any help and clarification.
 
1.2 is used at the design stage to take into account increased conductor resistance due to operating temperature as you have mentioned.

When carrying out initial verification or subsequent testing such as a periodic it is much easier to multiply the maximum permitted Zs by 0.8.

It's the same thing just saves you doing the calculations on site.
 
The 0.95 is for Cmin. This is applied first to the max Zs but since the 3rd amendment of the 17th edition all max Zs published in the standard have Cmin applied.

If you refer to manufacturers information then you may need to apply Cmin especially for older devices that are still in use today.

If running from a private supply you may not need to apply Cmin.

Always apply the factors separately as both may not always be required.
 
I was taught on the 2396 to always use the 1.2 correction factor when calculating the resistance of R1+R2.

To be fair it's very accurate
 

Reply to When to apply 1.2 factor to R1+R2... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
699
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
597
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have...
Replies
9
Views
7K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock