The contactors I have used before usually just have N/O and N/C contacts rather than C/O, but you can wire one side of one pair of each to give a 'common', this will then give you the C/O function.
 
Normally as Phil above says, you would use two N/O contactors mechanically interlocked for larger currents, often these have timers controlling the C/O times, especially if it is for automatic transfer switches

As Tony said what is the intended application ?

For smaller applications (circa 10A or so), to provide an always supply for controls etc. I have used Schneider/Merlin 3NO/2NC contactors wired as I suggested above.
 
If this Auto changeover system is being used as a power supply transfer switch, between two separate supplies (Eg, Utility Power and Generator Power) you will need a ''4 Pole change over switch, never use a 3 pole in such situations....

Can't and won't comment any further, until you give us some idea what this change over switch is being used for??
 

Reply to Where can i find a 100A/63A change over relay/contractor???? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello folks, So my van got found after being stolen ;D Now I'm installing my own alarm on the van which is triggered when a door is opened. Im...
Replies
4
Views
490
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
1K
this its part of uk power network guide provide to their siemens operative..im searching on the internet to find them on pdf format but i...
Replies
1
Views
399
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hello! I'm needing some help. I'm wiring in a start panel, using a spst toggle, and a (momentary?) push button. The idea is to flip the switch to...
Replies
0
Views
561

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock